Type M Factory Setting
- coal berner
- Member
- Posts: 3600
- Joined: Tue. Jan. 09, 2007 12:44 am
- Location: Pottsville PA. Schuylkill County PA. The Hart Of Anthracite Coal Country.
- Stoker Coal Boiler: 1986 Electric Furnace Man 520 DF
You need either a Draft Rite gauge or a Manometer to find out what your chimney draft is first then adjust the weight screw in and out on the M baro until matches the gauge .04 to .05 is a good start for a hand fed stove if your using a stoker stove then try .02 over the fire and .04 for the stack pipe draft check the draft right at the flue on the stove some stoker stoves have a little hole in the viewing door or on front of the stove to check over the fire draft . The link below shows the manomenter you want to get .There is also a Manomenter lending Program on this forum contact Memeber Matthaus to get on the list .csstoker wrote:does anyone know what the factory setting is for the Field Controls Type M baro?
http://www.dwyer-inst.com/PDF_files/mark2_iom.pdf
http://pdf.directindustry.com/pdf/bacharach/draft ... 26008.html