Wiring a Heat Exchanger and Modine and Pump.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Aug. 26, 2015 5:11 am



 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Aug. 26, 2015 5:38 am

If I have a call for heat with the modine, will the power to the pump back feed to the oil furnace fan side and power it also?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Aug. 27, 2015 5:50 pm

Aren't you using the zone valves?

Zone valves can have "end switch" to operate the relay. But you want one dpst relay box per one zone.

Each relay will start the same pump on 1st pole and at the same time start the fan on the 2nd pole of that relay.

So , no, each fan has a separate contol relay and only that one fan will switch on for that one t'stat/relay/zone.

Those relays you showed are okay.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. Aug. 27, 2015 7:06 pm

No I am not using zone valves, just one pump.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Aug. 27, 2015 8:19 pm

hotblast1357 wrote:No I am not using zone valves, just one pump.
Two different t'stats one pump.
One pump two different fan coils...hmmm. :gee:

Need to make both t'stats work the one common relay for that pump.
Then use two "strap on" aquastats, one on each of the fan coils. They must close on temp rise to start and stop the fan motors.
Last edited by McGiever on Thu. Aug. 27, 2015 8:29 pm, edited 1 time in total.

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Thu. Aug. 27, 2015 8:27 pm

Two of those will work just fine :) Set both next to pump/boiler. A 14-2 and a thermostat wire will handle the Modine. The air handler,,, will take care of itself with a pair.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Aug. 28, 2015 5:24 am

McGiever wrote:
hotblast1357 wrote:No I am not using zone valves, just one pump.
Two different t'stats one pump.
One pump two different fan coils...hmmm. :gee:

Need to make both t'stats work the one common relay for that pump.
Then use two "strap on" aquastats, one on each of the fan coils. They must close on temp rise to start and stop the fan motors.
So what your saying is control the coil by the pump? When a t'stat calls it will kick the pump on, which will warm the pipes, allowing the snap disc or aquastat to make connection turning the fan on? How do I control the individual aquastat? Run the t'stat through it so even if the pipe is warm it has to see a sense from the t'stat?


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Aug. 28, 2015 5:25 am

Scottscoaled wrote:Two of those will work just fine :) Set both next to pump/boiler. A 14-2 and a thermostat wire will handle the Modine. The air handler,,, will take care of itself with a pair.
Scott, two of what will work fine? Aquastats?

The air handle will take of itself with a pair of what?

Sorry it's early lol

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Aug. 28, 2015 11:57 am

Apologies, that will not work for you.

Use Scott's way.
McGiever wrote:
hotblast1357 wrote:No I am not using zone valves, just one pump.
Two different t'stats one pump.
One pump two different fan coils...hmmm. :gee:

Need to make both t'stats work the one common relay for that pump.
Then use two "strap on" aquastats, one on each of the fan coils. They must close on temp rise to start and stop the fan motors.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Aug. 28, 2015 6:39 pm

So what is Scott's way? Lol

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Aug. 28, 2015 7:53 pm

Two relay boxes, one relay box gets 14-2 romex type NM and a 1/ pair 24v t'stat to modine. Fan power 120v and 24v to operate relay back at pump for relay coil for start of pump.
Second relay box gets 1/ pair 24v t'stat only, run to oil furnace fan for existing fan relay already there. And also must start local pump.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sat. Aug. 29, 2015 5:09 am

Ok let me ask ou this, I already ran 14-3 out to the modine from the dump zone aquastat, I just didn't use the ground cuz it's only two wires, that makes connection out at the modine for the fan to power, is there a way I can just tie into that from the relay instead of running another power wire out there?

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Sat. Aug. 29, 2015 7:26 am

Dump zone will go across TT for that "zone". Just like the T-stat. NO POWER.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Aug. 29, 2015 7:50 am

You must use 2 relay boxes, 1 per zone. Each t'stats pull in the appropriate magnetic coil.

Each relay will start the same pump on 1st pole/set of contacts and at the same time start the the appropriate fan on the 2nd pole/set of contacts of that relay.

So , no backfeed, each fan (2) has a separate contol relay and only that one fan will switch on for that one t'stat/relay/zone.

As Scottscoaled is saying...in order to use the modine as a dump you only need the dump zone a'stat to wire parallel (24v) with the modines 24v t'stat wires at the modine's relay box magnetic coil...no addition wire needs ran to the garage...it is done with extra/parallel 24v control at the relay box and the relay will use the same existing 120v wire for power out to the fan.

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Sat. Aug. 29, 2015 10:42 am

You could get it done with one phone call.