Baseburner internal check damper use

Post Reply
 
scalabro
Member
Posts: 4197
Joined: Wed. Oct. 03, 2012 9:53 am
Location: Western Massachusetts
Baseburners & Antiques: Crawford 40, PP Stewart No. 14, Abendroth Bros "Record 40"
Coal Size/Type: Stove / Anthracite.
Other Heating: Oil fired, forced hot air.

Post by scalabro » Fri. Nov. 10, 2017 9:54 am

So it's extremely windy today with a current OAT of 31*, 30.10 and rising barometer and 33% humidity. The draft is bouncing up and down from .04 (no wind) to pegging the gauge at 1.2 My Stewart is screaming along on just the primary air coming in around the draw grate slot. You can see from the pictures it's completely buttoned up. The ash door and clinker door are gasketed with 700* silicone so no primary leaks.

So I pulled the internal check wide open and in 5 minutes or so she has calmed down quite a bit.

Today is exactly the type of day the designers of this stove meant the check to be used.

If she cools down excessively I can either open the primary a bit or close the check a bit or a combination of both.

Attachments

IMG_2742.JPG
.JPG | 704.9KB | IMG_2742.JPG
IMG_2743.JPG
.JPG | 666.9KB | IMG_2743.JPG
IMG_2744.JPG
.JPG | 811.4KB | IMG_2744.JPG
IMG_2745.JPG
.JPG | 846.7KB | IMG_2745.JPG


 
scalabro
Member
Posts: 4197
Joined: Wed. Oct. 03, 2012 9:53 am
Location: Western Massachusetts
Baseburners & Antiques: Crawford 40, PP Stewart No. 14, Abendroth Bros "Record 40"
Coal Size/Type: Stove / Anthracite.
Other Heating: Oil fired, forced hot air.

Post by scalabro » Fri. Nov. 10, 2017 10:00 am

After 5-10 minutes after fully opening the internal check damper.

Hopefully some other BB freaks will chime in with how they use their check :clap:

Attachments

IMG_2746.JPG
.JPG | 905.9KB | IMG_2746.JPG
IMG_2747.JPG
.JPG | 785.7KB | IMG_2747.JPG
IMG_2748.JPG
.JPG | 1017KB | IMG_2748.JPG

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Fri. Nov. 10, 2017 10:21 am

The basically leaky stove design needed something to compensate for that and the internal check damper was a better safer way.

 
User avatar
Pauliewog
Member
Posts: 1824
Joined: Mon. Dec. 02, 2013 12:15 am
Location: Pittston, Pennsylvania
Hot Air Coal Stoker Furnace: Alaska 140 Dual Paddle Feed
Baseburners & Antiques: Fame Rosemont #20, Home Stove Works #25, Glenwood #6, Happy Thought Oak, Merry Bride #214, Sunnyside, Worlds Argand #114, New Golden Sun , & About 30 others.
Coal Size/Type: Stove, Chesnut, Pea, Rice / Anthracite

Post by Pauliewog » Fri. Nov. 10, 2017 10:39 am

Same conditions here Scott, running this morning with the check damper about 1/4 out.

On cold days when there is a strong draft, I open the internal check , and throw it into direct a minute, then open the ash door.

It sucks the fine fly ash right off the top and sides of the ash pan making the removal dust free.


Paulie

 
User avatar
tcalo
Member
Posts: 2068
Joined: Tue. Dec. 13, 2011 4:57 pm
Location: Long Island, New York
Baseburners & Antiques: Crawford 40
Coal Size/Type: Nut/stove anthracite

Post by tcalo » Fri. Nov. 10, 2017 11:34 am

My G109 is chugging along. 275 at the top of the barrel, 130 on the flue about a foot above the stove. Primary open a bit. Mpd, secondary and internal check 100% closed. Baro is doing it's thing. House is a comfy 71.

 
User avatar
Canaan coal man
Member
Posts: 822
Joined: Thu. Nov. 08, 2012 12:37 pm
Location: East Canaan, CT
Stoker Coal Boiler: Efm 520
Hand Fed Coal Stove: A little cubby coal stove in the basement
Baseburners & Antiques: Glenwood #6
Coal Size/Type: Stove And Nut

Post by Canaan coal man » Fri. Nov. 10, 2017 12:33 pm

Sorry for being a dumb farmer but what dose your internal check damper do again for the suspended pot stoves?

 
User avatar
tcalo
Member
Posts: 2068
Joined: Tue. Dec. 13, 2011 4:57 pm
Location: Long Island, New York
Baseburners & Antiques: Crawford 40
Coal Size/Type: Nut/stove anthracite

Post by tcalo » Fri. Nov. 10, 2017 12:47 pm

It allows some primary air to bypass the pot and go directly into the rear flue. It helps idle the stove low on warm days and tame the draft on windy days.


 
User avatar
wsherrick
Member
Posts: 3744
Joined: Wed. Jun. 18, 2008 6:04 am
Location: High In The Poconos
Hand Fed Coal Stove: Glenwood Base Heater, Crawford Base Heater
Baseburners & Antiques: Crawford Base Heater, Glenwood, Stanley Argand
Coal Size/Type: Chestnut, Stove Size

Post by wsherrick » Fri. Nov. 10, 2017 1:26 pm

Now if you want to really slow the fire on these you use the check damper and the over fire damper in the loading door.
The neat thing about the placement of these dampers is that when you use them you aren't sending cold air to compromise the combustion efficiency of the suspended fire pots. The secondary air damper in the loading door admits small streams of air which are heated quickly enough to encourage combustion of hydrocarbons released during the early stages of the combustion cycle of a freshly loaded batch of coal. The check damper below the fire diverts primary air up the back pipe without it ever touching the surface of the fire pot. The fire remains at the temperature required for it to burn the fuel at high levels of efficiencies. The excellent design of these stoves allows you to have your cake and eat it too, almost.

 
coalfan
Member
Posts: 1829
Joined: Tue. Mar. 12, 2013 3:00 pm
Location: NW ohio
Hand Fed Coal Stove: ds circultor1500 \chubby coal stove
Coal Size/Type: nut/ pea ant.some bit.
Other Heating: kerosene\cold nat. gas

Post by coalfan » Fri. Nov. 10, 2017 1:53 pm

there you base burners go / WS has spoke live and learn from the best on that type of stove !!!!!!!!!!!

