Just picked up a new Watts M1 prv for my boiler and in reading the yellow tag that is attached noticed that it is not to be used on coal or wood fired boilers having an uncontrolled BTU heat output. What PRV should be used for wood and coal units? 30# is 30# right?

User avatar
McGiever
Member
Posts: 6084
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Tue. Jan. 31, 2012 5:25 pm

I don't know what one you need to use for coal.

30 #'s at a big enough capacity to handle the volume of a run away solid fuel boiler.

But one rated to at least 500,000 bth/hr might ought to work. :)

I smell a liability lawyer. :idea:
Last edited by McGiever on Tue. Jan. 31, 2012 5:30 pm, edited 1 time in total.

crazy4coal
Member
Posts: 516
Joined: Wed. Feb. 13, 2008 8:29 pm
Stove/Furnace Make: buderus
Stove/Furnace Model: logana
Location: Sussex County N.J.

Post Tue. Jan. 31, 2012 5:29 pm

This one is rated at 510,000 BTU an hr

User avatar
McGiever
Member
Posts: 6084
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Tue. Jan. 31, 2012 5:33 pm

Do you have uncontrolled BTU output?


crazy4coal
Member
Posts: 516
Joined: Wed. Feb. 13, 2008 8:29 pm
Stove/Furnace Make: buderus
Stove/Furnace Model: logana
Location: Sussex County N.J.

Post Tue. Jan. 31, 2012 5:36 pm

Hand fired boiler with a samson draft control

User avatar
steamup
Member
Posts: 1209
Joined: Fri. Oct. 03, 2008 12:13 pm
Stoker Coal Boiler: Axeman-Anderson AA-130, Keystoker K-6
Hand Fed Coal Boiler: HS Tarm 502 Wood/Coal/Oil
Coal Size/Type: pea, buck, rice
Location: Napoli, NY

Post Wed. Feb. 01, 2012 7:40 am

No doubt legal mumbo jumbo.

Someone had a problem somewhere and blamed the relief valve.

Hand fired equipment can be easily overfired.

Just make sure the relief valve has 2 to 3 times the max rated capacity of the hand fired equipment. That is usually not a problem with residential equipment.

crazy4coal
Member
Posts: 516
Joined: Wed. Feb. 13, 2008 8:29 pm
Stove/Furnace Make: buderus
Stove/Furnace Model: logana
Location: Sussex County N.J.

Post Wed. Feb. 01, 2012 4:32 pm

Thanks, I thought it was alot of BS. Iwas in the supply house today and asked about the disclaimer and the guts pulled some other sizes off the shelf and all had the same thing on them. Maybe they want a the valves with the weights hanging on a chain. More weight , more pressure! or just wire it closed...LOL