Same Flue for Oil and Coal Boilers???

This forum is for common products and questions such as chimney installations, CO detectors, coal bin designs and a variety of other general topics that do not fit into the other forums.
User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Sun. Jun. 01, 2008 5:10 am

wannabwarm wrote:Reading all your input has been a great learning exp for me. While we are on the subject is there any problem with having two coal fired units with 6" flues connected to the same 8" SS chimney?
Legally, I'm not sure, physically, the math says that 8" is not twice the area of two 6"....almost, but not. It's about 15% shy of being double the area. Two 6's would be 56.5 sq inches vrs 50 sq inches for one 8". Maybe you could get away with it, maybe you'd asphyxiate yourself.
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

syncmaster
Member
Posts: 300
Joined: Sat. Apr. 19, 2008 1:29 pm
Stoker Coal Boiler: harmanVF3000 Coal/oil option
Coal Size/Type: Rice
Stove/Furnace Make: VF3000
Stove/Furnace Model: Harman VF3000
Location: long Island,NY

Post Sun. Jun. 01, 2008 9:32 am

wannabwarm wrote: asphyxiate yourself.
Hey Feddy, watch you language !!!!


User avatar
LsFarm
Member
Posts: 7385
Joined: Sun. Nov. 20, 2005 8:02 pm
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland
Location: Michigan

Post Sun. Jun. 01, 2008 12:04 pm

Other than the 'code' issue and insurance coverage in a loss, there is one issue not discussed so far.

Every year on the forum we have some folks with draft problems.. expecially with hand fired stoves/boilers/furnaces that rely on the chimney draft to pull air through the fire. The boilers or furnaces that have fan-forced combustion air don't have this problem.. We often have people stuggling to get a fire to burn well because of poor draft, draft leaks in the stove, hand dampers set wrong, or other ' draft stealers'.

So if you have two appliances hooked to a common chimney,, you need to assess how much 'leakage' of draft [chimney vacuum] there will be through the unused appliance. If there is an automatic damper on the unused appliance blocking it's flue, then this will not be an issue.

A tall 8x8 inside chimney that can pull .05" + draft will do fine But an accurate measurement of the draft with a fire going is going to be needed..

Greg L

.
Burning Pea/Buckwheat through an antique stoker [semi retired SSboiler],
Running an Axeman-Anderson 260M boiler burning Pea, About 150-250#per day
Farming, Fixing, Fabricating and Flying: 'spare time' what's that?