Hi,my name is Mike and I am new to the forum and to coal.I am Installing a used Franco Belge 10.242 in great shape.I have purchased a Selkirk Metalbestos typeHT dbl walled stainless,Is this suitable.My next question is how far should the stove be kept off the back wall,thanks Mike.
- coaledsweat
- Site Moderator
- Posts: 13768
- Joined: Fri. Oct. 27, 2006 2:05 pm
- Location: Guilford, Connecticut
- Stoker Coal Boiler: Axeman Anderson 260M
- Coal Size/Type: Pea
If the Selkirk is marked 316, you should be fine. 304 will work too but will have a slightly reduced usable life. 36" is probably enough for a flammable wall, closer if it is protected with steel/tile/cement/etc.