Hey all, just got my manometer. As far as installation, is there any place on the 140 specifically to install it? I know some stoves have a place to insert the probe. Or do I just insert within the stove pipe before the barometric dampener?
- Idlorah
- Member
- Posts: 435
- Joined: Wed. Nov. 18, 2020 6:31 pm
- Location: New Ringgold, PA
- Stoker Coal Boiler: Allen 700 stoker
- Hand Fed Coal Stove: Gibralter MCC
- Coal Size/Type: Buck in the Allen and anything goes in the MCC, Anthracite
- Other Heating: None, maybe some wood in the MCC in the shoulder season
insert in flue before the baro.
- nepacoal
- Member
- Posts: 1516
- Joined: Wed. Nov. 21, 2012 7:49 am
- Location: Coal Country
- Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
- Hand Fed Coal Boiler: Harman SF-260 - retired
- Coal Size/Type: Buck
Typical stokers need to use over fire air to set the draft. I don't know how Alaska does it, but Keystoker has a hole in the fire door of their boilers, and usually has a set screw in the ash doors of their stoker stoves to check the over fire draft. Keystoker specifies between-.02 to -.03 for theirs. Draft in the stovepipe doesn't really mean anything with a typical stoker unless you have a direct vent or are having trouble setting your over fire draft with a chimney. I've had my stoker going on 7 years and have never needed to check the draft in my stovepipe. I keep my over fire draft right at -.02 (after a long run so the chimney is up to operating temperature).