Copper Pipes for Gas Boiler Steam Chest?

Post Reply
 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Mon. Apr. 11, 2016 8:34 pm

IMG_2687.JPG
.JPG | 123.4KB | IMG_2687.JPG
For you guys who are in the heating/plumbing business, is it ok to use copper pipes for the steam chest on a gas fired steam boiler? I can't find a reference for it but something sticks in my head that it should be black iron for this purpose. I inspected this home today and found the boiler piped like this. Am I crazy?

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Apr. 11, 2016 9:05 pm

Copper is ok on the returns, but not on the steam side. The expansion/contraction from the steam cycles stresses the joints and they are likely to break at some point. With that said, some of them run a long time with copper.

Might be worth finding a manual for that boiler and see if it mentions anything about the piping material.

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Mon. Apr. 11, 2016 10:36 pm

Back in the 1960s copper was very cheap and I remember a friend telling me that some were using it on Long Island to pipe steam.

Copper does expand a lot more than iron or steel, but I think it expands very little more than the copper used in hot water systems at 200 degrees which is common.


 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Tue. Apr. 12, 2016 5:10 am

The amount of expansion is part of the problem, the other is that you can't make swing joints with sweated fittings. On certain boilers the copper piping can put mechanical stress on the sections. With that said, if I inherited a system that was piped with copper and had been running a while without issues, I would just run it until something had to be addressed.

The use of copper rather than black iron isn't a code issue, and only a few boiler manuals actually say "do not use copper".

 
User avatar
blrman07
Member
Posts: 2383
Joined: Mon. Sep. 27, 2010 3:39 pm
Location: Tupelo Mississippi

Post by blrman07 » Tue. Apr. 12, 2016 7:05 am

It's not the copper pipe per se but the solder holding the joints together.

Max temp for soldered copper joints in use on a boiler is 250F
Max pressure for soldered joints corresponds to the temp with is 15 psi.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Apr. 12, 2016 7:21 am

So, *coalkirk*, maybe another question would be, was it done with a lower temp lead solder or maybe it was a better, higher temp alloy solder? :?:


 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Tue. Apr. 12, 2016 7:47 am

Boiler was 20 years old, no sign of a problem. Not sure how I could determine the solder. I pointed out the lack of a swing joint. Code doesn't require iron pipe. I downloaded several manufacturers installation manuals and none of them said do not use copper. So I guess the answer here is "it depends."

 
User avatar
blrman07
Member
Posts: 2383
Joined: Mon. Sep. 27, 2010 3:39 pm
Location: Tupelo Mississippi

Post by blrman07 » Tue. Apr. 12, 2016 10:47 am

Unless your going to be running high pressure steam in excess of 15 psi I would say at this time there is no problem.

The melting point of the lowest solder is 360 F. 15 PSI steam corresponds to 250 F so I believe that it would be safe to operate.

 
User avatar
Berlin
Member
Posts: 1890
Joined: Thu. Feb. 09, 2006 1:25 pm
Location: Wyoming County NY

Post by Berlin » Tue. Apr. 12, 2016 3:02 pm

I've seen and we have had to repair MANY steam boilers piped with copper near the boiler. The sweat joints do fail over time because of higher rates of expansion, although, it may be many many years before this happens. It is also my opinion - completely unresearched but supported by anecdotal evidence - that a lot of copper piping anywhere on a steam system leads to faster boiler rot-out; perhaps an interaction of the ample oxygen and copper with the cast iron...

Not against code, and may last for years without issue, but, good practice is all black iron on steam.

 
User avatar
jpete
Member
Posts: 10829
Joined: Thu. Nov. 22, 2007 9:52 am
Location: Warwick, RI
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice

Post by jpete » Sun. Jun. 05, 2016 7:59 pm

The main reason I believe is just the conductivity of the copper. I guess eventually it will heat up but from cold, that steam is going to condense rather rapidly which would cause the boiler to run longer to reach setpoint. Everything I was taught says no copper on a steam system. That said, I've seen a bunch of them.

Post Reply