What they are saying is correct...cannot have 2 different source 24volt transformers fighting each other...that is what you have. Humming!!!hotblast1357 wrote:New problem
so this is where I have the t'stat wires going to my furnace to turn on just the fan while also turning on the pump. If I unhook the t'stat wires from the fan, then the pump works correctly with the relay, and if I unhook the t'stat wires from the pump relay the fan comes on correctly, but if I have them both hooked up things start humming. Obviously something is back feeding on the 24 volt side, is there some other place I can run my TT wires in this diagram that will allow only my fan to come on?
You will need the 4th relay.
Furnace fan needs the furnace 24volts transformer's cicuit switched thru the 4th relay. But just the G wire.