Hi everyone,
I'm still relatively new to the coal world. It's been a few years and have learned somethings but I need some help on this one.
I have a koker lite, direct vent. It took me about 2 years to get it burning hot and efficient. Initially my stove face temp was around 350. I could not get it to burn any hotter. After the two years and messing with the draft settings and coal feed, last year I finally got it burning hot around 550-600 on my face temp. My house was in the upper 70s -80s when burning full throttle in the dead of winter.
I fired it up yesterday, doing the same thing I always have. I'm back to not being able to burn over 380 face temp. My house is only sitting in the upper 60s and it's 45 degrees outside.
Checked my draft settings, exactly where they were last year, just a tad over -.03, the fire looks good but seems like there was a bit more ash then I had last year. Figuring I bumped the coal feed, I went to turn it up and it's pretty much maxed out. Thinking the bed was too thick I turned it back down, and my temperature dropped.
The cam is turning fine looks like the pusher is moving okay. I'm at a loss here. I took the grates out and cleaned underneath them as well. I just feel with the coal feed being maxed out I should be getting burning coals in the ash and it should be a lot hotter.
Just looking to run this by some people and see if there are any ideas. I'm wondering if my gear motor or something like that is starting to go. Thanks!


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Oct. 26, 2018 10:51 am

At end of last seaon, Did you tear down the whole exhaust system and clean everything and give motors a couple drops of oil?

One season of direct vent operation is like putting 200,000 miles on a car.
Last edited by McGiever on Fri. Oct. 26, 2018 10:57 am, edited 2 times in total.

 
Ttem27
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:06 am
Hot Air Coal Stoker Stove: Keystoker Koker Lite
Coal Size/Type: Rice

Post by Ttem27 » Fri. Oct. 26, 2018 10:54 am

Yep, gave it the normal cleaning that I always do. Before I start it up I always take another look just to make sure I didn't miss anything. I did my normal, I just can't figure this one out....

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Oct. 26, 2018 10:57 am

What position is the "L" handle at? Might need adjusted in or out...likely pulled out some.

 
Ttem27
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:06 am
Hot Air Coal Stoker Stove: Keystoker Koker Lite
Coal Size/Type: Rice

Post by Ttem27 » Fri. Oct. 26, 2018 11:00 am

your talking on the push bar?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Oct. 26, 2018 11:04 am

Ttem27 wrote:
Fri. Oct. 26, 2018 11:00 am
your talking on the push bar?
Your adjustment for exhaust...what goes out allows how much fire can get in up front.
Last edited by McGiever on Fri. Oct. 26, 2018 11:16 am, edited 1 time in total.

 
Ttem27
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:06 am
Hot Air Coal Stoker Stove: Keystoker Koker Lite
Coal Size/Type: Rice

Post by Ttem27 » Fri. Oct. 26, 2018 11:11 am

So I have an L-handle on the top of the stove near the vent fan - that I adjust for my draft. The only other thing that looks like an L on the stove is the coal feed screw on the push motor


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Oct. 26, 2018 11:15 am

Draft, that's it.

 
Ttem27
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:06 am
Hot Air Coal Stoker Stove: Keystoker Koker Lite
Coal Size/Type: Rice

Post by Ttem27 » Fri. Oct. 26, 2018 11:19 am

Ok I'm following you. That I have set with a manometer. Currently sitting at -.03, tried moving it a little bit but it's not giving me that extra burn temp. Literally have not changed anything on the stove, coal is also the same from last year.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Oct. 26, 2018 3:18 pm

Have to ask then, is that draft setting of -.03 only after a long half hour continuous burn? Short runs don't count for accurate draft setting.

Report back after you find your fix...maybe you cleaned your stove too clean, that seems to be the only difference from then and now. ;)

 
Ttem27
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:06 am
Hot Air Coal Stoker Stove: Keystoker Koker Lite
Coal Size/Type: Rice

Post by Ttem27 » Fri. Oct. 26, 2018 3:32 pm

It was running full throttle for a few hours before I checked it. Checked it again about an hour ago. Same thing -.03. Only thing I can possibly think of is that maybe some of the cement dried on the grates or they’re slightly uneven. I don’t know...just trying to think of what it could be

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Oct. 26, 2018 3:33 pm

If it's not putting out enough heat, and the fire looks on the small side, and you think the feed rate is near max, the nylon cam is probably melted. This will cause a very short stroke of the stoker.

With these stoves you should always have a spare set of nylon screws and a nylon cam. Simple to replace but if this happens in January, on a Friday night and you have to order them from Keystoker, it could get very cold.

-Don

 
Ttem27
Member
Posts: 27
Joined: Sun. Dec. 21, 2014 8:06 am
Hot Air Coal Stoker Stove: Keystoker Koker Lite
Coal Size/Type: Rice

Post by Ttem27 » Sat. Oct. 27, 2018 12:51 am

Good to know, I'll have to get a whole new set and see what happens - thanks, - I'll let you know how I make out

 
NickG
Member
Posts: 24
Joined: Sun. Feb. 19, 2023 8:51 pm
Stoker Coal Boiler: Keystoker Lite
Coal Size/Type: Rice
Other Heating: Oil and wood

Post by NickG » Sun. Feb. 19, 2023 9:28 pm

I know this thread is old but I’m having the same issue. Did you figure it out? Thank you

 
waytomany?s
Member
Posts: 3747
Joined: Fri. Aug. 16, 2019 3:02 pm
Location: Oneida, N.Y.
Hand Fed Coal Stove: Harmon Mark II
Hand Fed Coal Furnace: Looking
Baseburners & Antiques: Looking
Coal Size/Type: Nut
Other Heating: newmac wood/coal combo furnace

Post by waytomany?s » Mon. Feb. 20, 2023 3:48 pm

NickG wrote:
Sun. Feb. 19, 2023 9:28 pm
I know this thread is old but I’m having the same issue. Did you figure it out? Thank you
Welcome Nick. Go ahead and start a new thread, you will probably have better luck getting answers that way.