Post Reply
 
Soccer918843
Member
Posts: 114
Joined: Thu. Aug. 27, 2020 11:44 am

Post by Soccer918843 » Tue. Jan. 18, 2022 7:19 am

My hitzer 608 will not stay stay lit and running I’ll get it going and it will start fine and get a roaring bed of coals going but when it dials itself down it goes out everytime I use to be fine with minimum feed at 6 but I have turned it up to 8 and it’s still going out on my what could be the issue thanks

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Jan. 18, 2022 8:22 am

Not much to go on here, but venture a guess of accuumulated fines under the grates and/or degraded grate gasket now leaking air. Has your stove been serviced since new?

 
Soccer918843
Member
Posts: 114
Joined: Thu. Aug. 27, 2020 11:44 am

Post by Soccer918843 » Tue. Jan. 18, 2022 8:44 am

I did clean out the fine ashes yesterday and it has went out twice since then. I’m going to replace the door gasket to rule that out and look at the grate gasket as well


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Jan. 18, 2022 8:54 am

The fines refered to were the black coal fines that sift down thru grate holes and acuumulate...not ash fines.

Does this have the Coal-trol?

 
Soccer918843
Member
Posts: 114
Joined: Thu. Aug. 27, 2020 11:44 am

Post by Soccer918843 » Tue. Jan. 18, 2022 9:29 am

Thanks sorry ya that’s what I meant u took the grate off and vacuumed underneath and cleaned the holes out as well

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Jan. 18, 2022 12:28 pm

Okay, found out some more of you set-up's details...

Post by Soccer918843 - Hitzer 608


 
Soccer918843
Member
Posts: 114
Joined: Thu. Aug. 27, 2020 11:44 am

Post by Soccer918843 » Tue. Jan. 18, 2022 8:47 pm

I called hitzer talked to Dean very knowledgeable man. So after going over some things with him my wiring on the fans were wired backwards the fan underneath the bed Of coals would shut off once up to temp and choke out. Which is what the front blower fan should be doing got them swapped around and seems great now. It use to be such a task getting a fire started now ik getting good air blowing through the grates it was very simple

Attachments


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Jan. 18, 2022 10:42 pm

Glad you were able to get the help you needed!