Coal-trol Thermostat Seems to Be 3-4 Degrees Off My Regular Thermostats

This forum is for common products and questions such as chimney installations, CO detectors, coal bin designs and a variety of other general topics that do not fit into the other forums.
xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Wed. Dec. 14, 2016 7:40 pm

My coaltrol thermostat seems to be 3-4 degrees off my regular thermostats. This is making it difficult to actually get the desired temperature in my house. Today I came home to my entire house being less than 67 degrees when the coaltrol was set at 71 and the temp was 72 on the thermostat. I even checked this to a thermostat right beside it, my thermostat was reading 67. I know the coaltrol has an adjusted setting, and on mine I can not access the biased ratio. I tried resetting but it didn't change anything with the adjusted temp.


Olllotj
Member
Posts: 411
Joined: Thu. Sep. 04, 2014 10:01 am
Stoker Coal Boiler: Keystoker KB-8
Coal Size/Type: Buckwheat
Other Heating: Utica Propane Hot Water Baseboard
Location: Western NY

Post Wed. Dec. 14, 2016 7:43 pm

Just turn it up by 3 deg

xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Wed. Dec. 14, 2016 7:45 pm

I have tried that, it ends up reaching that temp with no problem while the rest of the house is still not at the correct temp then starts to back off feed, it holds temp on that thermostat for a really long time, when it should actually be calling for heat. It just doesn't seem like it is actually reading temperature and temperate change correctly.

User avatar
windyhill4.2
Member
Posts: 5022
Joined: Fri. Nov. 22, 2013 2:17 pm
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both
Location: Jonestown,Pa.17038

Post Wed. Dec. 14, 2016 7:51 pm

Are you saying that if you set the coaltrol for 75* it will still only go to 67* ?
David **** John14:6 Jesus saith unto him,"I am the way.the truth,and the life;no man cometh unto the father,but by me." Wise men sought for Jesus when he was born,wise men still seek Jesus today. Seek & you shall find.

xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Wed. Dec. 14, 2016 7:59 pm

No, what seems to happen is, if I set it to say 75, the coaltrol thermostat seems to get up to 75 fairly quick, but then holds there for a while. This means it starts to back down the feed rate. The house starts dropping in temp, as I have seen first hand by looking at the other thermostats, but the coaltrol will still be reading 75, and feed rate continues to drop. Then it finally will drop a degree and it will start bumping up the feed rate, but at this point its behind a good bit then takes forever to catch back up, usually resulting in it being under temp in the mornings.

User avatar
WNY
Member
Posts: 5849
Joined: Mon. Nov. 14, 2005 8:40 am
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Stove/Furnace Make: Keystoker, LL & CoalTrol
Stove/Furnace Model: 90K, Hyfire I, VF3000 Soon
Location: Cuba, NY
Contact:

Post Wed. Dec. 14, 2016 8:15 pm

Make sure there is good airflow around the thermostat, make sure the hole on the top is not blocked. might depend on the location from the other thermostats?

Did you find the HLF setting?

it may be too far away from your heat source, your house cools down fast? coal take time to respond, sometimes you will get small temp swings.

There is a "compensation" or bias setting in the advanced setup to tweak the temperature up/down, mine was a couple degrees off from my Gas Furnace and other Digital thermostat.

Read thru the CoalTrol V3 Settings it explains all the settings.

Coal-Trol V3 Firmware Features
- Dave
Hyfire I & Keystoker 90K heating an 1890 Victorian
- Amsoil Authorized T1 Certified Dealer

User avatar
tsb
Member
Posts: 1798
Joined: Wed. Jul. 30, 2008 8:38 pm
Stoker Coal Boiler: Binford 2000
Hot Air Coal Stoker Stove: LL Pioneer top vent
Hand Fed Coal Stove: Saey Hanover II
Baseburners & Antiques: Grander Golden Oak , Glenwood # 6
Coal Size/Type: All of them
Location: Douglassville, Pa

Post Wed. Dec. 14, 2016 8:19 pm

As I recall, the control learns as it goes along. Maybe it just needs time to adjust. It's been a few years since I had mine running.
Coal -- It's not a hobby, It's an addiction.

