Distribution Motor Harman Stoke

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Mon. Jan. 14, 2019 8:26 am

Hi guys in a bit of panic, went downstairs to stoker and realized the distribution fan was not blowing felt it where the motor is and it was very hot. I unplugged it from the control box and tried another outlet no go, then waited about 15 min plugged it in and can hear the motor hum but no go.

A - it doesnt look like these fans have oil inlets
B - where can I find another fan locally, Lancaster County, PA here
C - for years I kept the fan alway plugged in no issues, this year I put both fans in the control box
D - of course now its getting really cold around here
E - what is the best solution as I figure an oem fan will cost $$$


 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Mon. Jan. 14, 2019 8:59 am

Is there a data plate on the fan? You can usually find a fasco or Dayton fan that will work.

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Mon. Jan. 14, 2019 9:22 am

There are oil ports, they are not obvious, just openings to run a few drops of oil down to the shaft.
20190114_091752.jpg
.JPG | 208.5KB | 20190114_091752.jpg
The replacement fan will need to have the same flange measurements to fit into the slots and be close to the 135cfm of the oem. I would think anything less than 200 cfm would be OK, you can always use a refrigerator magnetic to throttle down the input to it.

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Mon. Jan. 14, 2019 9:37 am

For local supply you can check with McCombs Supply to see if they have a wood/pellet stove dist blower with the same flange size. A quick look on their website shows a few in stock :yes:
....and quite a few out of stock. :no1:

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Mon. Jan. 14, 2019 10:01 am

the model id fasco 50752-500 - there is an online distributor that has that model it looks the same via the pic, but a question, I also looked at some on ebay and none of then have the cord\plug? is this something harman dis, put an electric cord on the end or do they normally come with one.

The motor you can hear but the squirrel cage doesnt move . there was some gunk on the fins not a tremendous amount but I cleaned\vacuumed no luck. also I never oiled the motor as I dont see where you would but maybe you need to?

I am not super electrical\motor inclined so some of this is foreign to me

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Mon. Jan. 14, 2019 10:09 am

titleist1 wrote:
Mon. Jan. 14, 2019 9:22 am
There are oil ports, they are not obvious, just openings to run a few drops of oil down to the shaft.

20190114_091752.jpg

The replacement fan will need to have the same flange measurements to fit into the slots and be close to the 135cfm of the oem. I would think anything less than 200 cfm would be OK, you can always use a refrigerator magnetic to throttle down the input to it.
you lost me at throttle down the input using refrig mag.

the fan is a fasco 50752-500 - there is a place online that seems to have sane motor but I need to call them. is it common to have to wire on a plug afterwards or do they come with one.

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Mon. Jan. 14, 2019 10:12 am

titleist1 wrote:
Mon. Jan. 14, 2019 9:22 am
There are oil ports, they are not obvious, just openings to run a few drops of oil down to the shaft.

20190114_091752.jpg

The replacement fan will need to have the same flange measurements to fit into the slots and be close to the 135cfm of the oem. I would think anything less than 200 cfm would be OK, you can always use a refrigerator magnetic to throttle down the input to it.
not obvious is an understatement, i considered putting a few drop dow. will do that now let it sit maybe it seized and will relubricate. wish i would have know this, stove is 12yrs old
I take it the combustion fan is same? I do oil auger motor


 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Mon. Jan. 14, 2019 11:01 am

The combustion fan has the same less than obvious oil ports.

You should be cleaning the squirrel cage fan blades periodically on both blowers too. I use q tips & whatever cleaning solution is handy and do it toward the end of Jan. I have spare blowers, rotate to the clean ones and clean the dirty blades so they are ready for the beginning of the next year.

The refrigerator magnet can be used to block the intake on the distribution fan if you get a replacement blower that has way more cfm than the 135 on the oem. Sort of like the plate that is on the combustion blower. Not that you need to throttle it back, but the higher airflow may not be needed.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Jan. 14, 2019 11:20 am

Some lads have even drilled their own holes as oil ports to add a few drops of oil each season...

Search site here for Turbine Oil...great lube and comes w/ long tube extention to reach any spot.

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Mon. Jan. 14, 2019 11:30 am

call my original dealer, he couldnt find the part# or give me a cost. Mcombs is out of stock on their fan, I assume I will need to take the cord off the one I have a wire it to the new box? does that sound right. I am trying to broaden my search as its cold and I dont want to wait a week or more for parts to come in.

I just spoke to elecmotor.com and they have the fan in stock. I asked if this fan needs to be oild and was told no, they are pre oiled and when they go they go

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. Jan. 14, 2019 11:42 am

Ask, Sometimes there is a ball bearing, PSC equivalent that will fit...diff. model number

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Wed. Jan. 16, 2019 6:55 pm

McGiever wrote:
Mon. Jan. 14, 2019 11:42 am
Ask, Sometimes there is a ball bearing, PSC equivalent that will fit...diff. model number
I got an exact replacement at electricmotors.com with tx an shipping it was 101$

 
dcveem3
Member
Posts: 89
Joined: Sat. Jan. 20, 2018 6:44 pm
Location: NorthWest York Co, PA
Stoker Coal Boiler: Someday!
Hot Air Coal Stoker Stove: Harman Magnum (temp basement duty)
Other Heating: Propane/Heat Pump

Post by dcveem3 » Wed. Jan. 16, 2019 8:56 pm

I ordered a larger one for mine. There's no way in my opinion, that blower is adequate at the stoves top 1/3 burn rate. Probably not an oversight for Harman since most of these stoves only run on the bottom 2/3 of their input.

Don

 
jimbo970
Member
Posts: 184
Joined: Sat. Oct. 14, 2006 9:20 am

Post by jimbo970 » Thu. Jan. 17, 2019 8:24 am

dcveem3 wrote:
Wed. Jan. 16, 2019 8:56 pm
I ordered a larger one for mine. There's no way in my opinion, that blower is adequate at the stoves top 1/3 burn rate. Probably not an oversight for Harman since most of these stoves only run on the bottom 2/3 of their input.

Don
what and where did you buy?

 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Thu. Jan. 17, 2019 5:52 pm

I use CRC Lectra-Motive cleaner and spray the entire fan including putting the red straw into the two oil ports to clear out any dirt in those ports. Then I lube with oil and oil monthly while in use. I have a fan going on 12 years so far.


Post Reply