Draft issues due to chimney cap?

 
brandonh98
Member
Posts: 84
Joined: Mon. Mar. 27, 2017 9:55 pm
Location: Drums, PA (NEPA)
Hot Air Coal Stoker Stove: Leisure Line Hyfire

Post by brandonh98 » Wed. Feb. 28, 2018 6:27 pm

I just wanted to get some input on this. I have horrible draft on my chimney when it gets warm out and I've tried just about every trick in the book. Did countless searching on this forum and others. One thing I haven't read much about is the chimney cap causing draft issues. I just took mine off today to do a test it out.

Previous owner had a wood burner and had a 5" SS chimney liner installed. The 8X8 clay tiles look brand new and the manufacture called for at least a 6" chimney liner so I elected to remove the liner altogether and go without one. The cap, however, stayed. Maybe the pictures will speak for themselves.

Let me know if you think removing the cap will improve draft or not, and I'll get back to you with the results of the test.
IMG_20180228_172140458_HDR.jpg
.JPG | 493.4KB | IMG_20180228_172140458_HDR.jpg
IMG_20180228_172323988.jpg
.JPG | 412.3KB | IMG_20180228_172323988.jpg
IMG_20180228_172340637.jpg
.JPG | 468.3KB | IMG_20180228_172340637.jpg
IMG_20180228_172355262.jpg
.JPG | 361.2KB | IMG_20180228_172355262.jpg


 
User avatar
coaledsweat
Site Moderator
Posts: 13761
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Feb. 28, 2018 6:44 pm

How tall is the chimney?

 
Olllotj
Member
Posts: 558
Joined: Thu. Sep. 04, 2014 10:01 am
Location: Western NY 14141
Stoker Coal Boiler: Keystoker KB-8
Coal Size/Type: Buckwheat
Other Heating: Utica Propane Hot Water

Post by Olllotj » Wed. Feb. 28, 2018 6:50 pm

That chimney needs a crown on top to protect the blocks!

A proper masons builders supply should have premade crowns that fit the 16x16 block with the 8x8 terra-cotta liner.

I removed my cap in order to stop the roof staining, and it worked great. Not sure how it effects the draft, but I’ve heard it both ways.

Here it is http://www.genestprecast.com/chimney-caps.html or you can pour in place
Last edited by Olllotj on Wed. Feb. 28, 2018 6:58 pm, edited 2 times in total.

 
Qtown1835
Member
Posts: 705
Joined: Sat. Nov. 08, 2014 11:47 am
Location: Quakertown, PA
Stoker Coal Boiler: Keystoker '81 KA4 (online 1/16/17)
Coal Size/Type: WAS Lehigh Rice (TBD)
Other Heating: EFM SPK600

Post by Qtown1835 » Wed. Feb. 28, 2018 6:51 pm

The cap shouldn't effect draft if anything I would think it would help to reatin some heat and keep the draft. You can try cracking a window, running stove hotter, and make sure dryer and bathroom vents are not running.

 
User avatar
freetown fred
Member
Posts: 30292
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Wed. Feb. 28, 2018 6:53 pm

As in, is the chimney a couple feet taller then the roof peak?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 28, 2018 6:54 pm

Weather Vane type chimney caps are reported to enhance chimney draft. I'm not sure of any other types being of draft related benefit.

 
brandonh98
Member
Posts: 84
Joined: Mon. Mar. 27, 2017 9:55 pm
Location: Drums, PA (NEPA)
Hot Air Coal Stoker Stove: Leisure Line Hyfire

Post by brandonh98 » Wed. Feb. 28, 2018 7:28 pm

Olllotj wrote:
Wed. Feb. 28, 2018 6:50 pm
That chimney needs a crown on top to protect the blocks!

A proper masons builders supply should have premade crowns that fit the 16x16 block with the 8x8 terra-cotta liner.

I removed my cap in order to stop the roof staining, and it worked great. Not sure how it effects the draft, but I’ve heard it both ways.

