Propane Fired Forced Water Baseboard Temp

Post Reply
 
PJT
Member
Posts: 456
Joined: Fri. Jan. 06, 2012 11:11 pm
Location: South Central CT
Baseburners & Antiques: Magee Royal Oak; Glenwood Modern Oak 116
Other Heating: propane

Post by PJT » Fri. Nov. 15, 2013 9:46 pm

Could someone tell me how hot a forced water propane fired baseboard system should be at the baseboards? I measured the cover of the baseboard at about 170 just now.

We recently changed from an oil fired boiler to a propane fired unit. I swear the baseboards are a lot hotter now and Im wondering if its dangerous. We have the same Weil Mclane boiler we had before they just swapped out the burner section.

Thanks for any advice!

 
User avatar
Carbon12
Member
Posts: 2226
Joined: Tue. Oct. 11, 2011 6:53 pm
Location: Harrisburg, PA
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice/Anthracite
Other Heating: Heat Pump/Forced Hot Air Oil Furnace

Post by Carbon12 » Fri. Nov. 15, 2013 9:56 pm

What are the high and low limits set for on the aqua stat? Is the room temp what the thermostat is set for?

 
PJT
Member
Posts: 456
Joined: Fri. Jan. 06, 2012 11:11 pm
Location: South Central CT
Baseburners & Antiques: Magee Royal Oak; Glenwood Modern Oak 116
Other Heating: propane

Post by PJT » Fri. Nov. 15, 2013 10:22 pm

Thanks for the reply!

yes room temps are where the thermostats are set...dont know how to check the aqua stat settings.....

it just seems like the system is running a lot hotter; you can feel a lot more heat a hanging in the air a lot more quickly than with the old setup.


 
User avatar
Carbon12
Member
Posts: 2226
Joined: Tue. Oct. 11, 2011 6:53 pm
Location: Harrisburg, PA
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice/Anthracite
Other Heating: Heat Pump/Forced Hot Air Oil Furnace

Post by Carbon12 » Fri. Nov. 15, 2013 10:31 pm

Hot water baseboard, heated by whatever means, is often set for a hi temp of 180 and low temp of 160. The installer may have adjusted the temperature settings on your boiler. 170 degrees is nothing to worry about, usually.

 
PJT
Member
Posts: 456
Joined: Fri. Jan. 06, 2012 11:11 pm
Location: South Central CT
Baseburners & Antiques: Magee Royal Oak; Glenwood Modern Oak 116
Other Heating: propane

Post by PJT » Fri. Nov. 15, 2013 10:42 pm

it's 170 on the baseboard cover....the pipe and fins must be hotter

thanks again

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Sat. Nov. 16, 2013 5:18 am

As mentioned, It would be normal to have the water temps 160 to 180. It would also be normal to have some over ride. If it shuts off at 180 just as the thermostat is satisfied, it could easily go above 180. 170 at the baseboard would be normal at the start of the loop. I guess if I were concerned I'd check the temp of the boiler....maybe it got bumped up a bit. If it's set to shut off above 180, feel free to back it down, but leave a 20 degree differential.


 
User avatar
whistlenut
Member
Posts: 3548
Joined: Sat. Mar. 17, 2007 6:29 pm
Location: Central NH, Concord area
Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
Baseburners & Antiques: Glenwoods
Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
Other Heating: Oil HWBB

Post by whistlenut » Sat. Nov. 16, 2013 8:30 am

Was the burner all that was changed? Perhaps they adjusted the aquastat, but 170 is very normal at the start of the loop. Try it out for a little while, them make changes as necessary. Sounds like you are comfortable, anyway. :!:

 
PJT
Member
Posts: 456
Joined: Fri. Jan. 06, 2012 11:11 pm
Location: South Central CT
Baseburners & Antiques: Magee Royal Oak; Glenwood Modern Oak 116
Other Heating: propane

Post by PJT » Sat. Nov. 16, 2013 8:51 pm

I believe thats all that was changed.

Thanks for the help everyone!

 
PJT
Member
Posts: 456
Joined: Fri. Jan. 06, 2012 11:11 pm
Location: South Central CT
Baseburners & Antiques: Magee Royal Oak; Glenwood Modern Oak 116
Other Heating: propane

Post by PJT » Thu. Nov. 28, 2013 9:08 pm

Well the other night I was in the cellar when the boiler came on....suddenly heard this weird hissing sound and looked up to see steam escaping from a relief valve near the circulators ...this time I took note of the boiler temp gauge....it was reading 270 (F) and the pressure was around 22....needless to say I called the propane co and they came right out.....they found they had wired the new propane unit incorrectly when they swapped it in a couple months ago.....now the temp gauge reads 180 and the pressure is around 12....

Thanks for all the help the other day guys!

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Thu. Nov. 28, 2013 9:21 pm

PJT wrote:weird hissing sound and looked up to see steam escaping