Hot Air Coal Stoker Furnace: Koker lite- house. Reading- garage
Coal Size/Type: Rice
Other Heating: Oil

Post by Benny » Wed. Jul. 25, 2018 10:23 am

My son is going to power vent because of draft issues, we got power vent, fume switch and rheostat, also going to order a dywer . Any advice is greatly appreciated, thanks

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Jul. 28, 2018 11:18 am

Is it the Fields SWR?

 
Benny
Member
Posts: 374
Joined: Sat. Nov. 11, 2017 6:32 am
Location: Ligonier Pa.
Hot Air Coal Stoker Furnace: Koker lite- house. Reading- garage
Coal Size/Type: Rice
Other Heating: Oil

Post by Benny » Sat. Jul. 28, 2018 11:57 am

Yes it is 4 inch

 
Benny
Member
Posts: 374
Joined: Sat. Nov. 11, 2017 6:32 am
Location: Ligonier Pa.
Hot Air Coal Stoker Furnace: Koker lite- house. Reading- garage
Coal Size/Type: Rice
Other Heating: Oil

Post by Benny » Sat. Jul. 28, 2018 12:56 pm

Sorry, SWG 4HDs 4” SS


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Jul. 28, 2018 10:33 pm

Perfect! :yes:
Study Up
PowerVent Installation

 
Benny
Member
Posts: 374
Joined: Sat. Nov. 11, 2017 6:32 am
Location: Ligonier Pa.
Hot Air Coal Stoker Furnace: Koker lite- house. Reading- garage
Coal Size/Type: Rice
Other Heating: Oil

Post by Benny » Mon. Jul. 30, 2018 5:39 am

Thank you McGiever, will do can you suggest a rheostat for fan speed?

 
flyboydale54
New Member
Posts: 8
Joined: Wed. Apr. 13, 2016 11:52 pm
Hot Air Coal Stoker Furnace: Leisure Line AK110 forced air stoker furnace
Coal Size/Type: Rice

Post by flyboydale54 » Thu. Nov. 29, 2018 3:24 pm

Benny wrote:
Wed. Jul. 25, 2018 10:23 am
My son is going to power vent because of draft issues, we got power vent, fume switch and rheostat, also going to order a dywer . Any advice is greatly appreciated, thanks
I have a brand new Dwyer Mark II Manometer. I have a Leisure Line AK-110 with 6" exhaust to Chimney exhaust. I would like to know exact details for installing it, such as where to connect it to on this furnace. You can view this rice coal furnace at www.leisurelinestove.com. I love the Dwyer unit and the high reviews on it, but I noticed the connections are plastic and I do not know where to mount this on my coal furnace. It seems to me that plastic connectors would melt with a coal furnace. If anyone that has a good working knowledge of this Manometer, I would appreciate explanations to where to connect this to on my furnace. Also, is the draft adjusted by the combustion blower where you move the plate to increase or restrict the air going to the underneath the coal, or the Barametric Damper on the Exhaust Pipe, or a little of both? Thank you. P.S. The 6" exhaust is located about the middle bottom of the side that goes through the blue side panel. The top door is made out of Cast Iron, so looking for a better place to mount the fitting through the furnace. Perhaps above or beside the top door if that is acceptable. That way I am only drilling through plate steel.
Product-AK-110-Hot-Air-Furnace.jpg
.JPG | 55.6KB | Product-AK-110-Hot-Air-Furnace.jpg
Last edited by flyboydale54 on Thu. Nov. 29, 2018 6:38 pm, edited 2 times in total.

 
xmanjeff
Member
Posts: 52
Joined: Thu. Apr. 09, 2015 7:41 pm
Location: niagara falls new york
Hot Air Coal Stoker Stove: keystoker 90 dv

Post by xmanjeff » Thu. Nov. 29, 2018 6:06 pm

I drilled and tapped a 10-32 hole in the side of my stove about 2 inches from bottom and 2 inches from front of stove and screwed in a 10-32x1/8 barbed fitting and just stuck the tube onto that


 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Thu. Nov. 29, 2018 6:27 pm

I used a bulkhead connector in my fire door connected to the manometer with high temp silicone tubing to monitor the over fire draft

Eaton Weatherhead 1074X4 Brass CA360 Mini-Barb Brass Fitting, Bulkhead Union, