Estimating Old Radiator Water Volume?

This forum is for common products and questions such as chimney installations, CO detectors, coal bin designs and a variety of other general topics that do not fit into the other forums.
biggreen1
Member
Posts: 173
Joined: Wed. May. 14, 2008 7:39 pm

Post Fri. Aug. 22, 2008 9:05 pm

I'm trying to estimate the total volume of my heating system to make sure I have the proper size expansion tank. Neither the book I bought nor the software that came with it covers estimating water volume of radiators. Does anyone know the approximate volume that my radiators would have per section? I've attached a couple pictures of them. They are mostly 38" tall X 10 1/2" deep. They vary in width from 1 1/2' to over 4'. If someone had an idea of what each section would contain I could estimate it pretty close.
Thank you. BG
Attachments
sullivan run road myers 052.jpg
sullivan run road myers 053.jpg


User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Fri. Aug. 22, 2008 9:20 pm

Take a look at this link:

There are pdf files of old radiator catalogs. One of them should have the info you need. Post your findings here, to help the next guy.
Last edited by Yanche on Sat. Apr. 01, 2017 12:39 am, edited 2 times in total.
Reason: <removed dead link>
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

biggreen1
Member
Posts: 173
Joined: Wed. May. 14, 2008 7:39 pm

Post Fri. Aug. 22, 2008 10:18 pm

thank you for the link. So far I know my radiators are made by American Radiator Co. The style is Rococo and they were made at least as far back as 1897. They have 5 square feet per section if they are 38" high. So far no volume info.

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Fri. Aug. 22, 2008 11:01 pm

figure this out in radiation to the load by compiling the radiators

based on 12 psi operating and 30psi relief

If less than 1,000 square feet of radiation - multiply the total by .03 for a steel tank
If between 1,000 and 2,000 use .025
if greater use .02

to convert this to use a diaphragm tank

tank your result and multiply times .55 if the building is two stories tall - or by .44 if three stories

The answer will give you the volume of the diaphragm expansion tank -- Manufacturers list volume in their literature.

This is likely over sized but it doesn't fail. :roll:
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
coalkirk
Member
Posts: 4681
Joined: Wed. May. 17, 2006 8:12 pm
Stoker Coal Boiler: 1981 EFM DF520
Coal Size/Type: anthracite/rice coal
Location: Forest Hill MD

Post Sat. Aug. 23, 2008 7:23 am

Those are some fine looking radiators.
You have enemies? Good. That means you've stood up for something, sometime in your life. Winston Churchill

"I would rather have a German division in front of me than a French one behind me." —General George S. Patton

Burning rice coal in a 1981 EFM DF520, nut coal in a hand fired Jotul 507.

BIG BEAM
Member
Posts: 723
Joined: Fri. Jan. 25, 2008 9:34 am
Stove/Furnace Make: USS Hot blast
Stove/Furnace Model: 1557M
Location: upstate NY

Post Sat. Aug. 23, 2008 9:13 am

X-trol 30= to old 30 gal tank.Better to big than to small!
DON

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Sat. Aug. 23, 2008 9:43 am

NOW is also the time to renew - or refurbish - or replace those green leaky - most likely not working balancing valves on the radiators.

Here is a link to a non electric thermal reacting valve that will control a hot spot in a multi radiator zone.
**Broken Link(s) Removed**or you can simply get a new valve.
http://www.statesupply.com/displayCateg ... Rad_Valves

This one is fun to look at
http://www.antiqueplumbingandradiators. ... spage.html

:D :D :D :D
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

rberq
Member
Posts: 5008
Joined: Mon. Apr. 16, 2007 9:34 pm
Hand Fed Coal Stove: DS Machine 1300 with hopper
Coal Size/Type: Blaschak Anthracite Nut
Other Heating: Oil hot water radiators (fuel oil); propane
Location: Central Maine

Post Sat. Aug. 23, 2008 10:10 am

Your radiators are very similar to mine. I have 54 sections. When the contractor replaced my boiler three years ago, he installed an Amtrol Extrol Model 60 expansion tank, listed as 7.6 gallons. (Originally he put in a smaller one, found it was inadequate, and replaced it with the Model 60. One symptom of "too small" was that the boiler relief valve was releasing a couple cups of water per day.)

