Losing Efficiency

Post Reply
 
prrgeo
New Member
Posts: 3
Joined: Thu. Jan. 23, 2014 2:13 pm
Hot Air Coal Stoker Furnace: Reading RSDB-06 Susquehanna
Coal Size/Type: Rice

Post by prrgeo » Thu. Jan. 23, 2014 2:36 pm

My Reading RSDB-06 hot air furnace is losing efficiency and can't keep up with the extreme cold here lately. It seems to me that the problem is that the cycles with the blower forcing air through the ducts are shorter than they used to be, so less heating for the house. Why? It is power vented and has had a fire going for about four months. Is the problem 1) buildup of ash within the furnace, reducing heat going to the plenum? 2)too much draft through the power vent, blowing useful heat outdoors? 3) air forced into the plenum by the blower fan, which is low on the cellar floor, too cold, cooling it too fast and shutting off the fan? 4) wrong settings or spread on the fan limit controller (although it used to work fine)? 5) just too darn cold right now? 6)none of the above? Any advice or experience would be appreciated. This is the sixth season with this unit.

 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Thu. Jan. 23, 2014 2:58 pm

I take it you don't have ducted cold air return?

Welcome to the coolest forum on the internet. .. :D

You can try changing your blower settings. Any of those things you listed could contribute to the shorter cycles.

 
User avatar
mariohotshot
Member
Posts: 114
Joined: Sun. Oct. 27, 2013 10:58 pm
Location: Blakeslee, PA

Post by mariohotshot » Thu. Jan. 23, 2014 5:39 pm

Where do you have you settings on the fan limit controller? Maybe you need to readjust them.


 
prrgeo
New Member
Posts: 3
Joined: Thu. Jan. 23, 2014 2:13 pm
Hot Air Coal Stoker Furnace: Reading RSDB-06 Susquehanna
Coal Size/Type: Rice

Post by prrgeo » Thu. Jan. 23, 2014 7:14 pm

Mariohotshot: Settings are 100-130. These are the factory settings - I have not changed them. George

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Jan. 23, 2014 7:20 pm

Maybe your stovepipe needs a good cleaning? It doesn't take a lot of ash in it to reduce output significantly.

 
samhill
Member
Posts: 12236
Joined: Thu. Mar. 13, 2008 10:29 am
Location: Linesville, Pa.
Hot Air Coal Stoker Furnace: keystoker 160
Hand Fed Coal Stove: hitzer 75 in garage

Post by samhill » Thu. Jan. 23, 2014 7:24 pm

How long is your vent pipe? I'd check to see if there was any flyash build-up, I can usually tell just by feeling the temp difference between the top & bottom of the horizontal run with my bare hand. With the low temps we have been having it will probably build up faster than normal.


 
waldo lemieux
Member
Posts: 2270
Joined: Sun. Sep. 30, 2012 8:20 pm
Location: Ithaca,NY

Post by waldo lemieux » Thu. Jan. 23, 2014 8:01 pm

Im thinking its time to clean the heat exchanger tubes . Sounds like build up to me....

 
prrgeo
New Member
Posts: 3
Joined: Thu. Jan. 23, 2014 2:13 pm
Hot Air Coal Stoker Furnace: Reading RSDB-06 Susquehanna
Coal Size/Type: Rice

Post by prrgeo » Tue. Jan. 28, 2014 1:39 pm

Thanks to everyone for their suggestions. George

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Tue. Jan. 28, 2014 2:14 pm

Sounds like it could be an 'all of the above' :)

After 4 months of burning, I'd say it's time to do a little maintenance and see what may be causing the issues...how many tons have you used so far?

since it would be the biggest safety issue, i'd start with checking the power vent and horizontal flue pipe for fly ash build up.

then check for ash build up inside the furnace impeding heat transfer.

after that see what your draft is reading to find out if you are sending heat out the flue

then check temps on stove and maybe adjust fan limit