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Fri. Nov. 10, 2017 2:03 pm

So the manually operated internal check damper did/does for the antique stoves what the baro does for the modern stove ?

Both systems are limiting draft thru the firepot by introducing air into the exhaust?

 
User avatar
Sunny Boy
Member
Posts: 25557
Joined: Mon. Nov. 11, 2013 1:40 pm
Location: Central NY
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace

Post by Sunny Boy » Fri. Nov. 10, 2017 2:13 pm

windyhill4.2 wrote:
Fri. Nov. 10, 2017 2:03 pm
So the manually operated internal check damper did/does for the antique stoves what the baro does for the modern stove ?

Both systems are limiting draft thru the firepot by introducing air into the exhaust?

Yes, Dave.

But the check dampers on antique stoves typically have a much smaller opening than a baro.

When fully closed, my 6 inch baro still has enough air leaking gap around the butterfly plate to equal the amount of opening of the check damper on my range, ..... and more gap than the total opening of the check damper of my base heater. So, a baro can sometimes be overkill for some of these smaller firepot antiques.

And check dampers don't bang shut with gusty winds. :D

Paul

 
fifthg
Verified Business Rep.
Posts: 356
Joined: Mon. Aug. 03, 2009 10:11 am
Location: southern anthracite field,Schuylkill County,Pa.
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: warm morning # 500
Baseburners & Antiques: Peninsular Western Hot Blast No.44K and Reading Foundry & Supply Co.

Post by fifthg » Fri. Nov. 10, 2017 2:29 pm

wsherrick wrote:
Fri. Nov. 10, 2017 1:26 pm
Now if you want to really slow the fire on these you use the check damper and the over fire damper in the loading door.
The neat thing about the placement of these dampers is that when you use them you aren't sending cold air to compromise the combustion efficiency of the suspended fire pots. The secondary air damper in the loading door admits small streams of air which are heated quickly enough to encourage combustion of hydrocarbons released during the early stages of the combustion cycle of a freshly loaded batch of coal. The check damper below the fire diverts primary air up the back pipe without it ever touching the surface of the fire pot. The fire remains at the temperature required for it to burn the fuel at high levels of efficiencies. The excellent design of these stoves allows you to have your cake and eat it too, almost.
My Peninsular hot blast 44 has an “ash out” lever,that opens a bypass from ash compartment directly to the chimney and around the pot.This is designed to suck ash out when shaking.I have learned to use that set up to help keep my stove idling.What a difference it made!As air tight as the stove is,my chimney draft still seems very strong,and it was hard to keep it idling until I tried this trick.

 
User avatar
Canaan coal man
Member
Posts: 822
Joined: Thu. Nov. 08, 2012 12:37 pm
Location: East Canaan, CT
Stoker Coal Boiler: Efm 520
Hand Fed Coal Stove: A little cubby coal stove in the basement
Baseburners & Antiques: Glenwood #6
Coal Size/Type: Stove And Nut

Post by Canaan coal man » Fri. Nov. 10, 2017 2:41 pm

tcalo wrote:
Fri. Nov. 10, 2017 12:47 pm
It allows some primary air to bypass the pot and go directly into the rear flue. It helps idle the stove low on warm days and tame the draft on windy days.
Ok nows i gets its.......... :clap: The G6's dont have anything that fancy i have secondary air and a external damper in the back of the stove to help with windy days thats it.

 
scalabro
Member
Posts: 4197
Joined: Wed. Oct. 03, 2012 9:53 am
Location: Western Massachusetts
Baseburners & Antiques: Crawford 40, PP Stewart No. 14, Abendroth Bros "Record 40"
Coal Size/Type: Stove / Anthracite.
Other Heating: Oil fired, forced hot air.

Post by scalabro » Fri. Nov. 10, 2017 3:11 pm

fifthg wrote:
Fri. Nov. 10, 2017 2:29 pm
My Peninsular hot blast 44 has an “ash out” lever,that opens a bypass from ash compartment directly to the chimney and around the pot.This is designed to suck ash out when shaking.I have learned to use that set up to help keep my stove idling.What a difference it made!As air tight as the stove is,my chimney draft still seems very strong,and it was hard to keep it idling until I tried this trick.
I don't use the check when shaking down simply because it ends up depositing quite a bit of fly ash in my 36 inch section of horizontal stove pipe. I do open it when I remove the COLD ashes though as it keeps the dust from exiting the ash pan drawer on removal of the ashpan.

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Fri. Nov. 10, 2017 3:43 pm

Canaan coal man wrote:
Fri. Nov. 10, 2017 2:41 pm
Ok nows i gets its.......... The G6's dont have anything that fancy i have secondary air and a external damper in the back of the stove to help with windy days thats it.
The G6 is a tighter stove, with a positive latch for the ash door as opposed to a lift over latch that requires more play in the hinge pins, Less need for further draft control, but it would be nice to have also.