Connecting 6" Stove Pipe to 5" SS Chimney Liner

Post Reply
brandonh98
Member
Posts: 48
Joined: Mon. Mar. 27, 2017 9:55 pm
Hot Air Coal Stoker Stove: Leisure Line Hyfire
Location: Drums, PA (NEPA)

Post Mon. Mar. 27, 2017 10:10 pm

Hi everyone,

I've been reading topics on this forum for months and finally have a question that I can't already find an answer to.

This week I purchased my first coal stove (Leisure Line Hyfire) and I'm currently in the process of hooking it up. I'm trying to figure out the best way to connect the 6" stove pipe to the 5" chimney liner. The 6" stove pipe fits nicely inside the thimble and there is roughly a 1/4" gap between the outside of the liner and the inside of the stove pipe. After numerous trips to lowes and online searching I cannot find any sort of adapter for this.

Some things to note, I'm not sure if the chimney liner is a full liner or just a short piece at the thimble. The snow just melted off the roof so I plan on getting up there this weekend and pull the cap off the chimney. House was built in 95 so I can't figure out why there would be a liner in there already? Pictures are worth 1000 words. I'm out of town this week but if it would be helpful I can post pics on Friday.

This site is awesome and thank you in advance for any input.

-Brandon

User avatar
freetown fred
Member
Posts: 21653
Joined: Thu. Dec. 31, 2009 12:33 pm
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut
Location: Freetown,NY 13803

Post Mon. Mar. 27, 2017 10:25 pm

Check chimney condition--if it looks OK-pull the liner--5" liner??????????????/ never heard that one. UNLESS, they had something weird hooked up. Pellet stove, etc.

User avatar
McGiever
Member
Posts: 6084
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Mon. Mar. 27, 2017 10:35 pm

Look to http://www.northlineexpress.com for your connector.

https://www.northlineexpress.com/5-duraflexss-connector-5dfs-fc-6434.html

https://www.northlineexpress.com/6-duraflexss-connector-6dfs-fc-6570.html

:idea: Shoot a video with your smart phone lowered down the chimney while being very securely tied. :idea:

brandonh98
Member
Posts: 48
Joined: Mon. Mar. 27, 2017 9:55 pm
Hot Air Coal Stoker Stove: Leisure Line Hyfire
Location: Drums, PA (NEPA)

Post Mon. Mar. 27, 2017 10:57 pm

freetown fred wrote:Check chimney condition--if it looks OK-pull the liner--5" liner??????????????/ never heard that one. UNLESS, they had something weird hooked up. Pellet stove, etc.
There was a large propane heater hooked up when I moved into the house.

brandonh98
Member
Posts: 48
Joined: Mon. Mar. 27, 2017 9:55 pm
Hot Air Coal Stoker Stove: Leisure Line Hyfire
Location: Drums, PA (NEPA)

Post Mon. Mar. 27, 2017 10:59 pm

McGiever wrote:Look to http://www.northlineexpress.com for your connector.

https://www.northlineexpress.com/5-duraflexss-connector-5dfs-fc-6434.html

https://www.northlineexpress.com/6-duraflexss-connector-6dfs-fc-6570.html

:idea: Shoot a video with your smart phone lowered down the chimney while being very securely tied. :idea:
Thank you for the links and the smartphone idea. That first connector may be exactly what I need.


User avatar
freetown fred
Member
Posts: 21653
Joined: Thu. Dec. 31, 2009 12:33 pm
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut
Location: Freetown,NY 13803

Post Tue. Mar. 28, 2017 12:17 am

If the chimney looks good, I WOULD pull the liner--they tend to deteriorate over time. I know the reducer is a quick fix, but quick is rarely the best!!!

User avatar
davidmcbeth3
Member
Posts: 5573
Joined: Sun. Jun. 14, 2009 2:31 pm
Coal Size/Type: nut/pea/anthra
Stove/Furnace Make: Hitzer
Stove/Furnace Model: 503

Post Tue. Mar. 28, 2017 1:39 am

freetown fred wrote:Check chimney condition--if it looks OK-pull the liner--5" liner??????????????/ never heard that one. UNLESS, they had something weird hooked up. Pellet stove, etc.
Or pull the 5" and replace with 6".

Or check with the stove manufacturer and get their opinion on constricting the piping, if you have not checked already.

Always a little bit leery of not going by what the manufacturer says is OK.

If manufacturer says "go for it" then there's some piece of mind there.

User avatar
coaledsweat
Site Moderator
Posts: 9922
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Tue. Mar. 28, 2017 7:33 am

Whether you go up a size or not, a HVAC supply house should be able to hand you a thimble adapter to fit the thimble to the stovepipe. I always use one, they seem to fit better than stovepipe.

brandonh98
Member
Posts: 48
Joined: Mon. Mar. 27, 2017 9:55 pm
Hot Air Coal Stoker Stove: Leisure Line Hyfire
Location: Drums, PA (NEPA)

Post Thu. Mar. 30, 2017 8:32 pm

freetown fred wrote:Check chimney condition--if it looks OK-pull the liner--5" liner??????????????/ never heard that one. UNLESS, they had something weird hooked up. Pellet stove, etc.
I took your advice and removed to liner. Chimney is in perfect condition.

Thanks again

User avatar
freetown fred
Member
Posts: 21653
Joined: Thu. Dec. 31, 2009 12:33 pm
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut
Location: Freetown,NY 13803

Post Thu. Mar. 30, 2017 8:53 pm

Nice, ya hooked up yet?


brandonh98
Member
Posts: 48
Joined: Mon. Mar. 27, 2017 9:55 pm
Hot Air Coal Stoker Stove: Leisure Line Hyfire
Location: Drums, PA (NEPA)

Post Thu. Mar. 30, 2017 11:27 pm

Yes sir. The six inch stove pipe fits perfectly inside the thimble, so without having to worry about sealing around the liner we are good to go.

User avatar
freetown fred
Member
Posts: 21653
Joined: Thu. Dec. 31, 2009 12:33 pm
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut
Location: Freetown,NY 13803

Post Fri. Mar. 31, 2017 6:58 am

Outstanding. Lookin fwd to some pix

CapeCoaler
Member
Posts: 4469
Joined: Sun. Feb. 10, 2008 3:48 pm
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove
Location: Cape Cod, MA

Post Fri. Mar. 31, 2017 12:23 pm

If it was for propane heater that 'liner' might have been 'b-vent'...
That is usually only for propane and gas...

User avatar
freetown fred
Member
Posts: 21653
Joined: Thu. Dec. 31, 2009 12:33 pm
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut
Location: Freetown,NY 13803

Post Fri. Mar. 31, 2017 12:25 pm

Or not. ;)