Small Off Grid Solar System ... I'm Taking the Solar Plunge

Post Reply
 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. May. 22, 2015 6:29 pm

So far I've purchased 4 x 260 Watt panels, an MPPT charge controller, and a 1500W 24V inverter. I still need to bag 4 x ~350 AH 6V deep cycle batteries, and all of the necessary racking, wires, junction boxes, and fuses to put this tiny system together. Will probably also need a 40 Amp rectifier and a generator. This system will not be grid tied. Hoping to get (on average) about 80 KWH per month from it. About 20% of our overall electrical demand (as long as we don't run the AC). Using it purely as a learning experience, but it may come in handy in a power outage.

Anyone know how to put one of these puppies together properly?


 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. May. 22, 2015 6:40 pm

Wow. That's pretty neat :D
How much you got into it cost wise?

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. May. 22, 2015 6:43 pm

what do you plan to power with it?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. May. 22, 2015 7:27 pm

Rob R. wrote:what do you plan to power with it?
I'm mainly hoping it will be sufficient to power both our refrigerator/freezer and our deep freezer if/when called upon. Both of our refrigeration units are new and combined they draw only half of the current of the older units they replaced. Realistically it won't power much more than that and a couple 10 Watt LED light bulbs (60 Watt equivalent). But after that, whatever roughly 2.6 KWH of on average daily output (after factoring in all of the inefficiencies of the system that I can think of) will permit. For comparison, we run our entire house on only about 8 to 10 KWH per day when the clothes dryer and the AC unit are not factored in.
Lightning wrote:Wow. That's pretty neat :D
How much you got into it cost wise?
Hoping to keep it at around $3K total (not including a generator). I'm in for $1,605 so far. That includes the 4 panels, the inverter, and the MPPT (maximum power point tracking) battery charge controller. Definitely doing this on the cheap. I just located a new 24V 40A battery charger (rectifier) that runs on 120 VAC single phase for only $206 delivered.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. May. 22, 2015 7:43 pm

Red = Positive
Black = Negative

Black (AC) = Hot
White (AC) = Neutral
Green = Earth Ground

Series connect the batteries for additive voltage.

You most likely know this already. :)

 
coalnewbie
Member
Posts: 8601
Joined: Sat. May. 24, 2008 4:26 pm
Location: Chester, NY
Hot Air Coal Stoker Stove: LL AnthraKing 180K, Pocono110K,KStokr 90K, DVC
Hand Fed Coal Stove: Invader 2
Baseburners & Antiques: Wings Best, Glenwood #8(x2) Herald 116x
Coal Size/Type: Rice,
Other Heating: Heating Oil CH, Toyotomi OM 22

Post by coalnewbie » Fri. May. 22, 2015 7:43 pm

I wish you well as I have tried this sort of system and failed miserably, perhaps you will do better.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. May. 22, 2015 7:50 pm

In case you were wondering, the 24V 40A battery charger would only come into play when there isn't enough sunlight to charge the battery bank with the solar panels. This rectifier can use either grid or generator sourced 120 VAC as its power source.

It's not good to leave a battery bank at half charge for any period of time. It's more than not good to take a FLA battery bank below the 50% charge level.

A 24V FLA (flooded lead acid) battery bank has exhausted 50% of its charge capacity when it voltage has dropped to 24.2V. You never want to go below that level.


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. May. 22, 2015 8:04 pm

coalnewbie wrote:I wish you well as I have tried this sort of system and failed miserably, perhaps you will do better.
What problems did you encounter?

 
grumpy
Member
Posts: 12276
Joined: Sat. Jan. 02, 2010 12:28 am

Post by grumpy » Fri. May. 22, 2015 11:19 pm

This might help with the battery's..

http://www.smartgauge.co.uk/batt_con.html

 
User avatar
davidmcbeth3
Member
Posts: 8505
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra

Post by davidmcbeth3 » Sat. May. 23, 2015 1:50 am

coalnewbie wrote:I wish you well as I have tried this sort of system and failed miserably, perhaps you will do better.
I have looked at 10 folks who went through a PV state rebate program ... they are generally happy with their system but also noted that the ROI is about 20 yrs.

I would need a ROI of 5 yrs before getting any type of system - its all about the $$$ with me. Currently, the technology isn't making it -- solar is just not viable in my latitude and weather cycles. Not yet anyway.

Wind is also a no-go, not enough wind.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. May. 23, 2015 3:36 am

grumpy wrote:This might help with the battery's..

http://www.smartgauge.co.uk/batt_con.html
That looks like excellent advice for parallel connected batteries, but to achieve 24V from 4 x 6V batteries I must wire mine in series. Your diagram shows the difficulty in balancing the charges properly in a parallel battery system.

The difference between series and parallel is that in series the voltages add up but the amps remain the same, whereas in parallel the amps add up but the voltage remains the same.

For me, it will be 4 x 6V and 350 AH batteries wired in series = 24V and 350 AH.

To keep from frying my MPPT charge controller my 4 solar panels must be wired in a 2 x 2 combination of the two methods known as 'series/parallel'.

 
User avatar
Freddy
Member
Posts: 7293
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Sat. May. 23, 2015 5:26 am

I've got solar & skipped the batteries. I grid tied and so far love it. I'm 4 years into a 9 0r 10 year payback. If I have time I'll come back & explain why I prefer grid tie..... in one breath I can tell you now..... it's cheaper & you get more power.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. May. 23, 2015 7:07 am

Freddy wrote:I've got solar & skipped the batteries. I grid tied and so far love it. I'm 4 years into a 9 0r 10 year payback. If I have time I'll come back & explain why I prefer grid tie..... in one breath I can tell you now..... it's cheaper & you get more power.
There is no doubt that a battery based off-grid type system costs fully twice as much (or more) as grid tied. That plus the FLA battery bank lasting only somewhere between 5 and 10 years. But it all depends upon your goals, and mine are not suited to grid tied. From what I've learned when the grid goes down a grid tied system goes down right with it. That means no power during an outage. My entire 'initial' aim is to have at least enough power to keep our frig and deep freezer up and running in an outage (without having to run an expensive generator, at least for 1 full day or less of outage, which is mostly what we see around here when we experience one). And mainly I want to learn its capabilities and have fun with it running other stuff during the 99% of the time when there are no outages. Sort of a hobby toy. You have to exercise the batteries on occasion anyway to my understanding, so why not have fun with it.

But with your electric car a grid tied system is perfect for you and a battery based system big enough to accomplish your goals would cost perhaps as much as your house.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. May. 23, 2015 7:17 am

Larry, Where will the excess power generated by solar go during those time periods after the batteries have become fully charged?
Must you manually switch the load(s) upon loss of utility power?

 
User avatar
johnjoseph
Member
Posts: 9299
Joined: Mon. Sep. 15, 2014 6:05 pm
Location: Aroostook County, Maine
Stoker Coal Boiler: Keystoker KA-6
Other Heating: pellet stove, oil boiler

Post by johnjoseph » Sat. May. 23, 2015 7:21 am

This is really interesting I like it! Keep us posted on this venture once it's complete and in use. I like he specifics your are able to pull from your coal use and if eventually you can apply those same types of specifics with your new electric system that would be beneficial for some that are looking at trying the same! Good luck with this venture! Great post Thanks!