last year i bought a house and it had a wood stove hooked to masonry chimney. after 1 season of that nonsense im thinking about switching to a rice coal stoker stove. can i just hook that right to the exsisting masonry chimney? i see all these options power vent and direct vent. I just want to make sure i do it right and safe. any help would be great.


 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Mon. Sep. 09, 2019 4:49 pm

Using a masonry chimney is the preferred way, provide it is in good shape. An interior chimney would be best.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Sep. 09, 2019 5:20 pm

mmadsen23 wrote:
Mon. Sep. 09, 2019 2:31 pm
last year i bought a house and it had a wood stove hooked to masonry chimney. after 1 season of that nonsense im thinking about switching to a rice coal stoker stove. can i just hook that right to the exsisting masonry chimney? i see all these options power vent and direct vent. I just want to make sure i do it right and safe. any help would be great.
You're in good shape with a masonry chimney! :D

If you thought burning wood was nonsense be glad you don't need any power-vent or direct-vent! :baby:

 
mmadsen23
New Member
Posts: 6
Joined: Mon. Sep. 09, 2019 2:15 pm
Hot Air Coal Stoker Stove: keystoker 105
Coal Size/Type: rice

Post by mmadsen23 » Mon. Sep. 09, 2019 5:59 pm

Thanks guys, i just dont really want any problems that could be prevented from the start! One more ?. do i need to use stainless steel pipe from the stove to the chimney?

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Sep. 09, 2019 6:59 pm

mmadsen23 wrote:
Mon. Sep. 09, 2019 5:59 pm
One more ?. do i need to use stainless steel pipe from the stove to the chimney?
NO! A masonry chimney needs no metal liner, no matter what your chimney sweep tells you.

The best way to vent a coal heating appliance is with a regular, old fashion, masonry chimney. No metal liners, no power vents, no direct vents, just natural draft from the chimney you already have is the best thing.

With a coal stove, the masonry chimney hardly ever needs cleaning. You will have to clean the stove pipe once in a while.

-Don

 
User avatar
Rob R.
Site Moderator
Posts: 17978
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Sep. 09, 2019 7:34 pm

Regular black stove pipe is all that is needed to connect the stove to the chimney. Make sure it has the proper clearance to combustibles and put 3 screws in each joint.

The coal stove will dry out all the creosote in your chimney and it will begin flaking off. If the chimney is reasonably clean I would plan on cleaning it in the spring after your first coal-fired winter. If the chimney hasn't been cleaned in a while, it would probably be best to have it cleaned before you fire up the coal stove.

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Mon. Sep. 09, 2019 8:17 pm

mmadsen23 wrote:
Mon. Sep. 09, 2019 5:59 pm
Thanks guys, i just dont really want any problems that could be prevented from the start! One more ?. do i need to use stainless steel pipe from the stove to the chimney?
Most people use single wall black pipe between the stove and chimney. Some of the old timers like my FIL still use galvanized for stoker boilers. SS will work but probably won't blend in as well as black pipe.


 
mmadsen23
New Member
Posts: 6
Joined: Mon. Sep. 09, 2019 2:15 pm
Hot Air Coal Stoker Stove: keystoker 105
Coal Size/Type: rice

Post by mmadsen23 » Mon. Sep. 09, 2019 10:45 pm

Thanks again everybody. I feel more comfortable now about doing it right!

 
User avatar
Richard S.
Mayor
Posts: 15183
Joined: Fri. Oct. 01, 2004 8:35 pm
Location: NEPA
Stoker Coal Boiler: Van Wert VA1200
Coal Size/Type: Buckwheat/Anthracite

Post by Richard S. » Tue. Sep. 10, 2019 6:33 am

mmadsen23 wrote:
Mon. Sep. 09, 2019 2:31 pm
can i just hook that right to the exsisting masonry chimney?
Make sure the chimney is cleaned. It doesn't have to be perfect but if there is a lot of creosote buildup you want to try and remove it. Two issues.... firstly coal will "dry out" the creosote and it will eventually fall off potentially blocking the flue. There has been posts in the past of people reporting very large sheets of it falling off. Secondly if the creosote is still present a chimney fire can still occur, if you have a barometric damper which is standard for coal stoker you now have a chimney fire on steroids.

Once the creosote is removed there is of course no possibility of a chimney fire.

 
gael
Member
Posts: 35
Joined: Tue. Dec. 27, 2022 3:04 am

Post by gael » Fri. Jan. 27, 2023 4:08 am

hi guys,

i got à ciney coal stove 102, with 3.14" back collar, so if read your post,

i have à masonry chimney of 23 feets high,
35 inch on 15". i do not need to put A liner in it???
there is no any danger of chimney fire or monoxyde carbon intoxication ???

 
User avatar
Idlorah
Member
Posts: 520
Joined: Wed. Nov. 18, 2020 6:31 pm
Location: New Ringgold, PA
Stoker Coal Boiler: Allen 700 stoker
Hand Fed Coal Stove: Gibralter MCC
Coal Size/Type: Buck in the Allen and anything goes in the MCC, Anthracite
Other Heating: None, maybe some wood in the MCC in the shoulder season

Post by Idlorah » Fri. Jan. 27, 2023 5:01 pm

gael wrote:
Fri. Jan. 27, 2023 4:08 am
hi guys,

i got à ciney coal stove 102, with 3.14" back collar, so if read your post,

i have à masonry chimney of 23 feets high,
35 inch on 15". i do not need to put A liner in it???
there is no any danger of chimney fire or monoxyde carbon intoxication ???
I have my hand fired stove in a brick chimney with no liner and I have no issues. you should be okay.

 
waytomany?s
Member
Posts: 3746
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Fri. Jan. 27, 2023 8:58 pm

gael wrote:
Fri. Jan. 27, 2023 4:08 am
hi guys,

i got à ciney coal stove 102, with 3.14" back collar, so if read your post,

i have à masonry chimney of 23 feets high,
35 inch on 15". i do not need to put A liner in it???
there is no any danger of chimney fire or monoxyde carbon intoxication ???
You don't need a liner IN it. You DO need to run your pipe up past the chimney damper plate and seal around it.

 
gael
Member
Posts: 35
Joined: Tue. Dec. 27, 2022 3:04 am

Post by gael » Sat. Jan. 28, 2023 9:23 am

I'm surprise because i did make à hole in the chimney to check
IMG_20230128_142018.jpg
.JPG | 268KB | IMG_20230128_142018.jpg
and it's full of créosote...
IMG_20230128_141905.jpg
.JPG | 400.7KB | IMG_20230128_141905.jpg
so I'm gonna reopen fully, sweep it, but without liner in it I'm really surprised i find it very risky

 
gael
Member
Posts: 35
Joined: Tue. Dec. 27, 2022 3:04 am

Post by gael » Sun. Jan. 29, 2023 12:29 pm

but i got one More question.

i désire to burn both coal and wood..
so for coal you are saying no liner inside the chimney.
but for wood i would need a liner in it right?
so if i burn both it's better to line the chimney, (i'm not gonna take on and take off all the time) if so, do i have to use à 3.14" pipe and liner same as my stove exhaust or do i have to put an adaptator and go on 6" liner?

 
waytomany?s
Member
Posts: 3746
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Sun. Jan. 29, 2023 7:24 pm

No liner in chimney for either. You do have to get your pipe up into chimney past the chimney damper. We're you able to.do that?