CO Detector With Ability to Shut Off Power
- av8r
- Member
- Posts: 1164
- Joined: Thu. Dec. 06, 2007 12:07 pm
- Location: Near Owego, NY
- Hot Air Coal Stoker Furnace: Leisure Line Hearth with twin turbos (sounds like it)
I've asked about this in the past and still can't find anything commercially available. I'd like to have a CO detector that would allow for shutting down power to a device, in this case the stoker motor on a coal stove. I know I can rig something up using a latching relay, but I'd prefer to buy something already built. Any ideas?
- av8r
- Member
- Posts: 1164
- Joined: Thu. Dec. 06, 2007 12:07 pm
- Location: Near Owego, NY
- Hot Air Coal Stoker Furnace: Leisure Line Hearth with twin turbos (sounds like it)
Thanks..that has relay contacts, but what do you use for the actual power shutoff module?nortcan wrote:I install one on each floor to shut off the power of the blower venting air around the Vig.
S-TECH, PS-001N
stech.com
I have a power box and the blower is plug in it.av8r wrote:Thanks..that has relay contacts, but what do you use for the actual power shutoff module?nortcan wrote:I install one on each floor to shut off the power of the blower venting air around the Vig.
S-TECH, PS-001N
stech.com
The relay is 12V,and I have a transfo 120V to 12 V placed in a regular electric 120V box with fem.120V plugs. Sorry for my poor translation.
In fact it's is in a gegular 120V outlet box. A plug cord get out of that box and connect to the power. The blower is connected to that outlet. From the relay wires run to the Co alarm. If Co is detected, alarms sound and the blower stops.
Easy to understand for you??????????????? if not I can ask a friend better words.
Attachments
- WNY
- Member
- Posts: 6307
- Joined: Mon. Nov. 14, 2005 8:40 am
- Location: Cuba, NY
- Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
- Coal Size/Type: Rice
- Contact:
Yes, in one of the old threads, the guy at CoalJack was offering them to the public, they are standard with their stoves.
I believe you can get them for Boats and RV's too, to shut off the generators if CO is present. Just have to wire them up a bit differently or may need a transformer (12V or 24V) They have many different ones available.
Coaljack C.O. Detector
I believe you can get them for Boats and RV's too, to shut off the generators if CO is present. Just have to wire them up a bit differently or may need a transformer (12V or 24V) They have many different ones available.
Coaljack C.O. Detector
- av8r
- Member
- Posts: 1164
- Joined: Thu. Dec. 06, 2007 12:07 pm
- Location: Near Owego, NY
- Hot Air Coal Stoker Furnace: Leisure Line Hearth with twin turbos (sounds like it)
So the relay is in the silver electrical box?nortcan wrote:I have a power box and the blower is plug in it.av8r wrote: Thanks..that has relay contacts, but what do you use for the actual power shutoff module?
The relay is 12V,and I have a transfo 120V to 12 V placed in a regular electric 120V box with fem.120V plugs. Sorry for my poor translation.
In fact it's is in a gegular 120V outlet box. A plug cord get out of that box and connect to the power. The blower is connected to that outlet. From the relay wires run to the Co alarm. If Co is detected, alarms sound and the blower stops.
Easy to understand for you??????????????? if not I can ask a friend better words.
thanks
Yes the relay is in it.
The power arrives at the white outlet, the silver box(connected to the white power outlet box) with the relay brings the power to one outlet for the transfo at the bottom and the other to the motor.
The power arrives at the white outlet, the silver box(connected to the white power outlet box) with the relay brings the power to one outlet for the transfo at the bottom and the other to the motor.
Attachments
- av8r
- Member
- Posts: 1164
- Joined: Thu. Dec. 06, 2007 12:07 pm
- Location: Near Owego, NY
- Hot Air Coal Stoker Furnace: Leisure Line Hearth with twin turbos (sounds like it)
Thanksnortcan wrote:Yes the relay is in it.
The power arrives at the white outlet, the silver box(connected to the white power outlet box) with the relay brings the power to one outlet for the transfo at the bottom and the other to the motor.
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Posted this earlier in your other thread...but neither is this a Plug N Play solution.
When this relay is combined w/ a Interconnected Detector it will switch whatever you connect to it.
This is the detector which is compatible w/ the relay:
Kidde-KN-COSM-IB-Hardwire-Combination-Interconnectable
When this relay is combined w/ a Interconnected Detector it will switch whatever you connect to it.
McGiever wrote:For others who may not be looking for a "plug-n-play" solution:
Carbon Monoxide Alarm Relay Module
This relay will only activate when it receives a CO signal from an interconnected Carbon Monoxide Alarm.
This is the detector which is compatible w/ the relay:
Kidde-KN-COSM-IB-Hardwire-Combination-Interconnectable
Last edited by McGiever on Tue. Nov. 29, 2011 8:31 pm, edited 2 times in total.
- av8r
- Member
- Posts: 1164
- Joined: Thu. Dec. 06, 2007 12:07 pm
- Location: Near Owego, NY
- Hot Air Coal Stoker Furnace: Leisure Line Hearth with twin turbos (sounds like it)
Thank youMcGiever wrote:Posted this earlier in your other thread...but neither is this a Plug N Play solution.
When this relay is combined w/ a Interconnected Detector it will switch whatever you connect to it.
Need a Combustion Gas Shut Off
- mariohotshot
- Member
- Posts: 114
- Joined: Sun. Oct. 27, 2013 10:58 pm
- Location: Blakeslee, PA
I like this idea. I just don't understand the hookup. Can someone please give more specific details on how to hook this up? Would an exhaust fan also help if it were connected to a CO detector? Thanks in advance!
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
hook up is: The relay gets signal from alarm and then relay switches off stoker burner.
I would be hesitant to have a CO alarm relay start an exhaust fan...it is possible the fan would worsen the CO levels depending on what caused the alarm in the first place.
I would be hesitant to have a CO alarm relay start an exhaust fan...it is possible the fan would worsen the CO levels depending on what caused the alarm in the first place.
- mariohotshot
- Member
- Posts: 114
- Joined: Sun. Oct. 27, 2013 10:58 pm
- Location: Blakeslee, PA
Thanks, but more specific in voltage connections. 120V feeding the stove is interuppted by the relay which is triggered by the co detector. I assume the relay is 12v? It needs a transformer. The alarm is only sending a signal to the relay which in turn opens the feeding circuit? Correct? A diagram would be great!
- mariohotshot
- Member
- Posts: 114
- Joined: Sun. Oct. 27, 2013 10:58 pm
- Location: Blakeslee, PA
I figured it out. Once I get it put together, I'll post some photos and some wire diagrams to share. No it does not cost $300 to build!