EFM 520 coal stove pipe won't heat up

Post Reply
 
bgleockler
Member
Posts: 21
Joined: Tue. Dec. 24, 2019 9:02 am
Location: Lansford, PA

Post by bgleockler » Wed. Dec. 30, 2020 1:16 pm

The last issue was fixed by replacing the timer, but now there's another issue that's been happening lately.

Sometimes the pipes won't heat up until I put more water in the stove. It heats up the pipe coming directly up from the stove, but won't go past that until I put more water in.
The water isn't low when this happens, it just won't heat up.

Included picture of the stove and pipe, the part coming out of the stove heats up, but doesn't go past it.
Is not a constant issue, just happened a few times recently.

Attachments

IMG_20201230_124903.jpg
.JPG | 215.2KB | IMG_20201230_124903.jpg

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Dec. 30, 2020 1:25 pm

Typically when the pipes don't heat up in a steam system it is because the vent(s) are not working. If the air can't get out, the steam can't get in the pipes.

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Wed. Dec. 30, 2020 2:11 pm

You could try purging built-up sediment from the LWCO.

Mike

 
bgleockler
Member
Posts: 21
Joined: Tue. Dec. 24, 2019 9:02 am
Location: Lansford, PA

Post by bgleockler » Wed. Dec. 30, 2020 2:19 pm

Does that mean just draining the water out?


 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Thu. Dec. 31, 2020 4:39 pm

My suggestion was for the low water cut-off only, so you shouldn't need to drain the whole system for that. At least some of the old school ones had integral drains; I have no clue about the others. Though steam systems generally tend to produce a lot of sediment, it's usually possible to keep it under control if you periodically release a little water from drains at low points in the near-boiler return piping.

Mike

 
ziggy87
Member
Posts: 311
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Fri. Jan. 01, 2021 11:31 pm

You might have a possible bad low water cut off (Levi), or a blocked return pipe. Can you take a picture of your lwco please. How often do you need to add water?

 
User avatar
Dakotaguy
Member
Posts: 134
Joined: Sun. Nov. 15, 2015 8:33 pm
Location: Summit hill pa
Stoker Coal Boiler: Efm 520 highboy
Coal Size/Type: Lots of rice from Lehigh
Other Heating: Pops 2010 df 520 stoker

Post by Dakotaguy » Fri. Jan. 08, 2021 10:45 pm

If you need help I'm 5 minutes away from you my parents have steam heat pretty simple but I will help if you need

Post Reply