1 90 or 2-45's

Post Reply
 
User avatar
spc
Member
Posts: 1801
Joined: Sat. Jan. 06, 2007 9:51 am
Location: Rhode Island

Post by spc » Thu. Nov. 22, 2007 3:28 pm

I was reading another post Smoke Rolls Out Load Door - Any Advice?. Will 2-45 degree elbows give me a better draft than 1-90? I have a top vent with about 18" vertical before the 90 & a "T" for the baro & then right to the thimble. Not to much pipe. Thanks.

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Nov. 22, 2007 8:43 pm

I subscribe to the least amount theorey. The least amount of pipe, elbows, angles and thimble pipe. If you have a great chimney, it really doesn't matter if you have a few turns. A poor one can make life difficult.


 
User avatar
WNY
Member
Posts: 6307
Joined: Mon. Nov. 14, 2005 8:40 am
Location: Cuba, NY
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Contact:

Post by WNY » Fri. Nov. 23, 2007 7:28 am

I don't think it would affect it that much, I would think the straighter the pipe, the better airflow and draft, also, I read somewhere, that Elbows, TEE, etc.. add "XX" in equivalent pipe length. (ie. 90 Deg. Elbow is equal to 10 feet of straight run? or something like that)

 
Matthaus
Member
Posts: 1923
Joined: Mon. Oct. 02, 2006 8:59 am
Location: Berwick, PA and Ormand Beach FL

Post by Matthaus » Fri. Nov. 23, 2007 12:39 pm

Actually two 6" 45* Els would have slightly less loss than a single 90* EL. The cost however, does not make this worth it. :)

Forgot the ratios on the table, they are 1/4, 1/2 and 3/4 going down from the top row for d/D.

Post Reply