Can someone clue me in here. I am using a hydronic distribution assembly for my system, and it has the option of 2 wire zone valves. I'd like to add these to system so that I can add a thermostat to each floor (three in total). I've wired up the Taco 3 wire valves before, but I am not certain how to get the boiler and the circulator to kick on with this type of valve. So before I do something stupid, I am asking for someone to point me in the right direction.
Pete
Wiring a Two Wire Zone Valve
-
- Member
- Posts: 127
- Joined: Fri. Mar. 04, 2011 6:29 pm
- Location: Quakertown PA
- Stoker Coal Boiler: EFM
- Coal Size/Type: Rice
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
Pete, Taco makes a nice relay box that allows for 2-wire zone valves and circulator/stoker operation. You could do the same thing with a 24v power supply, thermostats, and relays, but that green Taco box on the wall is tough to beat for simplicity.
http://www.pexsupply.com/Taco-ZVC403-4-3-Zone-Val ... h-Priority?/
http://www.pexsupply.com/Taco-ZVC403-4-3-Zone-Val ... h-Priority?/
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
The 4 zone valve version of this Taco unit sure made my zone valve and circulator wiring job easy!
- dave brode
- Member
- Posts: 478
- Joined: Fri. Jan. 15, 2010 5:47 pm
- Location: Frostburg, Maryland [western]
- Stoker Coal Boiler: Keystoker KAA-2
- Hand Fed Coal Boiler: used to have a 5 section Red Square
- Coal Size/Type: rice anthracite
On the subject,
No control man here, but could he use zone valves with isolated end switches [end switch terminals on each zone valve run back to "TT" on circulator controller?
The 8124 triple 'stat on my boiler has "TT" terminals, jump those close the connection w/a thermostat of end switch from a zone valve and the pump and stoker run. I've seen those pricey zone valve controllers, but are they really needed?
Dave
No control man here, but could he use zone valves with isolated end switches [end switch terminals on each zone valve run back to "TT" on circulator controller?
The 8124 triple 'stat on my boiler has "TT" terminals, jump those close the connection w/a thermostat of end switch from a zone valve and the pump and stoker run. I've seen those pricey zone valve controllers, but are they really needed?
Dave
- dave brode
- Member
- Posts: 478
- Joined: Fri. Jan. 15, 2010 5:47 pm
- Location: Frostburg, Maryland [western]
- Stoker Coal Boiler: Keystoker KAA-2
- Hand Fed Coal Boiler: used to have a 5 section Red Square
- Coal Size/Type: rice anthracite
There are "2 wire" zone valves [2 wires, or, terminals]: 2 wires, operate the valve, nothing else. The valves that I mentioned are actually 4 wire, with 2 from an isolated end switch going to TT etc.
Afaik, there are 3 wire valves actually operate like those with 4 wires and an end switch. Those are usually wired with more than one circuit sharing a terminal. I have a bit of gray matter deficit, so I have a hard time understanding this, but.....
http://www.houseneeds.com/upload/pdf/taco-zoneval ... iescat.pdf
I'm about to wire up a 24v "3 wire" Taco and a 24v "4 wire" honeywell, both will have a pair going back to "TT". Wish me luck. LOL
Dave
Fwiw, some other wiring info;
http://s3.pexsupply.com/manuals/1283431653990/386 ... D_FILE.pdf
http://s3.pexsupply.com/manuals/1350288596772/824 ... D_FILE.pdf
Afaik, there are 3 wire valves actually operate like those with 4 wires and an end switch. Those are usually wired with more than one circuit sharing a terminal. I have a bit of gray matter deficit, so I have a hard time understanding this, but.....
http://www.houseneeds.com/upload/pdf/taco-zoneval ... iescat.pdf
I'm about to wire up a 24v "3 wire" Taco and a 24v "4 wire" honeywell, both will have a pair going back to "TT". Wish me luck. LOL
Dave
Fwiw, some other wiring info;
http://s3.pexsupply.com/manuals/1283431653990/386 ... D_FILE.pdf
http://s3.pexsupply.com/manuals/1350288596772/824 ... D_FILE.pdf
- ntp71
- Member
- Posts: 277
- Joined: Sat. May. 17, 2008 9:14 am
- Location: Nanticoke, PA
- Hand Fed Coal Boiler: Reading Foundry Water Heater
- Hot Air Coal Stoker Stove: Old Mill Mini Stoker with Keystoker Feed System
- Hand Fed Coal Stove: Gibraltar SCR
- Baseburners & Antiques: Caloric UltraMatic Coal-Gas Range
- Coal Size/Type: Chestnut
Just adding my $0.02 here.
A few years ago I wired up two zone valves having two separate thermostats to my one furnace. I pretty much used the wiring diagram on the taco box to do this. My buddy insisted I need some type of controller to do this, however all I need was a transformer and a terminal board and my set up looks and works great.
Neal
A few years ago I wired up two zone valves having two separate thermostats to my one furnace. I pretty much used the wiring diagram on the taco box to do this. My buddy insisted I need some type of controller to do this, however all I need was a transformer and a terminal board and my set up looks and works great.
Neal
Attachments
-
- Member
- Posts: 127
- Joined: Fri. Mar. 04, 2011 6:29 pm
- Location: Quakertown PA
- Stoker Coal Boiler: EFM
- Coal Size/Type: Rice
Thanks guys, I suspected I was going to need another box. I am sure I could rig up something, but the install is actually looking pretty decent