I have read in several posts about installing a manometer to understand what exactly is happening in the flue and with the draft. The model I have seen most commonly suggested was the Dwyer. Since there was some great discussion about the Dwyer in other posts but not one exclusively for installing one I thought I'd create one. I plan on installing it this weekend. If I recall from the previous discussions that I'll end up hooking my hose to the low pressure side and even though my gauge will be reading a positive pressure it is actually a negative reading. I have some soft copper tubing (since the rubber hose would not withstand the heat) and some compression fittings to complete the install. I plan on inserting the copper tube a few inches above the baro at approximately where the white sticker is in the picture, but should it be installed below the baro?

Attachments

IMG_2594.JPG
.JPG | 666.5KB | IMG_2594.JPG
IMG_2595.JPG
.JPG | 596.9KB | IMG_2595.JPG
IMG_2596.JPG

Dwyer Mark II Model 25

.JPG | 763.4KB | IMG_2596.JPG


 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Nov. 24, 2017 4:26 pm

Yes, best case scenario is between the stove and baro. Instead of using the compression fittings, I would suggest just drilling a hole into the pipe the same size as the metal tubing so that it can be retracted easily. This way it's easy to check for any fly ash blockage of the probe, and to "zero" the manometer occasionally.

 
User avatar
tcalo
Member
Posts: 2068
Joined: Tue. Dec. 13, 2011 4:57 pm
Location: Long Island, New York
Baseburners & Antiques: Crawford 40
Coal Size/Type: Nut/stove anthracite

Post by tcalo » Fri. Nov. 24, 2017 4:29 pm

Ideally it should be hooked up between the stove and any draft controls (baro, mpd). So it should go in this order: stove, mano, mpd, baro.

Attachments

IMG_3199.JPG
.JPG | 603.9KB | IMG_3199.JPG
IMG_3200.JPG
.JPG | 714.4KB | IMG_3200.JPG

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Fri. Nov. 24, 2017 4:52 pm

I would avoid a permanent install. The device needs to be zeroed frequently and you can't do that installed. I use a small hole and a piece of curved brake line on the hose.

 
User avatar
tcalo
Member
Posts: 2068
Joined: Tue. Dec. 13, 2011 4:57 pm
Location: Long Island, New York
Baseburners & Antiques: Crawford 40
Coal Size/Type: Nut/stove anthracite

Post by tcalo » Fri. Nov. 24, 2017 4:55 pm

coaledsweat wrote:
Fri. Nov. 24, 2017 4:52 pm
I would avoid a permanent install. The device needs to be zeroed frequently and you can't do that installed. I use a small hole and a piece of curved brake line on the hose.
I pull the rubber hose off the gauge side to zero it.

Attachments

IMG_3201.JPG
.JPG | 855.4KB | IMG_3201.JPG

 
Benny
Member
Posts: 374
Joined: Sat. Nov. 11, 2017 6:32 am
Location: Ligonier Pa.
Hot Air Coal Stoker Furnace: Koker lite- house. Reading- garage
Coal Size/Type: Rice
Other Heating: Oil

Post by Benny » Fri. Nov. 24, 2017 5:30 pm

Where did you find the best price? Thinking of getting one

 
brandonh98
Member
Posts: 84
Joined: Mon. Mar. 27, 2017 9:55 pm
Location: Drums, PA (NEPA)
Hot Air Coal Stoker Stove: Leisure Line Hyfire

Post by brandonh98 » Fri. Nov. 24, 2017 10:50 pm

Benny wrote:
Fri. Nov. 24, 2017 5:30 pm
Where did you find the best price? Thinking of getting one
EBay


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Nov. 25, 2017 6:27 am


 
User avatar
WNY
Member
Posts: 6307
Joined: Mon. Nov. 14, 2005 8:40 am
Location: Cuba, NY
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Contact:

Post by WNY » Sat. Nov. 25, 2017 7:22 am

Just be careful filling it. it's REALLY touchy. only put a little bit of fluid in at a time. make sure you screw out the zero knob about 3-4 turn to adjust for Zero when filling it.

They can be found on ColePalmer, Ebay, Amazon, usually around $30-40 range. sometimes a little cheaper.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Nov. 25, 2017 7:37 am

I have one that is calibrated in Pascals also, but I have not installed it anywhere yet. My boiler still has the one calibrated in inches.

The Pascal scale is far more intuitively useful for the draft range we generally target.

5 Pascals = 0.02" water column
10 Pascals = 0.04" water column (this is the target most seem to shoot for)
15 Pascals = 0.06" water column
20 Pascals = 0.08" water column
25 Pascals = 0.10" water column
etc...

It's model # is MARK II M-700PA. Sans for the scale markings it is otherwise identical in every way to the "standard" Dwyer Mark II.

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Sat. Nov. 25, 2017 8:23 am

WNY wrote:
Sat. Nov. 25, 2017 7:22 am
Just be careful filling it. it's REALLY touchy. only put a little bit of fluid in at a time. make sure you screw out the zero knob about 3-4 turn to adjust for Zero when filling it.

They can be found on ColePalmer, Ebay, Amazon, usually around $30-40 range. sometimes a little cheaper.
OR, buy a Magnehelic gauge instead... no liquid to mess with....easy

 
Kramer1782
Member
Posts: 22
Joined: Tue. Jan. 24, 2017 9:14 pm
Location: Trout Run PA
Hot Air Coal Stoker Stove: Harman Magnum
Coal Size/Type: Rice
Other Heating: Electric baseboards (Utilized as backup)

Post by Kramer1782 » Sun. Nov. 26, 2017 11:04 pm

Got the unit installed today and it was pretty easy. I mounted and filled it per the included instructions and then installed the soft copper tubing. I inserted the tubing below the baro as tcalo suggested. I also opted to not have the permanent install into the flue pipe as coaledsweat suggested to see how I liked it for cleaning purposes. I was originally concerned about a lose connection with just inserting the tube into the pipe, thus the permanent connection. However there was a hole through the steel of the stove already that provided a sufficient mounting location and provided a secure fitting. Also filling the unit is touchy just as WNY suggested. I purchased my unit in amazon and it was about 40 bucks. Total install took about 15 minutes. I have not adjusted the baro since the install. When I fully opened the baro with my hand when the stove was on the draft dropped almost to 0. I plan on looking for a manual online for the Harman since I didn't get one with the house and attempt to determine what they reccomend my draft setting be at. When I first installed the baro when I replaced all the stove pipe I initially set it at 2 and started the stove up keeping a close eye on it. My Co detector went off and got up to 300 ppm before I got the windows open and some fans going. I then adjusted it to 6 and haven't had any Co readings since. I appreciate the guidance and the pictures they were helpful for my install. I'll post what the manual says my draft should be and if I need to make any adjustments. Also I look forward to any suggestions. Thanks.

Attachments

IMG_2625.JPG

Installed soft copper tubing with baro above and facing the opposite direction.

.JPG | 752KB | IMG_2625.JPG
IMG_2626.JPG

Copper tube to rubber hose compression fitting.

.JPG | 623.9KB | IMG_2626.JPG
IMG_2627.JPG

Mounting the unit on the wall. Ensure it's level.

.JPG | 552KB | IMG_2627.JPG
IMG_2628.JPG

Filling the unit with fluid.

.JPG | 575.6KB | IMG_2628.JPG
IMG_2629.JPG

Zeroing the unit.

.JPG | 600.7KB | IMG_2629.JPG
IMG_2631.JPG

0.04 with the stove running.

.JPG | 640.7KB | IMG_2631.JPG
IMG_2632.JPG

Rubber hose gets installed on the low pressure side.

.JPG | 551.1KB | IMG_2632.JPG
IMG_2633.JPG

Overview of the whole install.

.JPG | 619.6KB | IMG_2633.JPG
IMG_2635.JPG

0.03 with the stove fans off.

.JPG | 687.1KB | IMG_2635.JPG
IMG_2638.JPG

Current baro setting is at 6 so I'm assuming 0.06?

.JPG | 428.8KB | IMG_2638.JPG

 
Kramer1782
Member
Posts: 22
Joined: Tue. Jan. 24, 2017 9:14 pm
Location: Trout Run PA
Hot Air Coal Stoker Stove: Harman Magnum
Coal Size/Type: Rice
Other Heating: Electric baseboards (Utilized as backup)

Post by Kramer1782 » Sun. Nov. 26, 2017 11:49 pm

Manometer Install

I was browsing the site and discovering many other nuggets of great information. I came across this post from 2007 though I didn't see it when I searched for manometer or Dwyer in the site search function. Either way I thought I'd post it here as it's relevant to the conversation.

 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Mon. Nov. 27, 2017 5:04 am

Kramer1782 wrote:
Sun. Nov. 26, 2017 11:04 pm
I was originally concerned about a lose connection with just inserting the tube into the pipe, thus the permanent connection.
The connection at the pipe doesn't need to be completely air tight. A hole just big enough for the probe to get thru is sufficient.

 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Mon. Nov. 27, 2017 5:15 am

Kramer1782 wrote:
Sun. Nov. 26, 2017 11:04 pm
When I first installed the baro when I replaced all the stove pipe I initially set it at 2 and started the stove up keeping a close eye on it. My Co detector went off and got up to 300 ppm before I got the windows open and some fans going. I then adjusted it to 6 and haven't had any Co readings since.
Personally I don't think the draft failure and the baro set at -.02 are related. Maybe it was warm outside that day? Having the baro set at -.06 is a little bit high. The center of the weight corresponds with the value it's set at, like you have it.

Nice job with the install ;)