Manometer Install

 
User avatar
dave brode
Member
Posts: 478
Joined: Fri. Jan. 15, 2010 5:47 pm
Location: Frostburg, Maryland [western]
Stoker Coal Boiler: Keystoker KAA-2
Hand Fed Coal Boiler: used to have a 5 section Red Square
Coal Size/Type: rice anthracite

Post by dave brode » Sun. Oct. 24, 2010 6:55 pm

Here is my install.

I used common 3/16" brake line. Note the small 90* pipe thread to inverted flare fitting that allows be used. They come in straight too. Any good parts house.

I welded a 1/8" coupler onto the flue, but Dwyer included nuts with 1/8" pipe thread to attach the supplied barbed fitting to a flue pipe [with a washer]. Those nuts would work on the pipe thread end of the fittings that I used too.

I put a piece of hose on the high side nipple too, to prevent dirt from getting in.

Dave

Attachments

Oct24^03.JPG
.JPG | 147.1KB | Oct24^03.JPG
Oct24^14.JPG
.JPG | 172.1KB | Oct24^14.JPG
Oct24^11.JPG
.JPG | 100.9KB | Oct24^11.JPG


 
User avatar
sperry
Member
Posts: 67
Joined: Fri. Nov. 05, 2010 10:55 pm
Location: America
Stoker Coal Boiler: EFM 520

Post by sperry » Sun. Jan. 23, 2011 6:08 pm

Here's my install. Thanks for all the great install info :!:

Attachments

efm012011 003.jpg
.JPG | 148KB | efm012011 003.jpg
efm012011 016.jpg
.JPG | 117.8KB | efm012011 016.jpg

 
dandy
Member
Posts: 40
Joined: Wed. Jul. 16, 2008 6:12 pm
Location: northern maine

Post by dandy » Sat. Mar. 19, 2011 6:01 pm

Just did an install on my Ka-6 of a manometer using a magnhelic guage instead. THe guage seems to work just as good as the manometer, but I am not getting the reading of a dwyer 25. Still have minor issuse to address but since this is saturday afternoon and the parts stores are closed will get to them next week. just need a fireproof washer to install on stove pipe connection then use furnace cement on fitting to tie everything together. So far have under 20 dollars invested and I'm very happy with how it seems to perform....

 
User avatar
dh1200s
Member
Posts: 67
Joined: Sat. Jul. 18, 2009 1:12 pm
Location: Honey Brook, Pa.
Stoker Coal Boiler: Leisure Line WL-110
Hand Fed Coal Boiler: HS-Tarm 202
Hand Fed Coal Stove: Harman TLC 2000

Post by dh1200s » Tue. Nov. 15, 2011 6:02 am

I liked MURDOC1 post on this subject Draft Test Port Install in Stove Pipe... and went that direction with some small dia brass tubing I had on hand sleeving it down for using silicone tubing easily found at the hobby shop.

The two manometers I received from a discount vendor were delivered with oil but no tubing to connect from the adapter to the manometer..........Dick

Attachments

PB130032.JPG
.JPG | 76.7KB | PB130032.JPG
PB130040.JPG
.JPG | 30KB | PB130040.JPG
PB130037.JPG
.JPG | 38KB | PB130037.JPG
Mamometer fitting 4.JPG
.JPG | 63.4KB | Mamometer fitting 4.JPG
Mamometer fitting 3.JPG
.JPG | 52.5KB | Mamometer fitting 3.JPG
Mamometer fitting 5.JPG
.JPG | 51.7KB | Mamometer fitting 5.JPG

 
Boots
Member
Posts: 197
Joined: Thu. Nov. 10, 2011 4:38 pm
Location: Central PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Boiler: Burnham SFB 101 (sold)

Post by Boots » Sun. Feb. 26, 2012 8:59 am

I got my dwyer and got it installed. its been about 35*f during the day here and im getting .02 In of wc with boiler at low fire with 230*f stack temp. and about .03 to .04 in of wc at high fire with 500*f + stack temp. burnham recommends .05 in of wc. Im assuming that when the temp drops some more that my draft will go up but also im assuming that running .03-.04 inches will be ok. I mean my chimney drafts what it drafts, there is not much that can be done to change that. There is a little bit of ash in the pipe between the baro and the boiler but not much. and on the opposite side of the baro the pipe is clean. I cleaned the sealing surface of my chimney clean out door and sealed it with silicone to stop any potential leaks. My home is pretty tight so I cracked a basement window slightly to help improve the draft as well. What else can I do? at some point today I will climb up on the roof and look down the chimney to see if all is clear, which I expect it will be.

