In-joist radiant heat

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Mon. Jan. 24, 2022 7:25 pm

Hey everyone, looking for opinions.. after this heating season I will be installing in-joist radiant heat in the upstairs floor joist cavity, before I finish the downstairs, right now the downstairs is unfinished and wide open, I will be removing the oil furnace and ductwork, house is 30x38, 16” o.c. Joist, I’m thinking 4 equal sized zones, that will be living room, kitchen, bedroom/bathroom, bedroom/bathroom, is it easier to buy 4 rolls of 300’ of pex for each zone, or buy a 1000’ roll and one of those pex un-spoolers? I can get a 1000’ roll cheaper.. and would have some left over for future use.. I am using heat transfer plates, a 4 port manifold which will be in the center of house under stair well, I have a constant circulator now that feeds the manifold in the basement that has dhw, basement radiators on it, and I’m thinking I can just put a circulator with flow check valve on spare port and then have that feed the radiant manifold.. am I best to just use the existing thermostat for the hot air unit and have it control that 2nd circulator?

Thank you in advance!

Attachments

BAF46197-1091-4B14-9596-007C7186E5EE.png
.PNG | 258.3KB | BAF46197-1091-4B14-9596-007C7186E5EE.png
3B50C07B-E2F9-4E9D-8742-D856B9175764.png
.PNG | 726.1KB | 3B50C07B-E2F9-4E9D-8742-D856B9175764.png


 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Jan. 29, 2022 2:18 pm

I could go either way on the roll length. What size pex are you using? Normally with 1/2” you try to keep each loop 300’ or less. A 300’ roll would be handy in that regard.

I would also rethink your zones. It is nice to keep the bathrooms warm and the bedrooms cool. You say 4 zones but only mention 1 thermostat…do you just mean 4 loops? Is all of the flooring material the same?

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Jan. 29, 2022 6:31 pm

Goin with 1/2”

Yes 4 loops, 1 zone.

Each zone will be around 310-340’ including the runs to and from the manifold.

All flooring upstairs is linoleum on top of 3/4” plywood.

I want the whole house just one temp, it is now, no need to make one room different than the other…

Obviously I’ll need to throw a mixing valve in there somewhere also..

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Jan. 29, 2022 6:33 pm

I would consider 5/8” tubing. You can go up to 400’ with that.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Jan. 29, 2022 6:53 pm

Can you point me towards the aluminum panels for 5/8?

That’s the other argument I see a lot… do you need the aluminum panels? My grandfather next door to me has in joist radiant heat, with a older rubber type hose, just simply stapled to the bottom of the floor, with nothing under it, open joist, no insulation or anything, and it heats his house just fine…

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Jan. 29, 2022 7:11 pm

Some of the plates will work with either size.

You can get by without the plates if you run a high enough water temperature. I know some folks that did a staple up system without the plates and even with 180 degree water in it the room gets cool in weather like this.

I have not checked your math - are you planning one run of pex per joist cavity or two?

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Jan. 29, 2022 7:41 pm

2 runs of pex per joist, joist are 16” on center, house is 30x38..


 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sat. Jan. 29, 2022 7:47 pm

So what can you expect the BTU heating to be per foot of pex?

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Jan. 29, 2022 8:50 pm

Lightning wrote:
Sat. Jan. 29, 2022 7:47 pm
So what can you expect the BTU heating to be per foot of pex?
Enough lol I don’t know

 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Sat. Jan. 29, 2022 9:34 pm

When looking at the infloor heating, I read the metal transfer plates and PEX-AL-PEX were the better way to spread the heat for the flooring.

Not exactly the same thing but throwing that out there. Are you planning to use PEX-AL-PEX ?

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Jan. 29, 2022 9:37 pm

Nope no pex Al pex here just pex.

 
LTStorm07
Member
Posts: 106
Joined: Tue. Sep. 11, 2012 8:32 pm
Location: Stillwater, PA
Stoker Coal Boiler: 1980 EFM DF520
Hot Air Coal Stoker Furnace: Alaska Stoker II
Coal Size/Type: Rice
Other Heating: Heat pump / Propane

Post by LTStorm07 » Sat. Jan. 29, 2022 10:35 pm

I can tell you that my coworker just purchased a house with radiant floor heat that was added as a later thought after tearing out hot water baseboards. His floors do have the 1/2 barrier pex and plates, double passes, and believe it or not, it struggles in temps (0 degrees) like this. It has full fiberglass insulation sealing it into the joists and all. He had a HVAC company come check it out and they told him even with plates and all, there simply isn't enough radiation for his floor plan + ceilings. Apparently the previous owners had to crank the temp way up to make up for it. They were running 160 degree water unmixed. The HVAC company told him without the plates it would had really struggled. The homeowners put the system in themselves. He's looking at ultra low temp mini splits to help things out now since he can't keep the floor running over 150 degrees safely. His floors are all tile and hardwoods.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Jan. 29, 2022 10:48 pm

I could see where tile and hardwood would hinder the transfer of heat… I only have a sheet of plywood and roled linoleum so it should transfer heat quite well… of course it is a worry of mine that it won’t heat properly…. But I guess there’s no way of knowing till you do it.

I see you mentioned “+ceilings” so I’m assuming you mean he has vaulted or tall ceilings?

 
LTStorm07
Member
Posts: 106
Joined: Tue. Sep. 11, 2012 8:32 pm
Location: Stillwater, PA
Stoker Coal Boiler: 1980 EFM DF520
Hot Air Coal Stoker Furnace: Alaska Stoker II
Coal Size/Type: Rice
Other Heating: Heat pump / Propane

Post by LTStorm07 » Sun. Jan. 30, 2022 12:21 am

hotblast1357 wrote:
Sat. Jan. 29, 2022 10:48 pm
I see you mentioned “+ceilings” so I’m assuming you mean he has vaulted or tall ceilings?
Yep, he has vaulted ceilings with a fairly open floor concept and even with fans pushing it back down it doesn't help.

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Jan. 30, 2022 7:49 am

LTStorm07 wrote:
Sun. Jan. 30, 2022 12:21 am
Yep, he has vaulted ceilings with a fairly open floor concept and even with fans pushing it back down it doesn't help.
A heat loss calculation of that home would likely reveal that the heat loss is too high to be offset by radiant floors alone. A 2 stage thermostat and some radiators would have been a simple solution.

As for the temperature of the water, that is just a means to an end. You do not want the floor to be warmer than 80 degrees or so, or it will be uncomfortable.


Post Reply

Return to “Coal Bins, Chimneys, CO Detectors & Thermostats”