Harmon 160 Wiring Issues
-
- New Member
- Posts: 1
- Joined: Sat. Nov. 15, 2014 10:51 am
- Hand Fed Coal Boiler: harmon 160sf
- Coal Size/Type: stove coal
I have a Harman 160. I have been trying to figure out how the wiring is supposed to be hooked up for my White Rodgers Type 11A61-103 control valve. Does anyone have one wired up and working and could post a picture of it? Or have a wiring diagram? I have searched but havent been successful in my searches. Thanks! I could also wire up a standard triple aquastat, as I have access to used aquastats from a local plumbing business.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
How many wire are there for the WR valve?
2 or 4?
Just 2= 24volt to move the valve open and closed
with 4 = 2 @ 24 volt and 2@ end switch (dry contact) to signal a start to a relay for the 120 volt circ. pump.
All the different valve makers wire the same if you can recognize which 2 wires are for what.
2 or 4?
Just 2= 24volt to move the valve open and closed
with 4 = 2 @ 24 volt and 2@ end switch (dry contact) to signal a start to a relay for the 120 volt circ. pump.
All the different valve makers wire the same if you can recognize which 2 wires are for what.