Question on a Oil Bioler

Post Reply
 
User avatar
k9 Bara
Member
Posts: 499
Joined: Mon. Mar. 31, 2008 11:27 am
Location: Red Creek, Fair Haven area NY
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading

Post by k9 Bara » Sat. Sep. 08, 2012 3:44 pm

Background. The boiler is a buderus G205, oil burner.
Went to father in-laws house to test fire the boiler, checking for issues before the heating season. A problem I did find. Long story short, I have line power going into the (White Rodgers 8B48A) high limit switch, (looks like an aqua-stat to me) but no power coming out to burner. The water is cold and should be calling for heat. Before I just ordered the new switch, any other guess's? Power comes from emergency switch, to the limit switch, from there to burner and circ pump.

Thank you,

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Sep. 08, 2012 3:48 pm

Try shorting the TT terminals on the aquastat and see if it fires.

 
User avatar
k9 Bara
Member
Posts: 499
Joined: Mon. Mar. 31, 2008 11:27 am
Location: Red Creek, Fair Haven area NY
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading

Post by k9 Bara » Sat. Sep. 08, 2012 5:12 pm

Good call, I didn't do that. I was thinking the cold temp would automatically put power to the burner. But would be a quick test on it.

Thanks Rob.

 
User avatar
k9 Bara
Member
Posts: 499
Joined: Mon. Mar. 31, 2008 11:27 am
Location: Red Creek, Fair Haven area NY
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading

Post by k9 Bara » Sat. Sep. 08, 2012 6:00 pm

Wha la... fired up. :doh: So...the boiler doesn't maintain a certain water temp? Fires on demand only? Hmmm...

Thanks again Rob... a beer for you sir! :cheers:


 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Sat. Sep. 08, 2012 6:24 pm

Waaaahhhhhhhhhh! How come Robb gets to answer all the easy ones? Boo hooo :)

 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Sat. Sep. 08, 2012 9:12 pm

k9 Bara wrote:Wha la... fired up. :doh: So...the boiler doesn't maintain a certain water temp? Fires on demand only? Hmmm...

Thanks again Rob... a beer for you sir! :cheers:
Yes, my son has the same boiler. His fires only on demand. The water almost never reaches what I'd consider normal operating temperature. His radiators get warm and then the system shuts down as the thermostat is satisfied. Seems weird to me but I'm used to trying to maintain a boiler temperature. Have to ask the Germans where it was built.

 
User avatar
k9 Bara
Member
Posts: 499
Joined: Mon. Mar. 31, 2008 11:27 am
Location: Red Creek, Fair Haven area NY
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading

Post by k9 Bara » Sat. Sep. 08, 2012 10:36 pm

coalkirk wrote:
k9 Bara wrote:Wha la... fired up. :doh: So...the boiler doesn't maintain a certain water temp? Fires on demand only? Hmmm...

Thanks again Rob... a beer for you sir! :cheers:
Yes, my son has the same boiler. His fires only on demand. The water almost never reaches what I'd consider normal operating temperature. His radiators get warm and then the system shuts down as the thermostat is satisfied. Seems weird to me but I'm used to trying to maintain a boiler temperature. Have to ask the Germans where it was built.
Yeah, I was thinking that way. Was expecting it to fire to operating temp. Thank you for the help.