Draft Question

Post Reply
 
User avatar
1975gt750
Member
Posts: 206
Joined: Fri. Oct. 26, 2007 9:41 am
Location: new hampshire
Stoker Coal Boiler: keystoker kaa-2
Coal Size/Type: rice coal / blaschak
Other Heating: pensotti oil boiler with riello 40 burner

Post by 1975gt750 » Sun. Nov. 02, 2008 7:53 am

i justed got done installing my new chimney pipes from my keystoker kaa-2 to my excisting chimney.i set the draft per the keystoker manual and that is to set the draft at.02 at a high fire with the combustion blower off. which I can achieve by adjusting my baro damper. but the problem I am running into is after the draft is set at .o2 and then I turn my combustion blower on per keystoker manual the draft should fall to 0 but it does not it goes to about .005 just alittle above 0. should I be worried or what. besides that I have no other problems no smell never goes out burning 1 bag a day to heat 2000 square feet

chris

 
User avatar
rockwood
Member
Posts: 1381
Joined: Sun. Sep. 21, 2008 7:37 pm
Location: Utah
Hot Air Coal Stoker Furnace: Stokermatic
Hand Fed Coal Stove: Rockwood Stoveworks Circulator
Baseburners & Antiques: Malleable/Monarch Range
Coal Size/Type: Lump and stoker + Blaschak-stove size

Post by rockwood » Sun. Nov. 02, 2008 8:59 pm

The meter could be off a bit so maybe it's fine but you should keep an eye on your CO monitors just to be safe.


 
User avatar
coaledsweat
Site Moderator
Posts: 13768
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. Nov. 03, 2008 9:00 am

That's fine, going to zero or positive would be a greater concern. You still have a slight draft with the combustion blower running, I would think .005 is close enough.

 
User avatar
LsFarm
Member
Posts: 7383
Joined: Sun. Nov. 20, 2005 8:02 pm
Location: Michigan
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland

Post by LsFarm » Mon. Nov. 03, 2008 12:43 pm

Sounds perfect to me.

Greg L.