Whole House Fan and Reversed Draft

This forum is for common products and questions such as chimney installations, CO detectors, coal bin designs and a variety of other general topics that do not fit into the other forums.
User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Tue. May. 13, 2014 3:05 pm

My wife cranked up the whole house fan yesterday without opening windows and fortunately at the time I was near the boiler room and in the basement, as I immediately noticed a sulfur odor, and when I checked I saw that the chimneys draft had reversed. By the time my wife had turned the fan off the digital CO meter in the boiler room was already reading 13. Chimney draft immediately returned to normal when she shut the whole house fan off. We opened all of the windows and doors at that point, and the CO detectors upstairs never rose above zero.

Lesson learned that if the whole house fan is running plenty of windows and screen doors need to be open on all levels so it doesn't reverse the draft of the chimney. In fact, I'm questioning if even then it will be wise to run the whole house fan.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.


User avatar
northernmainecoal
Member
Posts: 502
Joined: Wed. Jan. 22, 2014 8:33 am
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Hitzer 30-95
Baseburners & Antiques: Herald Baseheater #6
Coal Size/Type: Rice/Nut/Stove
Location: Aroostook County, Maine

Post Tue. May. 13, 2014 3:12 pm

Glad you were right there and everyone is safe!
What exactly is a whole house fan?
Rob

User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Tue. May. 13, 2014 3:25 pm

northernmainecoal wrote:Glad you were right there and everyone is safe!
What exactly is a whole house fan?
It's a louvered fan which exhausts into the attic and cools the whole house down. It's a substantial fan. The windows and screen doors were mostly closed because it was raining cats and dogs outside.

The reason why I was in the basement is that for 2 hours straight the tornado sirens were going off on our street (we live right across from the Township Hall) and also in the communities to both the north and south of us. When the warning was lifted my wife (who was also in the basement for 2 hours) immediately said "I'm going upstairs to turn the whole house fan on to cool it down in here", and I stayed behind in the basement as she went up and turned it on.
Last edited by lsayre on Tue. May. 13, 2014 3:55 pm, edited 2 times in total.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Tue. May. 13, 2014 3:32 pm

The manometer indicated draft was -0.03" to -0.04" and it reversed to +0.01" when the whole house fan was turned on.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

rberq
Member
Posts: 5013
Joined: Mon. Apr. 16, 2007 9:34 pm
Hand Fed Coal Stove: DS Machine 1300 with hopper
Coal Size/Type: Blaschak Anthracite Nut
Other Heating: Oil hot water radiators (fuel oil); propane
Location: Central Maine

Post Tue. May. 13, 2014 3:58 pm

I used to worry about running the clothes dryer for the same reason, though obviously it is a much smaller fan, so I would open the laundry room window. But apparently my house is so leaky that the draft was going OUT the window rather than in. No sick house syndrome here, just lots of fresh air. :o
Simple answers for simple minds.

User avatar
Rob R.
Site Moderator
Posts: 11348
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Tue. May. 13, 2014 4:26 pm

Larry, do you have a vent in the boiler room for make up air?

Also, do you have a cover made for that whole house fan so it doesn't "ventilate" your house in the winter?

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Tue. May. 13, 2014 4:34 pm

Rob R. wrote:Larry, do you have a vent in the boiler room for make up air?
Any vent of logical size to feed combustion air to an appliance would be vastly overwhelmed by a Whole House fan. Even a combination of [comparatively small] bath and stove fans can offset appliance draft. Many open windows is the only solution.
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
McGiever
Member
Posts: 6000
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Tue. May. 13, 2014 5:23 pm

It isn't pretty when a whole house fan is turned on in the winter with a open fireplace burning.
SLOW AND STEADY WINS THE RACE


User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Tue. May. 13, 2014 5:44 pm

Rob R. wrote:Larry, do you have a vent in the boiler room for make up air?

Also, do you have a cover made for that whole house fan so it doesn't "ventilate" your house in the winter?
I still need to get outside air into the boiler room. Right now it is wide open to the basement, but I would like to close it off from the basement.

