i am installing a newyorker wood/coal unit. I want the controls to be seperate from the oil boiler its being plumbed to. I plan on using a L4006B for overheat, but which aquastat should I use in conjuction with a thermostat? the new yorker has a draft blower on it, I will need to control it and the circulator.

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Mon. Oct. 20, 2008 7:29 am

A Honeywell L8124C will do high & low with a differential and also use a thermostat and run a circulator....maybe even an L8124 A or B would suit you. I can't remember the difference in the details. I'm not sure what control is used to run a draft inducer. I think they come with their own seperate control.


 
ssupercoolss
Member
Posts: 40
Joined: Sat. Jun. 07, 2008 7:28 am

Post by ssupercoolss » Mon. Oct. 20, 2008 7:54 am

well I figure the draft blower would get connected to where you would connect the burner motor....the way I see it is the draft blower would run up to like 180 or so, then back on at 160......just like the burner.