High CO levels this morning.
Hey everyone I have some questions concerning carbon monoxide. I’ve had a detector down by my furnace since I’ve been burning and it never went off but does not give an actually number that you can read, just goes off when it’s too high. I bought two more and set them up last night and this morning all 3 in different locations were going off. Highest reading I got was 50 in the basement. I have no idea why all of a sudden.
First thing I though was maybe my fire is not hot enough. It’s been in the 50s during the day and I have the air cut way back on it to slow the burn. At night the temps have been in the 30s still.
When they went off I opened some doors and windows and opened the ash door. Shook the ash and let the fire get ripping. After 20mins I reset them all and shut all the doors and windows. They’re all reading zero now since then. And the highest saved reading I’ve gotten since resetting has been zero on all three levels of the house.
So my question would be is this a draft problem ? Or is it a fire not hot enough problem ? Even tho I have the air cut back the fire is still plenty warm enough to keep my house 68-70 through the 30-40 degree night. The fact that the fire takes off within 20mins with the ash door wide open, even after a 12 hour burn still loaded with ash has me confused.
In my mind I should be able to cut the air to the fire back as much as I need to slow the burn, and as long as it’s still drafting any carbon monoxide it produces should just go right up the chimney ? I’m new to this coal burning thing so maybe I’m not understanding drafting correctly ? Or could one of my pipes be leaking back into the house ? As of now I’m just letting the fire finish burning out until I can come up with a reason for why it got that high. Any help or opinions would be much appreciated!
First thing I though was maybe my fire is not hot enough. It’s been in the 50s during the day and I have the air cut way back on it to slow the burn. At night the temps have been in the 30s still.
When they went off I opened some doors and windows and opened the ash door. Shook the ash and let the fire get ripping. After 20mins I reset them all and shut all the doors and windows. They’re all reading zero now since then. And the highest saved reading I’ve gotten since resetting has been zero on all three levels of the house.
So my question would be is this a draft problem ? Or is it a fire not hot enough problem ? Even tho I have the air cut back the fire is still plenty warm enough to keep my house 68-70 through the 30-40 degree night. The fact that the fire takes off within 20mins with the ash door wide open, even after a 12 hour burn still loaded with ash has me confused.
In my mind I should be able to cut the air to the fire back as much as I need to slow the burn, and as long as it’s still drafting any carbon monoxide it produces should just go right up the chimney ? I’m new to this coal burning thing so maybe I’m not understanding drafting correctly ? Or could one of my pipes be leaking back into the house ? As of now I’m just letting the fire finish burning out until I can come up with a reason for why it got that high. Any help or opinions would be much appreciated!
- WNY
- Member
- Posts: 6307
- Joined: Mon. Nov. 14, 2005 8:40 am
- Location: Cuba, NY
- Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
- Coal Size/Type: Rice
- Contact:
Yes, it could depend on your chimney and draft settings. LIke lee said, get a draft gauge/manometer, mine will go off if I leave the ash door open too long while changing the pan, etc....some may leak out if the doors are opened/closed, depending on the draft you have. sometimes when it's warmer, you have to run a little hotter to keep a good draft.
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Right.. that is puzzling. It might be a brief draft reversal due to wind direction or some other factor. Refresh me about your setup. In the basement, I assume. Do you have a cold air return back to the furnace from the living area?
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
Okay... I think we're making progress here.. my hypothesis is that the convection blower on the coal furnace is creating a low pressure area in the basement, effectively sucking exhaust back down the chimney. This would be even more evident during mild weather and cooler burns.
That, coupled with sharing a flue is destroying the chimney draft. Do you depend on the oil burner at all? If not, I would suggest a lock out, tag out, cut power to it and stuff the oil burner's exhaust pipe with fiberglass insulation.
That, coupled with sharing a flue is destroying the chimney draft. Do you depend on the oil burner at all? If not, I would suggest a lock out, tag out, cut power to it and stuff the oil burner's exhaust pipe with fiberglass insulation.
Last edited by Lightning on Thu. Dec. 26, 2019 2:18 pm, edited 1 time in total.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
You can do a lot of air current and leak checking with a smoke/incense stick place where direction or leak might be suspect...
Also, with weaken fire it can be easier for other household exhaust equipment to over come any weak chimney draft, like clothes dryer and kitchen and bath exhaust fans ...All this especially with a 'shared chimney'...can you cover oil furnace barometric damper with aluminum foil?
Does home have a fireplace?
Also, with weaken fire it can be easier for other household exhaust equipment to over come any weak chimney draft, like clothes dryer and kitchen and bath exhaust fans ...All this especially with a 'shared chimney'...can you cover oil furnace barometric damper with aluminum foil?
Does home have a fireplace?
Last edited by McGiever on Thu. Dec. 26, 2019 2:25 pm, edited 1 time in total.
-
- Site Moderator
- Posts: 11417
- Joined: Wed. Nov. 05, 2008 5:11 pm
- Location: Kent CT
- Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
- Baseburners & Antiques: Glenwood Modern Oak 114
- Coal Size/Type: nut and pea
Once you get the manometer set up you should be able to confirm Lee's hypothesis pretty quickly by closing that door with blower running, and with door open.
I don’t use it for anything. I actually have it turned off in the breaker box. I can Disconnect it then block off the flu behind the Boro.Lightning wrote: ↑Thu. Dec. 26, 2019 1:49 pmOkay... I think we're making progress here.. my hypothesis is that the convection blower on the coal furnace is creating a low pressure area in the basement, effectively sucking exhaust back down the chimney. This would be even more evident during mild weather and cooler burns.
That, coupled with sharing a flue is destroying the chimney draft. Do you depend on the oil burner at all? If not, I would suggest a lock out, tag out, cut power to it and stuff the oil burner's exhaust pipe with fiberglass insulation.
So do you think by keeping the basement door closed it is causing the basement to become more of a low pressure area ?
Also as far as the cold air return goes. Should there be on to the actual coal furnace ? Or the fact that there is one to the oil furnace is good enough even tho the oil furnace doesn’t run at all ? Not sure I fully understand how the cold air returns work so sorry it If I sound ridicules