Wiring a Heat Exchanger and Modine and Pump.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Sep. 26, 2015 2:34 am

hotblast1357 wrote:New problem

so this is where I have the t'stat wires going to my furnace to turn on just the fan while also turning on the pump. If I unhook the t'stat wires from the fan, then the pump works correctly with the relay, and if I unhook the t'stat wires from the pump relay the fan comes on correctly, but if I have them both hooked up things start humming. Obviously something is back feeding on the 24 volt side, is there some other place I can run my TT wires in this diagram that will allow only my fan to come on?
What they are saying is correct...cannot have 2 different source 24volt transformers fighting each other...that is what you have. Humming!!!
You will need the 4th relay.

Furnace fan needs the furnace 24volts transformer's cicuit switched thru the 4th relay. But just the G wire.


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Sep. 26, 2015 6:52 pm

All done. everything is working correctly now, thanks too scott, the last pic is from my cell, using the MANYTHING app, I can now check in on the boiler from anywhere.

Attachments

image.jpeg
.JPEG | 123.7KB | image.jpeg
image.jpeg
.JPEG | 130.3KB | image.jpeg
image.png

this is a pic from my cell, using the MANYTHING app.

.PNG | 484.8KB | image.png

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Sep. 26, 2015 8:07 pm

Very nice. I am looking forward to hearing how the system works in the cold weather.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Sep. 26, 2015 8:45 pm

im looking forward too it also rob, I think its going to work very well compared to the hotblast furnace.. the hotblast performed great and was excellent on coal, but with this I have a lot more options and controls.

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Sat. Sep. 26, 2015 8:51 pm

Good job & just in time,cold weather is probably dropping in on you guys each morning now or will soon.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Sep. 26, 2015 8:52 pm

yes it is, had 37 here this morning, was 62 inside, wife was NOT HAPPY lol right now its 48 outside and 73 inside, much better.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Sep. 26, 2015 9:00 pm

Nice job H.B. I'm glad you got that all figured out. I couldn't tell what the heck was go'in on with those relays without being there and looking at them so I kept my mouth shut. Lucky we have a lot of people on this forum that have experience and knowledge they are willing to share.

-Don


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Sep. 26, 2015 9:07 pm

yes don im very thankful of the people on here, in the end it could of been done a lot easier with two pumps but I just didnt see the need for that much pump power when I didnt need it.

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Sat. Sep. 26, 2015 10:03 pm

hotblast1357 wrote:yes it is, had 37 here this morning, was 62 inside, wife was NOT HAPPY lol right now its 48 outside and 73 inside, much better.
We had 30* outside temp last yr. b4 we got ours fired,your wife should be very happy with you tomorrow a/m when the boiler is maintaining a comfortable temp in your house :)

 
User avatar
SWPaDon
Member
Posts: 9857
Joined: Sun. Nov. 24, 2013 12:05 pm
Location: Southwest Pa.
Hand Fed Coal Furnace: Clayton 1600M
Coal Size/Type: Bituminous
Other Heating: Oil furnace

Post by SWPaDon » Sat. Sep. 26, 2015 11:19 pm

Glad to hear you got the New Yorker up and running. :up:

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Sep. 27, 2015 6:17 am

thanks guys, yes very happy this morning, a little warmer out this morning, 39, but a nice 72 in the house, its suppose to get 73 today but I don't think it will with everything being so cold already.

 
waldo lemieux
Member
Posts: 2270
Joined: Sun. Sep. 30, 2012 8:20 pm
Location: Ithaca,NY

Post by waldo lemieux » Sun. Sep. 27, 2015 12:02 pm

Nice shootin SC :rambo: trouble shootin that is :D

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Sep. 27, 2015 12:07 pm

Others may benefit if you explain how you wired the RIB's and which model you used.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Sep. 27, 2015 12:50 pm

Yes rob I thought so also, tonight when I get home I will make a detailed wiring diagram on the laptop.

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Sun. Sep. 27, 2015 1:58 pm

That information is Top Secret :) You know what happens if it is leaked out? :lol: :lol:


Post Reply