User avatar
windyhill4.2
Member
Posts: 5022
Joined: Fri. Nov. 22, 2013 2:17 pm
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both
Location: Jonestown,Pa.17038

Post Wed. Dec. 14, 2016 8:22 pm

Sounds to me like the coaltrol is in the warmest room of the house
Try closing some registers near it & open the registers in the cool areas.
No matter what the name is on a thermostat,it can't tell room temp of a room 25' away.
David **** John14:6 Jesus saith unto him,"I am the way.the truth,and the life;no man cometh unto the father,but by me." Wise men sought for Jesus when he was born,wise men still seek Jesus today. Seek & you shall find.


xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Wed. Dec. 14, 2016 9:08 pm

WNY wrote:Make sure there is good airflow around the thermostat, make sure the hole on the top is not blocked. might depend on the location from the other thermostats?

Did you find the HLF setting?

it may be too far away from your heat source, your house cools down fast? coal take time to respond, sometimes you will get small temp swings.

There is a "compensation" or bias setting in the advanced setup to tweak the temperature up/down, mine was a couple degrees off from my Gas Furnace and other Digital thermostat.

Read thru the CoalTrol V3 Settings it explains all the settings.

Coal-Trol V3 Firmware Features
Mine does not have the bias setting in the advanced menu, I've checked through it multiple times.

xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Wed. Dec. 14, 2016 9:10 pm

windyhill4.2 wrote:Sounds to me like the coaltrol is in the warmest room of the house
Try closing some registers near it & open the registers in the cool areas.
No matter what the name is on a thermostat,it can't tell room temp of a room 25' away.
The register is closed in this room, its the dining room, which is the furthest room from the stove. I stuck one of my honeywell thermostats that I bought right beside it, its reading 70 degrees while the coaltroal is reading 73.

I have a thermostat in my living room, hallway and bedroom, plus I had an extra one that I use to check temps of different rooms.

Just checked it again, it is now showing 75, while the other honeywell is still 70

User avatar
Flyer5
Verified Business Rep.
Posts: 10382
Joined: Sun. Oct. 21, 2007 4:23 pm
Stoker Coal Boiler: Leisure Line WL110
Hot Air Coal Stoker Stove: Leisure Line Pioneer
Location: Montrose PA
Contact:

Post Tue. Dec. 20, 2016 8:50 am

xandrew245x wrote:
windyhill4.2 wrote:Sounds to me like the coaltrol is in the warmest room of the house
Try closing some registers near it & open the registers in the cool areas.
No matter what the name is on a thermostat,it can't tell room temp of a room 25' away.
The register is closed in this room, its the dining room, which is the furthest room from the stove. I stuck one of my honeywell thermostats that I bought right beside it, its reading 70 degrees while the coaltroal is reading 73.

I have a thermostat in my living room, hallway and bedroom, plus I had an extra one that I use to check temps of different rooms.

Just checked it again, it is now showing 75, while the other honeywell is still 70
There is a calibration in the advanced menu. The newer thermostats you just calibrate by tapping up or down till you get the correct temp. The older thermostats are done at TB 130 is default. Its in the manual.
http://www.leisurelinestove.com


You know when people say it was "better back in my day"?

They were right.

xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Tue. Dec. 20, 2016 6:38 pm

Flyer, I have looked through the entire advanced menu and haven't been able to change the adjusted temp. It seems to have balanced itself out a bit since I first posted, it seems to be only about 1 degree off now.

User avatar
WNY
Member
Posts: 5849
Joined: Mon. Nov. 14, 2005 8:40 am
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Stove/Furnace Make: Keystoker, LL & CoalTrol
Stove/Furnace Model: 90K, Hyfire I, VF3000 Soon
Location: Cuba, NY
Contact:

Post Tue. Dec. 20, 2016 6:44 pm

Depending on the software version , once your in the bias setting, you tap the up or down like 5 times to change 1 degree, so it's pretty sensitive and you have try a few taps, let it calibrate and settle out, and then check it.
- Dave
Hyfire I & Keystoker 90K heating an 1890 Victorian
- Amsoil Authorized T1 Certified Dealer

xandrew245x
Member
Posts: 505
Joined: Sat. Nov. 24, 2012 2:26 pm
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace
Location: Gardners, PA

Post Tue. Dec. 20, 2016 6:46 pm

Yep just figured that out, you have to press it 5 times to get what degree changes, I got it solved now. Thanks guys!

User avatar
WNY
Member
Posts: 5849
Joined: Mon. Nov. 14, 2005 8:40 am
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Stove/Furnace Make: Keystoker, LL & CoalTrol
Stove/Furnace Model: 90K, Hyfire I, VF3000 Soon
Location: Cuba, NY
Contact:

Post Tue. Dec. 20, 2016 6:46 pm

I totally forgot about that until now! glad you figure it out at the same time! LOL
- Dave
Hyfire I & Keystoker 90K heating an 1890 Victorian
- Amsoil Authorized T1 Certified Dealer