Will this harm a dayton blower?

Post Reply
 
sitdwnandhngon
Member
Posts: 39
Joined: Fri. Jul. 20, 2018 7:26 pm
Hot Air Coal Stoker Stove: Alaska Stoker II

Post by sitdwnandhngon » Tue. Nov. 06, 2018 4:55 pm

So we have been very impressed so far with the Alaska Stoker I installed this summer. I was nervous at first since I am used to the coal furnace we had, so it was hotter shorter bursts of heat.

It takes about a whole day to bring the house and basement up to temperature (I've been running it two turns below the highest most of the fall, and had to shut it down twice because it was too warm in here) and it's keeping us very comfortable.

However, we lost our air filter when I pulled the furnace system out. Trying to get at least some filtration on the air going upstairs I slapped a shop vac filter on to the side of it. It slowed down the air flow noticably, but also brought up the stove temp about 50 degrees at the same low setting. So more heat, but less air, probably a wash for keeping the house warm.

Do you think it will hurt the blower at all though having the restriction from the filter on the supply side?

Image

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Tue. Nov. 06, 2018 5:41 pm

You already found out it slowed it down even being nice and clean, so maybe add a foam sleeve over the pleated filter to make it easy to later pop it off and rinse in sink with soapy water at regular interval.

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Tue. Nov. 06, 2018 5:48 pm

Build or buy a filter box...
The shop filter is too fine of a filter...
When it gets dirty ...
It will restrict the flow even more...
The box should hold a standard air filter...


 
sitdwnandhngon
Member
Posts: 39
Joined: Fri. Jul. 20, 2018 7:26 pm
Hot Air Coal Stoker Stove: Alaska Stoker II

Post by sitdwnandhngon » Tue. Nov. 06, 2018 6:10 pm

CapeCoaler wrote:
Tue. Nov. 06, 2018 5:48 pm
Build or buy a filter box...
The shop filter is too fine of a filter...
When it gets dirty ...
It will restrict the flow even more...
The box should hold a standard air filter...
I think I'll have to do that, I was just down there measuring. I still have the old old cold air return in place, I could adapt it probably.

I did a very scientific test with a balloon. The register without the filter pushes the balloon up 2 feet, with the filter it only pushes it about 1 inch.

 
User avatar
2001Sierra
Member
Posts: 2211
Joined: Wed. May. 20, 2009 8:09 am
Location: Wynantskill NY, 10 miles from Albany
Hot Air Coal Stoker Stove: Keystoker 90 Chimney vent
Coal Size/Type: Rice
Other Heating: Buderus Oil Boiler 3115-34

Post by 2001Sierra » Tue. Nov. 06, 2018 9:38 pm

CapeCoaler wrote:
Tue. Nov. 06, 2018 5:48 pm
Build or buy a filter box...
The shop filter is too fine of a filter...
When it gets dirty ...
It will restrict the flow even more...
The box should hold a standard air filter...
I too agree, get/make a box that interfaces with a larger pleated air filter. I use a 16 x 20 x2 pleated filter that filters the air going from the stove to the upstairs.