Post by HarrisK » Sat. Sep. 29, 2018 10:10 pm

Been searching the forum for quite some time and haven’t really found a concrete answer. I have a question regarding the horizontal length of chimney for a Harman magnum stoker. Where I want to position the stoker is about 12 feet away from an existing masonary chimney. Any advice on if this will work would be great. It will have a pretty good pitch as to where it will tie into chimney is about 8ft high. The existing chimney is 22 feet.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Sep. 30, 2018 10:33 am

As discribed it will work, but, be forewarned, more horizontal pipe will gather more fly ash. So make pipe easy for inspections and accessable for cleaning out.. Tee's with a cap used where a 90 would've been.

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Sun. Sep. 30, 2018 12:34 pm

Thank you for the reply. Is there any rule as to how much horizontal is permissible inside a home?

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sun. Sep. 30, 2018 1:58 pm

The longer the horizontal run, the higher the chimney should be. No formula that I know of but expect to clean it A LOT! 12' is a bunch for a 22' chimney. Is the chimney interior or exterior?

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Sun. Sep. 30, 2018 4:17 pm

It is exterior

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sun. Sep. 30, 2018 5:25 pm

Why does it have to be so far away? Ductwork issue?

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Sun. Sep. 30, 2018 6:16 pm

If I move it closer it will have to go in the separate furnace room. I’m looking to use the radiant heat for the finished basement and potentially duct the heat upstairs. Plus I would like to have the aesthetic look of the stove in the occupied area.


 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Mon. Oct. 01, 2018 8:19 am

With such a long horizontal run I would suggest a manometer permanently installed to watch the draft as the temps change. You may find you need to run the stove 'hotter' during periods that have lots of idle time to keep the draft. That would just mean less time between timer runs or longer timer run times. You would burn a little more coal but knowing the draft would be fine would be worth it to me. This might only be necessary when temps are above a certain point. The manometer will help by giving the draft numbers during different burn conditions.

The fly ash will lay in that horizontal run and need to be cleaned. I would check the pipe after each ton of coal burned to see what the build up looked like and then plan to clean it accordingly. in addition to using a T instead of a 90, putting a T sideways in the middle of the 12' run so you can pop off the cap and take a look and also clean it through there may be a good idea.

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Mon. Oct. 01, 2018 8:44 am

Yes I notice with my other hand fed stove that if the temps are up during the day it does not burn as well I figured due to the draft. Where does one usually install the manometer? I like the idea of a sideways T I didn’t think of that one. Thank you for the reply.

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Mon. Oct. 01, 2018 9:58 am

Also can anyone post the dimensions of the magnum stoker ash pan. I need to have one made up and I can’t seem to find the size anywhere. I would rather get one made or make my own then spend 150+ on one from Harman dealer

 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Mon. Oct. 01, 2018 1:47 pm

The Magnum ash pan is 17.25" x 13.25" x 7.5" high... at least that is what mine measures.

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Oct. 01, 2018 2:27 pm

I have about 12' of flue pipe on my boiler, with a few feet of rise from one end to the other. I clean the flyash out twice per year, and the boiler works well.

 
urhstry
Member
Posts: 44
Joined: Wed. Nov. 04, 2015 4:27 pm
Location: Elysburg, PA
Stoker Coal Boiler: Harman Verti-flow
Hand Fed Coal Boiler: Harman Mark III
Coal Size/Type: pea and nut
Other Heating: OWB

Post by urhstry » Mon. Oct. 01, 2018 2:53 pm

I have already taken my 4 feet of horizontal run off as the unit was running, dumped it into ash pan and put it right back in. One minute, tops. Not suggesting you do that but it worked for me when my airflow decreased.

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Mon. Oct. 01, 2018 3:56 pm

That’s what I like to hear. Real world experience. I know every scenario is different and I “think” it will work in my case but that being said I’m not an expert on coal burning like the members here. So I just wanted to get some advice.

 
HarrisK
New Member
Posts: 8
Joined: Fri. Aug. 31, 2018 1:09 pm
Hot Air Coal Stoker Stove: Harman magnum
Hand Fed Coal Stove: Harman magnafire
Coal Size/Type: Rice / nut
Other Heating: Oil burner

Post by HarrisK » Mon. Oct. 01, 2018 3:56 pm

urhstry wrote:
Mon. Oct. 01, 2018 1:47 pm
The Magnum ash pan is 17.25" x 13.25" x 7.5" high... at least that is what mine measures.
Thank you for the measurements