Decreasing Draft without Baro Damper

Post Reply
 
mxadkins
New Member
Posts: 4
Joined: Wed. Jan. 30, 2019 5:39 pm
Hot Air Coal Stoker Stove: Hearth 90k

Post by mxadkins » Wed. Jan. 30, 2019 5:47 pm

Hello Everyone,

I just bought a new home that uses a Keystoker Hearth 90k Stove. In my neediness and from reading posts hear I have permanently installed a Magnehelic on the stove checking draft over the fire and I am getting .04-.05 readings. My combustion motor is wide open and I don’t have a baro damper as the Hearth is running directly to chimney at bottom of stove. To decrease the draft I only see two options:

1) Install a higher CFM combustion motor

2) “Manually” damper the chimney a bit

Anything I’m missing? Any concerns with manual damper?

Thanks for the help and input.

 
User avatar
coaledsweat
Site Moderator
Posts: 13767
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Jan. 30, 2019 5:52 pm

Why do you want to reduce the draft?

 
mxadkins
New Member
Posts: 4
Joined: Wed. Jan. 30, 2019 5:39 pm
Hot Air Coal Stoker Stove: Hearth 90k

Post by mxadkins » Wed. Jan. 30, 2019 6:04 pm

Keystoker recommends .02 -.03


 
User avatar
Lightning
Site Moderator
Posts: 14669
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Wed. Jan. 30, 2019 8:03 pm

Pushing more combustion air thru the stove just to lower the pressure is not the answer. It will take heat up the chimney with it.

 
franco b
Site Moderator
Posts: 11417
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Wed. Jan. 30, 2019 9:33 pm

You could install a baro directly into the chimney.

The manufacturers recommendation is probably a minimum.

 
User avatar
CoalisCoolxWarm
Member
Posts: 2323
Joined: Wed. Jan. 19, 2011 11:41 am
Location: Western PA
Stoker Coal Boiler: Keystoker KA-6
Hand Fed Coal Furnace: old Sears rebuilt, bituminous- offline as of winter 2014
Coal Size/Type: Anthracite Buckwheat
Other Heating: Oil Boiler

Post by CoalisCoolxWarm » Wed. Jan. 30, 2019 10:10 pm

Lightning wrote:
Wed. Jan. 30, 2019 8:03 pm
Pushing more combustion air thru the stove just to lower the pressure is not the answer. It will take heat up the chimney with it.
^^This^^

Using a baro will still "allow the chimney to take the air it wants" except it uses some of the room air at 60F-75F (usually) to mix in with the high temp air from the fire (150F-200F or more).

If the entire volume of air going up the chimney is the hotter air from the firebox, guess where the BTUs are going instead of heating your home ;)

Barometric dampers really are a simple wonder of the solid fuel burning field. Simple mechanism and automatic once it is set.


 
mxadkins
New Member
Posts: 4
Joined: Wed. Jan. 30, 2019 5:39 pm
Hot Air Coal Stoker Stove: Hearth 90k

Post by mxadkins » Wed. Jan. 30, 2019 10:36 pm

I agree a baro makes the most sense.. the issue is that I don’t think one can be installed because of my stove setup. The pipe from the stove goes directly into a brick chimney. And the stove is only 1/2” away from the brick.

 
mxadkins
New Member
Posts: 4
Joined: Wed. Jan. 30, 2019 5:39 pm
Hot Air Coal Stoker Stove: Hearth 90k

Post by mxadkins » Wed. Jan. 30, 2019 10:41 pm


 
User avatar
StanT
Member
Posts: 261
Joined: Fri. Aug. 29, 2008 5:10 am
Location: Ne Pa

Post by StanT » Thu. Jan. 31, 2019 2:01 pm

Block the combustion fan some. that will decrease the cfm going into the stove.
I use the register filters to decrease mine and it helps keep the fan blades clean.

Goof Luck, Stant