Puffback Blew Pipe Off of Chimney and Stove

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 12:20 pm

Was loading our Harman MkIII last night, experimenting with a mix of pea and nut. Made a mistake -- let the flames go out which, as expected, resulted in a puffback. My fault, I know. Lesson learned.

The problem is, this puffback blew the pipe off of the stove/chimney. Evacuated the family and pets, called the fire department who shut down the stove and vented the house. Assessing the "damage" today, and I discovered that the chimney pipe was not secured to the stove, and the flue collar was not secured to the masonry behind the stove. Also, the pipe was not secured to the elbow coming out of the stove, so when the gasses lit, it blew the flue collar out of the wall and the pipe from the stove. Pipe has 2 screws (not 3) securing it to the collar.

Thing is, we had the chimney/stove inspected in fall and they replaced the pipe.

Should all sections of the pipe be fastened? I can, without much effort, remove the pipe/flue collar from the wall and stove. This doesn't seem right. I'm about ready to call the company and give them a piece of my mind, but figured I'd get a sanity check first.
Last edited by gbru316 on Tue. Mar. 14, 2017 12:42 pm, edited 1 time in total.


 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Tue. Mar. 14, 2017 12:25 pm

All connections should have 3 screws securing them at each joint.

 
User avatar
freetown fred
Member
Posts: 30292
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Tue. Mar. 14, 2017 12:26 pm

You betcha ALL sections should be.

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 12:32 pm

Thanks guys, thats what I thought.

What about the flue collar/chimney adapter? Should that be secured to the wall? There are predrilled holes in the collar that look like they're supposed to be used for mounting hardware.
Last edited by gbru316 on Tue. Mar. 14, 2017 12:42 pm, edited 1 time in total.

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 12:41 pm

Pictures:
IMG_20170314_123714.jpg
.JPG | 105.2KB | IMG_20170314_123714.jpg
IMG_20170314_123749.jpg
.JPG | 83.5KB | IMG_20170314_123749.jpg
IMG_20170314_123733.jpg
.JPG | 105.5KB | IMG_20170314_123733.jpg
IMG_20170314_123721.jpg
.JPG | 122.6KB | IMG_20170314_123721.jpg

 
User avatar
Sunny Boy
Member
Posts: 25517
Joined: Mon. Nov. 11, 2013 1:40 pm
Location: Central NY
Hand Fed Coal Boiler: Anthracite Industrial, domestic hot water heater
Baseburners & Antiques: Glenwood range 208, # 6 base heater, 2 Modern Oak 118.
Coal Size/Type: Nuts !
Other Heating: Oil &electric plenum furnace

Post by Sunny Boy » Tue. Mar. 14, 2017 12:47 pm

gbru316 wrote:Thanks guys, thats what I thought.

What about the flue collar/chimney adapter? Should that be secured to the wall? There are predrilled holes in the collar that look like they're supposed to be used for mounting hardware.
That's why the holes are put there. ;)

Paul

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 12:53 pm

Sunny Boy wrote:
gbru316 wrote:Thanks guys, thats what I thought.

What about the flue collar/chimney adapter? Should that be secured to the wall? There are predrilled holes in the collar that look like they're supposed to be used for mounting hardware.
That's why the holes are put there. ;)

Paul
lol that's what my thought was, but since this is only my second season with stoves in general, I wasn't sure if there were acceptable deviations.

They're sending someone out first thing tomorrow morning to fix everything and they're going to talk to their insurance company about the carpet. I plan on staying home from work to "supervise" given that they dropped the ball so spectacularly the first time around.

Is there a guide that shows/explains exactly how the stove should be connected to the chimney? Attachment points, types of fasteners, etc? I'd prefer to know exactly what needs done tomorrow to make everything safe so it's not the blind leading the blind.


 
User avatar
freetown fred
Member
Posts: 30292
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Tue. Mar. 14, 2017 1:10 pm

Welcome to the BIG puff back club G.

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 1:21 pm

freetown fred wrote:Welcome to the BIG puff back club G.
Maybe I can use it as leverage to convince my wife to buy a stoker ;)

 
User avatar
Rob R.
Site Moderator
Posts: 17965
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Tue. Mar. 14, 2017 1:43 pm

It appears to me that the elbow came apart at the seam. Unless the pipe needs to be mounted at a funny angle, I would use a tee or a non-adjustable elbow at that location.

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 2:09 pm

Rob R. wrote:It appears to me that the elbow came apart at the seam. Unless the pipe needs to be mounted at a funny angle, I would use a tee or a non-adjustable elbow at that location.
Thanks, this is why I posted :-)

I'll ask the guy if this is an option.

 
coalnewbie
Member
Posts: 8601
Joined: Sat. May. 24, 2008 4:26 pm
Location: Chester, NY
Hot Air Coal Stoker Stove: LL AnthraKing 180K, Pocono110K,KStokr 90K, DVC
Hand Fed Coal Stove: Invader 2
Baseburners & Antiques: Wings Best, Glenwood #8(x2) Herald 116x
Coal Size/Type: Rice,
Other Heating: Heating Oil CH, Toyotomi OM 22

Post by coalnewbie » Tue. Mar. 14, 2017 2:27 pm

http://www.midlandhardware.com/631796.html?gclid=CJzhxPLO1tICFQhWDQodeLkHtA

and screwed in three places both ends. I agree with Rob, the elbow opened up. Forget the stoker, just use that great stove properly. The school of experience is the best. Its just that the fees are high. You will never do that again. :)
I'll ask the guy if this is an option.
Do it yourself the guy is an idiot.

 
gbru316
Member
Posts: 93
Joined: Wed. Feb. 10, 2016 10:55 pm
Hand Fed Coal Stove: Harman Mk III
Other Heating: Oil forced air

Post by gbru316 » Tue. Mar. 14, 2017 2:43 pm

coalnewbie wrote:http://www.midlandhardware.com/631796.html?gclid=CJzhxPLO1tICFQhWDQodeLkHtA

and screwed in three places both ends. I agree with Rob, the elbow opened up. Forget the stoker, just use that great stove properly. The school of experience is the best. Its just that the fees are high. You will never do that again. :)
I'll ask the guy if this is an option.
Do it yourself the guy is an idiot.
You're damn right I'll never do that again :D

Agree that guy is an idiot, but he said there'd be no charge to make the repairs. He specifically asked me what I wanted done, and I said "make it safe." So long as he's receptive to my guidance, why would I stop him from doing the work and paying for it?

Also, my 1 year old CO detector never went off. Max reading in the room with the stove was > 300 ppm per fire department. Detector displayed a max reading of 267 ppm when I regained access. Kind of scary that the stove could be directly venting to the house and I'd be unaware of it for a significant period of time.

I know they design delays into CO detectors to avoid false alarms (this one says 150 ppm for 10-50 minutes), but there's gotta be one that is a bit more "trigger happy," preferable with a digital display so that I can decide if there's an issue or not. Any recommendations?

 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Tue. Mar. 14, 2017 2:49 pm

Rob R. wrote:It appears to me that the elbow came apart at the seam. Unless the pipe needs to be mounted at a funny angle, I would use a tee or a non-adjustable elbow at that location.
Good call on strong replacement parts, I also would use 22 gauge as well.

 
waldo lemieux
Member
Posts: 2270
Joined: Sun. Sep. 30, 2012 8:20 pm
Location: Ithaca,NY

Post by waldo lemieux » Tue. Mar. 14, 2017 2:52 pm

Gee I don't know.... Looks like all the joints are screwed to me. The thing blew apart the 90. Ya cant fault anybody for that :gee: Too, with that much pipe into the chimney and it still blew out.... I don't think Id be ready to label the guy an idiot, and he did offer to come and fix it.


Post Reply