Here it is http://www.genestprecast.com/chimney-caps.html or you can pour in place
Never even heard of a chimney crown. Thank you for the link. So I guess the weather will eventually destroy the top of the chimney? That chimney has been covered with that aluminum cap since it was built in 1995.


 
brandonh98
Member
Posts: 84
Joined: Mon. Mar. 27, 2017 9:55 pm
Location: Drums, PA (NEPA)
Hot Air Coal Stoker Stove: Leisure Line Hyfire

Post by brandonh98 » Wed. Feb. 28, 2018 7:30 pm

freetown fred wrote:
Wed. Feb. 28, 2018 6:53 pm
As in, is the chimney a couple feet taller then the roof peak?
Chimney would need to be 15 feet taller to be above the peak of the roof. There is nothing within 12' of the top of the chimney though. It's a long gently sloping roof.

 
brandonh98
Member
Posts: 84
Joined: Mon. Mar. 27, 2017 9:55 pm
Location: Drums, PA (NEPA)
Hot Air Coal Stoker Stove: Leisure Line Hyfire

Post by brandonh98 » Wed. Feb. 28, 2018 7:35 pm

coaledsweat wrote:
Wed. Feb. 28, 2018 6:44 pm
How tall is the chimney?
27' from thimble to top of chimney. What does that tell you?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Feb. 28, 2018 7:37 pm

brandonh98 wrote:
Wed. Feb. 28, 2018 7:35 pm
27' from thimble to top of chimney. What does that tell you?
At 27' tall it should draft like a champ.

 
User avatar
coaledsweat
Site Moderator
Posts: 13761
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Feb. 28, 2018 7:40 pm

brandonh98 wrote:
Wed. Feb. 28, 2018 7:35 pm
27' from thimble to top of chimney. What does that tell you?
It tells me "toss the cap."

 
User avatar
Lightning
Site Moderator
Posts: 14652
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Wed. Feb. 28, 2018 7:42 pm

Do you have a manometer installed? What are your numbers?

 
User avatar
CoalJockey
Verified Business Rep.
Posts: 1324
Joined: Sun. Mar. 09, 2008 11:18 am
Location: Loysburg, PA
Stoker Coal Boiler: Several EFM 520 refurbs...one 900, one 1300 mega-stoker
Hand Fed Coal Stove: (2) Warm Morning Stoves

Post by CoalJockey » Wed. Feb. 28, 2018 7:47 pm

coaledsweat wrote:
Wed. Feb. 28, 2018 7:40 pm
It tells me "toss the cap."
100% agreed with CS Brandon. Back in the Fall, I was in your exact shoes as I tried to run an EFM through a liner and a cap just like that. It would pressurize the firebox and just wouldn’t breath. I later found out the liner was perforated when we pulled it out.

The difference is nothing short of dramatic. There are times it will stand the baro wide open... heaven forbid the Jack Russell dog walks by it, she will be up the pipe like a rocket!

 
User avatar
freetown fred
Member
Posts: 30292
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Wed. Feb. 28, 2018 7:52 pm

You're good with that B.
brandonh98 wrote:
Wed. Feb. 28, 2018 7:30 pm
Chimney would need to be 15 feet taller to be above the peak of the roof. There is nothing within 12' of the top of the chimney though. It's a long gently sloping roof.

 
brandonh98
Member
Posts: 84
Joined: Mon. Mar. 27, 2017 9:55 pm
Location: Drums, PA (NEPA)
Hot Air Coal Stoker Stove: Leisure Line Hyfire

Post by brandonh98 » Wed. Feb. 28, 2018 8:14 pm

Lightning wrote:
Wed. Feb. 28, 2018 7:42 pm
Do you have a manometer installed? What are your numbers?
Yes, on a cold day the dampener holds it right at 0.05 with the dampener only open slightly. When it gets above freezing it struggles to stay at 0.04. A warm day in the 40's it'll go down to 0.02 or 0.01. It's at this point I start to smell it and the CO detector starts giving a low reading (not alarming, maybe 10-30ppm).