I need to know if I am on the right track, with interconnecting my KAA-2 and furnace blower together? In the triple aquastat there are the 2 terminals for the stat. If run a single wire from 1 terminal to the blower circuit on my furnace, when the stat. calls for heat and completes the circuit it should start the blower right?


User avatar
McGiever
Member
Posts: 6068
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sat. Jan. 28, 2017 7:57 pm

Most of the time the furnace blower is already on a 24 volt relay, so use the coal thermostat to start and stop the blower as well.