As someone said in an earlier posting, better too big than too small.

Incidentally, I think the contractor said my total radiator capacity was 55,000 BTU. I just realized when counting the sections, that works out to about 1000 BTU per section.
I'm trying to make this foolproof, but I'm badly outnumbered.


biggreen1
Member
Posts: 173
Joined: Wed. May. 14, 2008 7:39 pm

Post Sat. Aug. 23, 2008 6:00 pm

Yanche,
I checked all the pdf files on that web site, lots of good, interesting info but no volumes that I could find. I'm going to look some more.
Coalkirk,
Thanks, I sure couldn't afford to replace them.
rberg,
Thats great info. I ran my info through Stings formula below.
Sting,
Here is what I come up with using your formula:
147 sections X 5 sq. ft. per section= 735 sq. ft. X .03= 22.05 X .55 for my 2 story house= 12.1275gal.
According to that, a extrol 60 with a capacity of 7.6 gal. is not enough. I really should have a extrol 90 with a 14 gal. capacity. The "expert" at the local plumbing store is confident that a 60 is enough. It's been working OK with the 60, probably because we usually only use 7 of the 12 radiators. He said hardly anyone uses a 90 and it's a special order. He quoted a price of about $125 which seemed good compared to what I've seen at a couple on-line places. As Big Beam said, better to big than two small so I'm going with a 90.

If I can find water capacities I'll post them. Thank you all

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Sat. Aug. 23, 2008 8:29 pm

Glad to help!

and please note again -- this formula will likely oversize the expansion tank - but when shooting semi blindly with volume - its the final result that counts.

if you have been getting by with the 60 -- let it be so!

should you have drama in the future -- well maybe just plumb a vertical port some place before the circ pump - that you can isolate (normally you have an isolation already on the pump and an isolation valve on the boilers) and install another 60 in the future -- if needed... 8-)
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Sat. Aug. 23, 2008 10:18 pm

Take a look at one of my posts on expansion tanks:

installation questions

Send me the information the various fields are asking for an I'll run it through the calculator and post the results

This is the software calculator you get with John Siegenthaler's book.
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

biggreen1
Member
Posts: 173
Joined: Wed. May. 14, 2008 7:39 pm

Post Sat. Aug. 23, 2008 11:30 pm

Yanche,
That's one of the books I've been reading and that is the software I was trying to use. Without a estimate of radiator volume how can you use it?

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Sun. Aug. 24, 2008 12:14 am

And that's the problem. The volume of these was lost with the manufacturer. You can guess - but we did a better guess with the radiation. and measuring the pipe runs - good luck - I might consult a palm reader! :P

I was monkey wrench on a job recently and the customer had a newer Hi end water softener that metered gals used. We set it the night before to recharge and filled the system noting the before and after registration of the meter.

Sort of a rear view mirror approach to system sizing -- but any port in a storm :lol: ah captain?
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
wsherrick
Member
Posts: 3731
Joined: Wed. Jun. 18, 2008 6:04 am
Hand Fed Coal Stove: Glenwood Base Heater, Crawford Base Heater
Baseburners & Antiques: Crawford Base Heater, Glenwood, Stanley Argand
Coal Size/Type: Chestnut, Stove Size
Location: High In The Poconos

Post Sun. Aug. 24, 2008 12:50 am

Don't even think about replacing those radiators.

rberq
Member
Posts: 5008
Joined: Mon. Apr. 16, 2007 9:34 pm
Hand Fed Coal Stove: DS Machine 1300 with hopper
Coal Size/Type: Blaschak Anthracite Nut
Other Heating: Oil hot water radiators (fuel oil); propane
Location: Central Maine

Post Sun. Aug. 24, 2008 9:06 am

wsherrick wrote:Don't even think about replacing those radiators.


Agreed. I have fought that battle twice now with my wife. We have a 28 X 14 living room where the cast iron radiators cover about 7 linear feet of wall, and give a nice even heat. The contractor estimated we would have to cover almost every inch of wall available to get equivalent heat from hot water base board. And then what becomes of the ten feet of bookcases, the table in the corner, the stereo cabinet, the antique desk, the grandfather clock, etc. etc.? They just don't look the same when forced to sit six inches out from the walls.
I'm trying to make this foolproof, but I'm badly outnumbered.