Questions Concerning Smoke Pipe and Coal Usage

Gary1
Member
Posts: 55
Joined: Thu. Jul. 11, 2013 10:07 pm

Post Mon. Jan. 20, 2014 5:58 pm

I'm in the process of having a D S Machine kozy-King 400 funace installed in my basement and have a question about the smoke pipe. It would be approximately 4 feet in length, from the back of the furnace to the thimble, and have a rise of about 3 inches per foot. Would it be practical to have most of its 4 feet length double walled, to keep the high heat away from the ceiling floor joists which are about 15 inches above the smoke pipe, and still have a portion of the pipe single walled so that I can monitor its temperature? If so, how should it be configured? The first 2 feet from the back of the furnace double walled, then the next foot single walled, and the rest double walled again? Or the first 3 feet double walled and the last foot single walled?

My second question relates to coal usage. Due to its corrosive nature will it damage the copper flashing around my chimney over time? Thanks, and I look forward to your replies...Gary


User avatar
lsayre
Member
Posts: 12542
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Mon. Jan. 20, 2014 7:05 pm

I believe that any flue pipe that is within 18" of the ceiling must be double walled.

waldo lemieux
Member
Posts: 2265
Joined: Sun. Sep. 30, 2012 8:20 pm
Stove/Furnace Make: efm
Stove/Furnace Model: s-20
Location: Ithaca,NY

Post Mon. Jan. 20, 2014 7:13 pm

Just heat shield the floor joists with some sheet metal and take advantage of the heat thrown off the single wall pipe, its not like a wood flue where there is a danger of a chimney fire.

User avatar
michaelanthony
Member
Posts: 4060
Joined: Sat. Nov. 22, 2008 10:42 pm
Hand Fed Coal Stove: Vigilant 2310, gold marc box stove, vogelzang pot belly coat rack
Baseburners & Antiques: Home Sparkle 12
Coal Size/Type: Coal Contractor's stove, a little Kimmels 'nut
Other Heating: Very cold FHA oil furnace
Location: millinocket,me.
Contact:

Post Mon. Jan. 20, 2014 7:15 pm

I was 15 inches away from my ceiling joists so I installed a metal barrier with 1 inch spacers against the ceiling joist above the pipe and kept the pipe single wall. I wanted the radiant heat in my basement and not up the chimney!

sorry waldo, you're a faster typist

User avatar
lsayre
Member
Posts: 12542
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Mon. Jan. 20, 2014 7:39 pm

The heat shield answer is the best idea!

User avatar
2001Sierra
Member
Posts: 1850
Joined: Wed. May. 20, 2009 8:09 am
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34
Stove/Furnace Model: Keystoker 90 Chimney Vent
Location: Wynantskill NY, 10 miles from Albany

Post Mon. Jan. 20, 2014 8:12 pm

An answer to your flashing question. Over time the thin aluminum flashing they are selling does corrode a bit. I have changed my flashing twice in 33 years, once because I restacked the brick, and the second time because it actually corroded. The last time I thought I was doing a basic repoint andminor repair, and ended up replacing it all, had I known that before I started copper would of been used. When my final roof goes on (present one is 30 plus years, I will be installing copper. Both will outlast me :shock:
I also now coat the brick with a breathable water proofing, which is holding up well on the mortar joints, lot easier to go up with a brush a slap the clear on vs. repointing.

User avatar
carlherrnstein
Member
Posts: 970
Joined: Tue. Feb. 07, 2012 8:49 am
Hot Air Coal Stoker Stove: combustioneer model 77B
Coal Size/Type: pea stoker/Ohio bituminous
Location: Clarksburg, ohio

Post Tue. Jan. 21, 2014 7:51 am

Copper flashing? Wow your lucky, the only thing better than copper is lead flashing, that stuff is easy to work and lasts literally hundreds of years.

Copper holds up lot better than aluminum, I would say it would be fine, any ash should be rinsed off by melting snow or rain and wouldn't be there long enough to cause a problem.

User avatar
titleist1
Member
Posts: 4404
Joined: Wed. Nov. 14, 2007 4:06 pm
Hot Air Coal Stoker Stove: Harman Mag Stoker (old style) one in basement, one in workshop
Hand Fed Coal Stove: Harman Mark III on standby for long power outages
Coal Size/Type: Rice/Anthracite; Nut/Anthracite
Location: Cecil County, MD

Post Tue. Jan. 21, 2014 8:15 am

Regarding the copper, your flashing should be fine. I rigged a couple 14awg pieces of copper wire across the top of my stack to hold the chimney cap on two years ago. They crisscross the top of the chimney directly in line with the exhaust. I checked them a few weeks ago and they have not deteriorated at all.

