Yes, another manometer question

Post Reply
 
coalcherry
New Member
Posts: 13
Joined: Sun. Mar. 25, 2018 2:46 pm

Post by coalcherry » Sun. Oct. 27, 2019 8:00 pm

Hi all,
Wonderin' about my draft.Manometer is about .06 with it surging today with high winds as much as .08. Mfr recommends. 04. It's still warm here during the day.
Question is, should I adjust baro now or wait for colder weather? I am running my stoker on its lowest setting and it is working fine with no smells or co. I have co detectors throughout my house also a handheld by my stove.
I know there's a wealth of knowledge on coalpail so thank you in advance.🍺

 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Sun. Oct. 27, 2019 8:33 pm

.08 is more draft than .04. In other words with the high winds your chimney is sucking more heat from stove. Typically the baro is adjusted during a typical heat load on the stove, and that would also mean during colder outdoor temperature.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Oct. 27, 2019 8:40 pm

Keep in mind that wind gusts will still make the mano jump just briefly due to the inertia required to open the baro door.

 
coalcherry
New Member
Posts: 13
Joined: Sun. Mar. 25, 2018 2:46 pm

Post by coalcherry » Sun. Oct. 27, 2019 8:47 pm

Ok, I copy both answers. Winds have died down now and stove is steady at .06 but I think its be cause it's still warm.


 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Oct. 27, 2019 8:50 pm

If its steady at .06 then yes, adjust the baro door to open sooner.

 
coalcherry
New Member
Posts: 13
Joined: Sun. Mar. 25, 2018 2:46 pm

Post by coalcherry » Sun. Oct. 27, 2019 8:52 pm

Hey thanks Lightning.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Oct. 27, 2019 8:59 pm

coalcherry wrote:
Sun. Oct. 27, 2019 8:52 pm
Hey thanks Lightning.
Your welcome :)

As it gets colder outside and the appliance works harder to meet heating demand the chimney draft will increase. So you may or may not need to adjust it again later during the heating season.