24 f outside
Min 5
Max 20
CFM 37
Ran the stove for a few days with no problem this morning at 6am the CO detector in the living room went off. The bedroom was reading 45 ppm
I shut down the coal stove and switched to oil.
Any ideas?
CO detectors went off early this morning LL econo 1
- WNY
- Member
- Posts: 6300
- Joined: Mon. Nov. 14, 2005 8:40 am
- Location: Cuba, NY
- Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
- Coal Size/Type: Rice
- Contact:
is your CO detector new?
Check your chimney for any blockages/snow, etc...
check your draft, you should always use a gauge to set it correctly. .02-.04
whats your baro damper setting at? or do you have a power vent?
check all motors, gaskets, etc... and make sure they are working properly
I thought most LL stoves use 6 and 40 on coaltrol
Check your chimney for any blockages/snow, etc...
check your draft, you should always use a gauge to set it correctly. .02-.04
whats your baro damper setting at? or do you have a power vent?
check all motors, gaskets, etc... and make sure they are working properly
I thought most LL stoves use 6 and 40 on coaltrol
- Tifford
- Member
- Posts: 81
- Joined: Sat. Mar. 04, 2017 7:58 pm
- Location: Central NY
- Stoker Coal Boiler: Econo 1 by Leisure Line
- Coal Size/Type: Rice
I have 2 CO detectors both were within point of eachother when the living room went off first.
No obstacles in the pipes that I can see.
No power vent
I have a leasure line econo 1 that I bought used to save some money. I thought I read somewhere (maybe on this forum) that the econo 1 should have its max backed off a bit.
I will try 6 and 40 tonight and see what happens.
No obstacles in the pipes that I can see.
No power vent
I have a leasure line econo 1 that I bought used to save some money. I thought I read somewhere (maybe on this forum) that the econo 1 should have its max backed off a bit.
I will try 6 and 40 tonight and see what happens.
- McGiever
- Member
- Posts: 10122
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
CO monitors going off due to draft being out of adjustment…Coal trol settings doesn’t fix that!!
With out a manometer to set draft properly your are flying blindfolded.
Dwyer Mark II 25
With out a manometer to set draft properly your are flying blindfolded.
Dwyer Mark II 25