Amitrol hw indirect wh-41z is throwing cold water into my system. When we shut down the heating zones for the season our showers get cold. It appears the hot water supply from the top of the indirect gets dumped into the same pipe of my efm525 coil before going to the mixing valve. However, the cold water from the indirect makes the pipe cold. When I shut off the valve of the indirect hot water supply our showers go hot...thoughts?....am I not understanding the system or is it not functioning correctly? Dan
Attachments
Lets make sure we understand what your saying?
The hot out of the indirect goes to the inlet of the coil inside the EFM and then out to the faucets? Is that what your saying?
You should be able to have the outlet from the indirect go to your faucets not the inlet to the coil in the boiler. OR shut off the indirect and have the outlet from the coil go directly to your faucets.
Or did I completely blow it in my understanding of your system?
The hot out of the indirect goes to the inlet of the coil inside the EFM and then out to the faucets? Is that what your saying?
You should be able to have the outlet from the indirect go to your faucets not the inlet to the coil in the boiler. OR shut off the indirect and have the outlet from the coil go directly to your faucets.
Or did I completely blow it in my understanding of your system?
- Lightning
- Site Moderator
- Posts: 14659
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
For us to help, could you draw up a simple diagram of how the DHW is plumbed from where water enters the house to thru the boiler and indirect tank and finally to the faucet? Then just snap a picture of it and post it..
-
- Member
- Posts: 151
- Joined: Mon. Sep. 17, 2012 9:34 pm
- Stoker Coal Boiler: EFM 520
- Coal Size/Type: rice
If you look at the piping you will see the pipe labeled domestic out hot, this goes into the pipe coming out from my EFM Coil hot, thIs pipe feeds into the hot side of the mixing valve. The domestic hot coming out of my amitrol indirect, the pipe labeled hot is feeding cold water out of the indirect into the hot side of my mixing valve. When I shut off the valve of this pipe I get hot showers, others they are cold...does this mean my indirect isn't working properly?
- Rob R.
- Site Moderator
- Posts: 17980
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
Sounds like you shut off the zone to the indirect as well.When we shut down the heating zones for the season our showers get cold.
You mention the coil and the indirect...which one are you trying to use?
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Are you saying that you have hot water entering the "hot" side of the mixing valve (from the boiler), as well as hot water entering the "cold" side of the mixing valve (from the indirect tank)? The cold side should be receiving cold feed from your city water or well water line. The hot side should be receiving its feed from the indirect tank. And the indirect tank should be heated via a zone loop coming off of the boiler and going through the indirects internal coil.mcguirehg wrote:If you look at the piping you will see the pipe labeled domestic out hot, this goes into the pipe coming out from my EFM Coil hot, thIs pipe feeds into the hot side of the mixing valve. The domestic hot coming out of my amitrol indirect, the pipe labeled hot is feeding cold water out of the indirect into the hot side of my mixing valve. When I shut off the valve of this pipe I get hot showers, others they are cold...does this mean my indirect isn't working properly?
-
- Member
- Posts: 151
- Joined: Mon. Sep. 17, 2012 9:34 pm
- Stoker Coal Boiler: EFM 520
- Coal Size/Type: rice
If you look directly above the water auto fill valve that is the pipe coming from the top of the indirect, domestic hot water, that pipe feeds into the pipe above it ( EFM hot coil pipe) and this hot water feeds into the hot side of the mixing valve. The problem being the domestic hot water coming from the indirect isn't hot, but rather cold. I believe it should be hot, but isn't. As a result, I shut the pipe down with the ball valve and my hot water returns and showers are hot again. I'm beginning to think there is a problem with the indirect and not my settings resulting in the cold showers.
- Rob R.
- Site Moderator
- Posts: 17980
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
If the indirect is not maintaining temperature, either the control is not set properly, not functioning properly, or for some reason the boiler water can't circulate through the indirect. You are going to get lots of suggestions by asking the opinion of people that have never been in your boiler room. The problem HAS to be simple, because it is a simple system. Do some troubleshooting.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
How is the indirect receiving heat? Why is your indirect feeding the cold side of the mixing valve when it should be feeding the hot side?