Venting Problems With Magnum???

Post Reply
 
pa coal cracker
Member
Posts: 57
Joined: Sun. Dec. 02, 2007 9:38 am
Location: Hegins Pa

Post by pa coal cracker » Sun. Dec. 23, 2012 8:46 pm

Had this stove since 2009, no problems until this year.
I'm getting the sulfur smell. ( not all the time)
Manometer reading in flue .06, fire box .06 ( burning buckwheat)
30 ft chimney (block withe clay flue) was cleaned in Sept. (hardly any dirt).
I do the basic cleaning every spring,I put a new glass in this year. All the gaskets are original (they seem ok).
Any sugestions? thank you

 
User avatar
michaelanthony
Member
Posts: 4550
Joined: Sat. Nov. 22, 2008 10:42 pm
Location: millinocket,me.
Hand Fed Coal Stove: Vigilant 2310, gold marc box stove
Hand Fed Coal Furnace: Gold Marc Independence
Baseburners & Antiques: Home Sparkle 12
Coal Size/Type: 'nut
Other Heating: Fujitsu mini split, FHA oil furnace

Post by michaelanthony » Sun. Dec. 23, 2012 8:58 pm

Do you have a CO detector? If not I would get one, while I was at the store buying the detector I would buy new gasket and start there.

 
pa coal cracker
Member
Posts: 57
Joined: Sun. Dec. 02, 2007 9:38 am
Location: Hegins Pa

Post by pa coal cracker » Sun. Dec. 23, 2012 9:01 pm

Yep I have a detector


 
User avatar
tsb
Member
Posts: 2621
Joined: Wed. Jul. 30, 2008 8:38 pm
Location: Douglassville, Pa
Stoker Coal Boiler: Binford 2000
Hot Air Coal Stoker Stove: LL Pioneer top vent
Hand Fed Coal Stove: Saey Hanover II
Baseburners & Antiques: Grander Golden Oak , Glenwood # 6
Coal Size/Type: All of them

Post by tsb » Sun. Dec. 23, 2012 9:10 pm

Have you changed coal ? The Blaschak coal I got last year has a
funky sulfur smell in the hopper. Not real bad, but enough to notice.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Dec. 23, 2012 9:55 pm

pa coal cracker wrote:Manometer reading in flue .06, fire box .06 ( burning buckwheat)
Throttle the air back a little, you want the fire box draft to be a lower reading than the flue draft. When the *over the fire* draft is equal or greater than the flue draft, the fire box can become slightly pressurized and will find any imperfections in the gaskets or back up into hopper and seep exhaust gases.

 
pa coal cracker
Member
Posts: 57
Joined: Sun. Dec. 02, 2007 9:38 am
Location: Hegins Pa

Post by pa coal cracker » Mon. Dec. 24, 2012 4:53 am

Turned the air back (.04 -.05) firebox..........(.06) flue
I agree this will certainly help if not totaly fix the problem.
How long between gasket changes, and is there anything else I should be doing along with yearly cleaning?
I have never removed the main feeder body, I check the mounting bolts making sure they are tight,clean and blow it out.


 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Mon. Dec. 24, 2012 8:28 am

Have you always burned buck? The magnum prefers rice. If I try to burn buck in my boiler, which uses the same stoker as your magnum, I get the smell out of the hopper. Try switching to rice. Or a rice buck mix.

 
pa coal cracker
Member
Posts: 57
Joined: Sun. Dec. 02, 2007 9:38 am
Location: Hegins Pa

Post by pa coal cracker » Tue. Dec. 25, 2012 12:27 pm

I've been burning buck since day one, never had a problem.
I never had to change any settings up until now. The more I think about it the buckwheat seems bigger in size.
Which would let more air through into the fire box. Could be the screens are getting a little worn at the breaker.