Stove Pipe Clearance Question

This forum is for common products and questions such as chimney installations, CO detectors, coal bin designs and a variety of other general topics that do not fit into the other forums.
Post Reply
ez2remember
New Member
Posts: 16
Joined: Wed. Jan. 02, 2013 1:14 pm

Post Sun. Jan. 13, 2013 11:00 am

Hey guys,
so with the way I am running my stove pipe, I have 10 inches from an elbow to the exposed floor joists above it (the stove is in an unfinished basement with a through-wall chimney).
Since I am using single wall durablack, I need to have at least 18 inches from the stove pipe to any combustibles. Obviously I don't have that much clearance to my floor joist.
What I need to know is if I hang a 24 gauge sheet of aluminum 12x24 from the floor joist above the stove pipe (and ensure there is at least a 1" air gap from sheet metal to joist), will that work to get me my clearance?

Thanks guys, I appreciate the help
-Steve


franco b
Site Moderator
Posts: 8437
Joined: Wed. Nov. 05, 2008 5:11 pm
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea
Location: Kent CT

Post Sun. Jan. 13, 2013 11:07 am

That should work well. You could also as an alternative put the heat shield on the pipe.