Pressure Switch to Help Summer Outfires.

This forum is for common products and questions such as chimney installations, CO detectors, coal bin designs and a variety of other general topics that do not fit into the other forums.
User avatar
Lightning
Member
Posts: 8281
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post Sun. Jan. 13, 2013 10:06 am

Rigar wrote:....do you have a baro installed ?
A baro helps a tame a strong draft but doesn't help a weak one..
Rigar wrote:....in the summer ?
No, I don't burn in the summer.. But I do idle it thru warm days on the shoulder months, thats when I risk draft failure.

Rigar
Member
Posts: 857
Joined: Tue. Dec. 04, 2012 6:30 am
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice
Stove/Furnace Make: Keystoker
Stove/Furnace Model: A 150 warm air furnace
Location: central new york (syracuse area)

Post Sun. Jan. 13, 2013 10:20 am

Rigar wrote:....do you have a baro installed ?
A baro helps a tame a strong draft but doesn't help a weak one "

...but HEAT will
....'Rigar

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sun. Jan. 13, 2013 5:04 pm

Interesting...

Here's my $.02...

How about a "repeat timer" with a "stack temp switch" supervising it...only "repeats" if "stack" temp falls below the set point of "switch". :)

This is a highly adjustable circuit...One can adjust the "timer"...and even adjust the "stack switch" set point, allowing a nice range for "fine tuning".
SLOW AND STEADY WINS THE RACE

Rigar
Member
Posts: 857
Joined: Tue. Dec. 04, 2012 6:30 am
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice
Stove/Furnace Make: Keystoker
Stove/Furnace Model: A 150 warm air furnace
Location: central new york (syracuse area)

Post Sun. Jan. 13, 2013 5:15 pm

McGiever makes a great point...and I thought some sort of timer was understood

...2 more cents from me
...the timer should be "retriggerable"......so the cycle RESTARTS each time its enegized
...other wise it could potentially be in its "OFF" time when it is called upon...and depending on your repeat parameters...you could still lose draft all together while it "catches up"
....'Rigar


User avatar
lsayre
Member
Posts: 12185
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Jan. 13, 2013 5:22 pm

The TORK EJWT "Percentage Timer" resets itself and starts counting time all over again from zero every time the current feeding it is dropped. A relay can be incorporated to drop the current to the timer whenever the stack is hot enough to draft sufficiently.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

Rigar
Member
Posts: 857
Joined: Tue. Dec. 04, 2012 6:30 am
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice
Stove/Furnace Make: Keystoker
Stove/Furnace Model: A 150 warm air furnace
Location: central new york (syracuse area)

Post Mon. Jan. 14, 2013 9:54 am

Rigar wrote:McGiever makes a great point...and I thought some sort of timer was understood

...2 more cents from me
...the timer should be "retriggerable"......so the cycle RESTARTS each time its enegized
...other wise it could potentially be in its "OFF" time when it is called upon...and depending on your repeat parameters...you could still lose draft all together while it "catches up"
...i meant "one shot"..... triggerable or non should not really matter in your case... As you would be looking for a short fire to regain draft only...
... I get these terms confused all the time... sorry

p.s. MACROMATIC makes a huge selection of these type of timers.... and they are very affordable
....'Rigar

User avatar
Rob R.
Site Moderator
Posts: 11342
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Mon. Jan. 14, 2013 11:56 am

I have a Macromatic repeat-cycle relay on my EFM...part # TR-63122. It restarts the cycle when the power is cycled. Mine begins with the "off cycle", but you they make one that beings with "on" as well.

Post Reply