Can a Class A chimney be installed through the ridge vent center line of a home? As it turns out, if I choose to install a stove on the inside wall of our living room it looks like the best place for the chimney would be going straight through the center line peak of the roof.


User avatar
McGiever
Member
Posts: 6068
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sat. Aug. 31, 2013 8:43 am

Some things that need to be addressed would be structural issues...you don't want to compromise structural integritry and of course this application will require a non conventional flashing at roof penetration.

User avatar
michaelanthony
Member
Posts: 4060
Joined: Sat. Nov. 22, 2008 10:42 pm
Hand Fed Coal Stove: Vigilant 2310, gold marc box stove, vogelzang pot belly coat rack
Baseburners & Antiques: Home Sparkle 12
Coal Size/Type: Coal Contractor's stove, a little Kimmels 'nut
Other Heating: Very cold FHA oil furnace
Location: millinocket,me.
Contact:

Post Sat. Aug. 31, 2013 8:45 am

No , it looks like the chimney will have some off set piping in order to NOT go through the center line of the ridge!

User avatar
lsayre
Member
Posts: 12540
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sat. Aug. 31, 2013 10:06 am

I would much prefer to avoid offsets and keep it straight.

I did find this: http://www.icc-rsf.com/main.php?t=chem_produits&i=121&l=en

And this: http://www.icc-rsf.com/c/iccrsf/file_db/chem_prod ... 09-101.pdf
Last edited by lsayre on Sat. Aug. 31, 2013 11:07 am, edited 1 time in total.

User avatar
carlherrnstein
Member
Posts: 970
Joined: Tue. Feb. 07, 2012 8:49 am
Hot Air Coal Stoker Stove: combustioneer model 77B
Coal Size/Type: pea stoker/Ohio bituminous
Location: Clarksburg, ohio

Post Sat. Aug. 31, 2013 10:59 am

I don't see why not, so long as you minimize the cutting of load bearing members and reinforce where you cant get away from it. I have seen peak flashing in stores at different times, here is a link that shows some for sale. http://www.amazon.com/s/ref=nb_sb_noss?url=search ... f+Flashing

WNYRob
Member
Posts: 264
Joined: Thu. Apr. 14, 2011 12:13 pm
Hot Air Coal Stoker Stove: Keystoker Koker controlled with CoalTrol
Location: Springville, NY

Post Sat. Aug. 31, 2013 4:56 pm

Can you install the chimney off to one side of the ridge, come straight down with it and then just offset the stove pipe coming off the stove to meet the chimney. I had an existing chimney that ran a couple inches off one of my outside walls of the basement so there was no moving it. I just have a slight offset in the stove pipe because the stove outlet couldn't be positioned close enough to the wall. It doesn't effect draft and any ash accumulation is easily vacuumed out via the barometric damper tee.

waldo lemieux
Member
Posts: 2262
Joined: Sun. Sep. 30, 2012 8:20 pm
Stove/Furnace Make: efm
Stove/Furnace Model: s-20
Location: Ithaca,NY

Post Sat. Aug. 31, 2013 7:03 pm

ISayre

If the house has trusses for a roof system ,Greenlight. If you have rafters bearing on a ridgeboard(1x? or 2x?),Greenlight.If you have a massive BEAM on which the rafters set or are hung from joist hangers,Redlight!!! It is most unlikely you have that condition in this neck of the woods. If you have any doubt simply post a photo of the ridge and I can tell you for certain.

Waldo

User avatar
lsayre
Member
Posts: 12540
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sat. Aug. 31, 2013 7:18 pm

waldo lemieux wrote:ISayre

If the house has trusses for a roof system ,Greenlight. If you have rafters bearing on a ridgeboard(1x? or 2x?),Greenlight.If you have a massive BEAM on which the rafters set or are hung from joist hangers,Redlight!!! It is most unlikely you have that condition in this neck of the woods. If you have any doubt simply post a photo of the ridge and I can tell you for certain.

Waldo
It is a truss roof. The house was made in 1964.


waldo lemieux
Member
Posts: 2262
Joined: Sun. Sep. 30, 2012 8:20 pm
Stove/Furnace Make: efm
Stove/Furnace Model: s-20
Location: Ithaca,NY

Post Sat. Aug. 31, 2013 8:21 pm

Let er' have it! ;)

User avatar
2001Sierra
Member
Posts: 1850
Joined: Wed. May. 20, 2009 8:09 am
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34
Stove/Furnace Model: Keystoker 90 Chimney Vent
Location: Wynantskill NY, 10 miles from Albany

Post Sat. Aug. 31, 2013 9:14 pm

How would you install the flashing? Typically the flashing follows a roof pitch.

User avatar
KLook
Member
Posts: 3650
Joined: Sun. Feb. 17, 2008 1:08 pm
Stoker Coal Boiler: Harman VF 3000
Coal Size/Type: rice, bagged, Blaschak
Other Heating: Gas boiler backup/main
Stove/Furnace Model: VF 3000
Location: Harrison, Tenn

Post Sat. Aug. 31, 2013 9:25 pm

I have custom made flashing. After all, the old timers did it with steel. There are places that can bend any shapes you like. Find a good metal fabricator and just tell him the pitch and the hole size. I helped a friend make one out of copper. He silver soldered the corners!

Kevin

waldo lemieux
Member
Posts: 2262
Joined: Sun. Sep. 30, 2012 8:20 pm
Stove/Furnace Make: efm
Stove/Furnace Model: s-20
Location: Ithaca,NY

Post Sun. Sep. 01, 2013 4:50 am

Not that you would do it ,but if your going through the peak of the roof, you could cut it tight and caulk it. so little water hits the very peak(yearly rainfall) minus whatever the cap deflects ,it would never show. I cant tell you how many 4" sewer vents Ive found when replacing a roof, where the plumber used a hole saw ,stuffed the pipe up through and ran off :shock: and nary a water stain to be found! @[email protected]% plumbers anyway! :out:

User avatar
michaelanthony
Member
Posts: 4060
Joined: Sat. Nov. 22, 2008 10:42 pm
Hand Fed Coal Stove: Vigilant 2310, gold marc box stove, vogelzang pot belly coat rack
Baseburners & Antiques: Home Sparkle 12
Coal Size/Type: Coal Contractor's stove, a little Kimmels 'nut
Other Heating: Very cold FHA oil furnace
Location: millinocket,me.
Contact:

Post Sun. Sep. 01, 2013 7:13 am

WNYRob wrote:Can you install the chimney off to one side of the ridge, come straight down with it and then just offset the stove pipe coming off the stove to meet the chimney. I had an existing chimney that ran a couple inches off one of my outside walls of the basement so there was no moving it. I just have a slight offset in the stove pipe because the stove outlet couldn't be positioned close enough to the wall. It doesn't effect draft and any ash accumulation is easily vacuumed out via the barometric damper tee.
...I like your thinking.

User avatar
lsayre
Member
Posts: 12540
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Sep. 01, 2013 7:20 am

See the top link I posted above. Adjustable pitch angle flashing for chimneys that go through roof peaks.

User avatar
lsayre
Member
Posts: 12540
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Sep. 01, 2013 9:47 am

Attached here is a quick and dirty sketch of the general lay of the floorplan of our upstairs level. The broken line is the center line of the home (despite my failure to actually proportion things so it would look that way in the PDF), and the red box is my thought as to the best place to put a hand fired coal stove (thought the better half would like me to put it in the basement). If she allows me to win (not likely), is this red box location the best choice I have?