The whole house fan has louvers that close when it isn't running. Perhaps I should cover the louvers up with plastic sheeting during the winter.
Last edited by lsayre on Tue. May. 13, 2014 8:23 pm, edited 1 time in total.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
Rob R.
Site Moderator
Posts: 11348
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Tue. May. 13, 2014 6:02 pm

Sting wrote:
Rob R. wrote:Larry, do you have a vent in the boiler room for make up air?
Any vent of logical size to feed combustion air to an appliance would be vastly overwhelmed by a Whole House fan. Even a combination of [comparatively small] bath and stove fans can offset appliance draft. Many open windows is the only solution.
Yep...but this still seemed like a good time to mention make up air.

User avatar
Rick 386
Member
Posts: 2474
Joined: Mon. Jan. 28, 2008 4:26 pm
Stoker Coal Boiler: AA 260 heating both sides of twin farmhouse
Hot Air Coal Stoker Stove: LL Hyfire II w/ coaltrol in garage
Coal Size/Type: Pea in AA 260, Rice in LL Hyfire II
Other Heating: Gas fired infared at work
Location: Royersford, Pa
Contact:

Post Tue. May. 13, 2014 7:22 pm

lsayre wrote:
I still need to get outside air into the boiler room. Right now it is wide open to the basement, but I would like to close it off from the basement...................................
Larry,

Can you seal off the basement door from the first floor ?? That way you can provide make up air in the basement for the boiler only. Sealing the door would prevent the draw extending into the basement. Or at least severely limit it.

Our old twin farmhouse has 2 doors open to the basement from inside each side of the upstairs and also 2 bilco doors on either end of the basement. They do not seal real tight either. We do run a large about 18" diameter fan in the 2nd floor window at the top of the stairs. We rarely see a backflow on the flue.

I have mentioned on here several times before that at my old shop whenever I would turn on the spraybooth fan, it would backdraft both the coal and oil burner flues. Only solution was to fully open the far shop window. And I was using a 24" fan attached to a 1/2 hp motor. Yeah it did draw some air !!!!!

Rick
Master of "Trial and Error."

User avatar
coalkirk
Member
Posts: 4679
Joined: Wed. May. 17, 2006 8:12 pm
Stoker Coal Boiler: 1981 EFM DF520
Coal Size/Type: anthracite/rice coal
Location: Forest Hill MD

Post Tue. May. 13, 2014 8:07 pm

lsayre wrote:In fact, I'm questioning if even then it will be wise to run the whole house fan.
I think you answered your own question. Whole house fans and combustion appliances don't play nice together.
You have enemies? Good. That means you've stood up for something, sometime in your life. Winston Churchill

"I would rather have a German division in front of me than a French one behind me." —General George S. Patton

Burning rice coal in a 1981 EFM DF520, nut coal in a hand fired Jotul 507.

User avatar
rubicondave33
Member
Posts: 310
Joined: Sat. Jan. 26, 2008 10:02 am
Stoker Coal Boiler: EFM DF520
Coal Size/Type: Rice/Anthracite
Stove/Furnace Make: efm
Stove/Furnace Model: DF520
Location: Indiana, PA

Post Tue. May. 13, 2014 8:16 pm

We ran a whole house fan for years (before I installed central air) with no issues. I have make up air for my boiler, and the boiler room has a door on it as well. The space where my whole house fan lived is now the return air for my air handling unit in the attic.

User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Tue. May. 13, 2014 8:22 pm

Rick 386 wrote:
Larry,

Can you seal off the basement door from the first floor ?? That way you can provide make up air in the basement for the boiler only. Sealing the door would prevent the draw extending into the basement. Or at least severely limit it.

Rick
I can shut the door at the top of the stairs coming up from the basement. With a window open in the basement, and windows open upstairs, and the door closed between the basement and the upstairs, it should bode better for the whole house fan.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Wed. May. 14, 2014 7:41 am

Rob R. wrote:Yep...but this still seemed like a good time to mention make up air.
and an excellent opportune moment , it was sir Image
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!