Post by McMillan2015 » Wed. Sep. 30, 2020 4:41 pm

*posted in another board but not sure if I used the right one.

Hello! I'm completely new to coal. I've been researching and researching and starting to feel overwhelmed so...here is the deal:

Bought a 1871 farmhouse last winter. Roughly 1600 sq ft of living space with 2 floors and an unfinished basement. Lived off space heaters and baseboard heaters upstairs. We were COLD. We had our pipes freeze 3 times between December and April. Our basement is a walkout basement. Chimney is unusable due to the new roof being built over top of it. We have an old oil furnace that vented through the chimney and all ductwork still available.

So, my questions is...would a hyfire 180 or keystoker koker be best? Or is there another option to consider?


 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Sep. 30, 2020 6:56 pm

Welcome to the forum Mc,

Since you listed stoker stoves/furnaces I moved you question to that section.

I moved into a similar house years ago and my solution was a Harman MK2. It heated my 800 sq ft house built in 1816 completely. There was no other heat source. This Harman is a hand fired stove though.

A HyFire 180 or a Koker 160 should have more than enough BTU to heat your house. The question would be, can you move the heat around to the rest of the house?

-Don

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Wed. Sep. 30, 2020 8:58 pm

1600 sq ft of living space with burner in the basement might actually mean you're heating 3200 sq ft of 1871 Farm House and that is a horse of a different color...

 
McMillan2015
New Member
Posts: 11
Joined: Tue. Sep. 29, 2020 3:48 pm
Other Heating: Baseboard electric, kerosene heater

Post by McMillan2015 » Wed. Sep. 30, 2020 10:15 pm

StokerDon wrote:
Wed. Sep. 30, 2020 6:56 pm

A HyFire 180 or a Koker 160 should have more than enough BTU to heat your house. The question would be, can you move the heat around to the rest of the house?

-Don
We have all the ductwork still from the furnace. We should be able to tap into that, yes?
I have no idea what the difference is with a hand fired stove vs kokers. I've never been exposed to coal other than one time, 20 years ago, at a friend's house we played in the coal bin- it was a terrible idea, haha.

 
McMillan2015
New Member
Posts: 11
Joined: Tue. Sep. 29, 2020 3:48 pm
Other Heating: Baseboard electric, kerosene heater

Post by McMillan2015 » Wed. Sep. 30, 2020 10:18 pm

McGiever wrote:
Wed. Sep. 30, 2020 8:58 pm
1600 sq ft of living space with burner in the basement might actually mean you're heating 3200 sq ft of 1871 Farm House and that is a horse of a different color...
Our upstairs we have baseboards in and could really make do with just some additional heat I think. The main floor and basement need more of the heat due to only 2 baseboards downstairs and none in the basement. Our electric isn't outrageous here but it is when you use space heaters for 5 months (like we did last year). There is a noticeable difference in heat movement when the door to the stairs going upstairs is opened or closed as well. So I imagine we can regulate the movement a fair amount. I do think we need more than 90k or 110k. Thats why I'm leaning more toward the hyfire currently because we could get the heat jacket and vent some upwards and decide how much goes into the basement. Keeping it above freezing would be preferred. We really can't afford too high of a price currently so thats another factor.

 
coalder
Member
Posts: 1501
Joined: Mon. Dec. 16, 2013 1:48 pm
Location: somewhere high in the catskill mountains
Hand Fed Coal Boiler: harman sf 160
Coal Size/Type: Nut
Other Heating: wood parlor stove

Post by coalder » Thu. Oct. 01, 2020 8:40 am

Not for nothing, if your old chimney if relatively sound it is no big deal to cut out the roof, where chimney is and extend it. Then you could do whatever you want. Worst case scenario it may require a ss liner. In which case I would look into "Olympia chimney supply". www.olympiachimney.com
They offer a SS 316-L liner that they claim is guaranteed for life even with coal.
Just a thought
Jim

 
McMillan2015
New Member
Posts: 11
Joined: Tue. Sep. 29, 2020 3:48 pm
Other Heating: Baseboard electric, kerosene heater

Post by McMillan2015 » Thu. Oct. 01, 2020 11:32 am

coalder wrote:
Thu. Oct. 01, 2020 8:40 am
Not for nothing, if your old chimney if relatively sound it is no big deal to cut out the roof, where chimney is and extend it. Then you could do whatever you want. Worst case scenario it may require a ss liner. In which case I would look into "Olympia chimney supply". www.olympiachimney.com
They offer a SS 316-L liner that they claim is guaranteed for life even with coal.
Just a thought
Jim