 
User avatar
Wiz
Member
Posts: 926
Joined: Sun. Nov. 27, 2011 8:45 pm
Location: Tannersville Pa
Stoker Coal Boiler: Keystoker Ka 6
Coal Size/Type: Casey Junk Coal :(

Post by Wiz » Tue. Sep. 18, 2012 7:54 pm

I see that most use the dwyer oil fill manometer, why not the digital ones.

http://www.dwyer-inst.com/Product/Pressure/Manome ... s/Digital/

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 18, 2012 7:58 pm

Wiz wrote:I see that most use the dwyer oil fill manometer, why not the digital ones.

http://www.dwyer-inst.com/Product/Pressure/Manome ... s/Digital/
The oil filled manos only cost about $34. And calibration is as simple as leveling them and having them filled with the proper amount of the proper oil. How do you calibrate one of those $200+ digital manometers, and how long does it stay calibrated?


 
User avatar
Wiz
Member
Posts: 926
Joined: Sun. Nov. 27, 2011 8:45 pm
Location: Tannersville Pa
Stoker Coal Boiler: Keystoker Ka 6
Coal Size/Type: Casey Junk Coal :(

Post by Wiz » Tue. Sep. 18, 2012 8:03 pm

lsayre wrote:
Wiz wrote:I see that most use the dwyer oil fill manometer, why not the digital ones.

http://www.dwyer-inst.com/Product/Pressure/Manome ... s/Digital/
The oil filled manos only cost about $34. And calibration is as simple as leveling them and having them filled with the proper amount of the proper oil. How do you calibrate one of those $200+ digital manometers, and how long does it stay calibrated?

I found them for $36.89 on eb@y

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Sep. 18, 2012 8:09 pm

Try Cole Parmer. Less expensive, and way less shipping cost to boot.

 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Tue. Sep. 18, 2012 9:41 pm

"dave brode" Here is my install.

I used common 3/16" brake line. Note the small 90* pipe thread to inverted flare fitting that allows be used. They come in straight too. Any good parts house.

What a nice setup! What kind of wax do you use on your equipment :roll:

 
User avatar
Wiz
Member
Posts: 926
Joined: Sun. Nov. 27, 2011 8:45 pm
Location: Tannersville Pa
Stoker Coal Boiler: Keystoker Ka 6
Coal Size/Type: Casey Junk Coal :(

Post by Wiz » Sun. Sep. 30, 2012 12:29 pm

Order a dwyer 25 mano, should be here by weds. I'll see how far off my draft is ;)

 
User avatar
Poconoeagle
Member
Posts: 6397
Joined: Sat. Nov. 08, 2008 7:26 pm
Location: Tobyhanna PA

Post by Poconoeagle » Wed. Oct. 03, 2012 9:52 pm

Hey Wiz, check out,"Got a manometer-now what" thread......

8-)

 
User avatar
Wiz
Member
Posts: 926
Joined: Sun. Nov. 27, 2011 8:45 pm
Location: Tannersville Pa
Stoker Coal Boiler: Keystoker Ka 6
Coal Size/Type: Casey Junk Coal :(

Post by Wiz » Thu. Oct. 04, 2012 5:51 pm

Poconoeagle wrote:Hey Wiz, check out,"Got a manometer-now what" thread......

8-)
Yup read that one, good info... Heading out to workshop, my manometer is here.

 
User avatar
Wiz
Member
Posts: 926
Joined: Sun. Nov. 27, 2011 8:45 pm
Location: Tannersville Pa
Stoker Coal Boiler: Keystoker Ka 6
Coal Size/Type: Casey Junk Coal :(

Post by Wiz » Fri. Oct. 05, 2012 9:11 pm

Keystoker Ka-6.... Recommends draft setting at idle -.01 and draft settings at demand -.02 Checking of draft is to be check at pre drilled hole in door.

Image

Image

Image

 
User avatar
SMITTY
Member
Posts: 12526
Joined: Sun. Dec. 11, 2005 12:43 pm
Location: West-Central Mass
Stoker Coal Boiler: EFM 520 Highboy
Coal Size/Type: Rice / Blaschak anthracite
Other Heating: Oil fired Burnham boiler

Post by SMITTY » Fri. Oct. 05, 2012 9:16 pm

Minus? On my setup that indicates NO draft ... actually a backflow at that stage .... hence the red because that's not good .... :gee: