EFM 520 coal stove won't stop running

Post Reply
 
bgleockler
Member
Posts: 21
Joined: Tue. Dec. 24, 2019 9:02 am
Location: Lansford, PA

Post by bgleockler » Mon. Dec. 28, 2020 9:11 am

What would cause the stove to not stop running?
The heat is turned down on both thermostats, the timer is running like it's supposed to be off on the box, but the stove runs continuously.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Dec. 28, 2020 9:36 am

Failed timer or stuck relay is most likely. Should be easy to tell with a multimeter.

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Mon. Dec. 28, 2020 9:44 am

I had a thermostat go bad and it ran continuously... Can just disconnect thermostat wires at either end to test.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Dec. 28, 2020 9:48 am

one possibility...If Timer failed in the "run cycle" nudge rotating tripper plate manually will let aquastat then regain control again..
Timer will need repaired/replaced to run in mild weather w/o having a "out-fire".
Last edited by McGiever on Mon. Dec. 28, 2020 10:29 pm, edited 1 time in total.


 
bgleockler
Member
Posts: 21
Joined: Tue. Dec. 24, 2019 9:02 am
Location: Lansford, PA

Post by bgleockler » Mon. Dec. 28, 2020 11:36 am

Ok thanks for the help

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. Dec. 28, 2020 2:08 pm

The boiler doesn't run off the thermostat. It's runs off of the water temperature in the vessel. If it is running beyond the high setpoint it most likely is the timer or the aquastat high limit switch is bad.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Dec. 30, 2020 1:23 pm

coaledsweat wrote:
Mon. Dec. 28, 2020 2:08 pm
The boiler doesn't run off the thermostat. It's runs off of the water temperature in the vessel. If it is running beyond the high setpoint it most likely is the timer or the aquastat high limit switch is bad.
It is a steam boiler. It will run indefinitely if the thermostat calls for heat and the pressurtrol doesn't trip.