The heat shield is the way to go. In the workshop used a piece of 8" flue pipe around the 6" and simply put 1" screws thru the 8" to space it away from the 6". The screws do not go into the 6", they just provide points for the 8" to sit on the 6" pipe.


User avatar
Berlin
Site Moderator
Posts: 1847
Joined: Thu. Feb. 09, 2006 1:25 pm
Hot Air Coal Stoker Furnace: Will-Burt Combustioneer 77B
Coal Size/Type: Ohio BITUMINOUS pea stoker coal
Location: Buffalo/Adirondacks, NY

Post Tue. Jan. 21, 2014 1:25 pm

carlherrnstein wrote:Copper flashing? Wow your lucky, the only thing better than copper is lead flashing, that stuff is easy to work and lasts literally hundreds of years.

Copper holds up lot better than aluminum, I would say it would be fine, any ash should be rinsed off by melting snow or rain and wouldn't be there long enough to cause a problem.
Copper is better than aluminum, but, anything that touches masonry should be lead. I use lead on everything. It will outlive your grandkids.

Gary1
Member
Posts: 55
Joined: Thu. Jul. 11, 2013 10:07 pm

Post Wed. Jan. 22, 2014 10:54 pm

Thanks to you all for your responses. I know a single walled pipe with a heat shield above it would be the easiest way out normally, but I have hot air and cold air return ductwork from my oil furnace in the way, so it wouln't be easy to install a shield. Also, I don't need the heat off a single walled pipe to heat my basement since I have over 80 feet of non-insulated ductwork that radiates heat and keeps my basement warm. The new furnace will be hooked into this ductwork. I like Titleist 1's idea of using an 8" pipe around an interior 6" pipe, held in place with 1" screws to maintain a 1" air gap. How do you seal the 1" gap at the end of the pipe that connects to the smoke collar of the furnace, with some type of metal cap? At any rate, I'm back to my original question which was how to configure a double walled pipe with a section that would be single walled so that I can monitor its heat output?

I'm glad to hear that coal usage won't ruin copper flashing. I know from forum postings that it will ruin galvanized and stainless steel flue pipes, so why don't they make copper flue pipes, or at least copper lined flue pipes? Is it because of cost?

User avatar
titleist1
Member
Posts: 4404
Joined: Wed. Nov. 14, 2007 4:06 pm
Hot Air Coal Stoker Stove: Harman Mag Stoker (old style) one in basement, one in workshop
Hand Fed Coal Stove: Harman Mark III on standby for long power outages
Coal Size/Type: Rice/Anthracite; Nut/Anthracite
Location: Cecil County, MD

Post Wed. Jan. 22, 2014 11:07 pm

Gary1 wrote: How do you seal the 1" gap at the end of the pipe that connects to the smoke collar of the furnace, with some type of metal cap?
You don't seal it at either end, you want air to flow through that space. Cut the 8" about 4 inches short of the 6" and leave a couple inches at each end exposing the 6" flue pipe.

As for monitoring temp in the flue pipe, you can get a barbeque probe thermometer and insert it into the flue pipe. You can thread those right into the pipe. The couple inches at the stove side should be enough to insert the thermometer. They are only $10 - $12 at big box stores.

Gary1
Member
Posts: 55
Joined: Thu. Jul. 11, 2013 10:07 pm

Post Wed. Jan. 22, 2014 11:19 pm

Thanks for the info Titleist1...Gary

smokerdude
Member
Posts: 104
Joined: Sat. Dec. 14, 2013 9:09 am
Hot Air Coal Stoker Stove: Keystoker 90 Alaska
Hand Fed Coal Furnace: DS Kozy King
Coal Size/Type: Nut and Rice
Location: Allenwood PA

Post Thu. Jan. 23, 2014 7:21 am

I think that Kozy king 400 takes an 8 inch pipe. Mine is a 300 and it takes a 7 incher.

Gary1
Member
Posts: 55
Joined: Thu. Jul. 11, 2013 10:07 pm

Post Thu. Jan. 23, 2014 8:22 am

Your right, smokerdude. The 400 does take an 8" pipe, so I'll need a 10" pipe around it. Both the 300 and 400 now use 8" pipes....Thanks, Gary

User avatar
coalder
Member
Posts: 1000
Joined: Mon. Dec. 16, 2013 1:48 pm
Hand Fed Coal Boiler: harman sf 160
Coal Size/Type: Nut
Other Heating: wood parlor stove
Location: somewhere high in the catskill mountains

Post Thu. Jan. 23, 2014 8:32 am

Code is 18" from top of stove pipe to any combustible. I would highly recommend a mantle shield as it meets code. I believe it' called the" home saver mantle shield" But I could be wrong. Other methods may work , but this product meets code and reduces clearance to 9".
JF