I can ask around about that. We aren't entirely sure of the integrity of the chimney above the second floor. I imagine it is ok but not sure how much that would cost to do.


 
coalder
Member
Posts: 1501
Joined: Mon. Dec. 16, 2013 1:48 pm
Location: somewhere high in the catskill mountains
Hand Fed Coal Boiler: harman sf 160
Coal Size/Type: Nut
Other Heating: wood parlor stove

Post by coalder » Thu. Oct. 01, 2020 1:44 pm

Most chimneys take a real beating from the flashing up, due to weather exposure. Below the flashing is usually fine. Can you take a photos of the chimney especially where it terminates near the roof & check for the presence of a flue? Like they say, "a picture is worth a thousand words".
Jim

 
McMillan2015
New Member
Posts: 11
Joined: Tue. Sep. 29, 2020 3:48 pm
Other Heating: Baseboard electric, kerosene heater

Post by McMillan2015 » Thu. Oct. 01, 2020 1:47 pm

coalder wrote:
Thu. Oct. 01, 2020 1:44 pm
Most chimneys take a real beating from the flashing up, due to weather exposure. Below the flashing is usually fine. Can you take a photos of the chimney especially where it terminates near the roof & check for the presence of a flue? Like they say, "a picture is worth a thousand words".
Jim
Probably not. The chimney is exposed in the basement. When we gutted the kitchen we exposed it but decided to enclose it with sheetrock again. Second floor it is enclosed with sheetrock and there is no roof/attic access.

 
coalder
Member
Posts: 1501
Joined: Mon. Dec. 16, 2013 1:48 pm
Location: somewhere high in the catskill mountains
Hand Fed Coal Boiler: harman sf 160
Coal Size/Type: Nut
Other Heating: wood parlor stove

Post by coalder » Thu. Oct. 01, 2020 3:51 pm

You can tell if the chimney has a liner by looking through the thimble or clean out door. If it does & the chimney is sound It would be well worth the money & effort to cut an attic entry in the sheetrock, then cut a chase through the roof & raise the chimney. This would afford you an opportunity to put a coal boiler in the basement & heat your entire house along with DHW. I know it sounds like a lot; but you will appreciate it long term.
Jim

 
McMillan2015
New Member
Posts: 11
Joined: Tue. Sep. 29, 2020 3:48 pm
Other Heating: Baseboard electric, kerosene heater

Post by McMillan2015 » Thu. Oct. 01, 2020 5:16 pm

coalder wrote:
Thu. Oct. 01, 2020 3:51 pm
You can tell if the chimney has a liner by looking through the thimble or clean out door. If it does & the chimney is sound It would be well worth the money & effort to cut an attic entry in the sheetrock, then cut a chase through the roof & raise the chimney. This would afford you an opportunity to put a coal boiler in the basement & heat your entire house along with DHW. I know it sounds like a lot; but you will appreciate it long term.
Jim
Just had the guy in that would do the install. He believes they dropped the excess chimney bricks from above the roof down the chimney.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Thu. Oct. 01, 2020 7:01 pm

I'm not sure what you are planning, stoker, hand fired, boiler or furnace but either way, you will need a chimney.

-Don

 
McMillan2015
New Member
Posts: 11
Joined: Tue. Sep. 29, 2020 3:48 pm
Other Heating: Baseboard electric, kerosene heater

Post by McMillan2015 » Thu. Oct. 01, 2020 7:08 pm

StokerDon wrote:
Thu. Oct. 01, 2020 7:01 pm
I'm not sure what you are planning, stoker, hand fired, boiler or furnace but either way, you will need a chimney.

-Don
I thought without a chimney you direct vent?

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Thu. Oct. 01, 2020 7:19 pm

McMillan2015 wrote:
Thu. Oct. 01, 2020 7:08 pm
I thought without a chimney you direct vent?
In my opinion, direct vent and power vent are no where near as good as a chimney. Besides that, it limits you to small, flat great stokers. They also require a lot of maintenance.

A solid fuel heating unit requires a constant draft. A chimney will provide this constant draft naturally. If you have no chimney and are using a powered ventilating system, it has to run 24/7. Any motor or fan blade running in a flyash filled environment 24/7 will need cleaning very often.

-Don

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Oct. 01, 2020 9:56 pm

McMillan2015 wrote:
Thu. Oct. 01, 2020 7:08 pm
I thought without a chimney you direct vent?
That there is dealer talk to make a sale. :roll: