Setting the Feed rate on Coal-Trol When Lighting Stove

Post Reply
 
User avatar
StanT
Member
Posts: 261
Joined: Fri. Aug. 29, 2008 5:10 am
Location: Ne Pa

Post by StanT » Sun. Apr. 23, 2017 7:19 am

When my stove is shut down for cleaning and I start it back up the feed rate is always over 90. Is there a way to reset this or lower it as I get a full grate of fire when I light it.

Help Please.

Thanks, Stant


 
User avatar
pvolcko
Verified Business Rep.
Posts: 1063
Joined: Mon. Jan. 16, 2006 4:26 pm
Location: Syracuse, NY
Contact:

Post by pvolcko » Mon. Apr. 24, 2017 9:28 am

When you're cleaning it set the setpoint a bit below room temp, this will keep it from ramping up while it is out of service.

If you have a thermostat with V4 009 or higher version of the firmware there is also a feature to reset the FR logic. Go to the FR screen, press and hold the down button for 15 seconds. The FR will reset to a low value (maybe not 0 depending on where your setpoint is vs room temp).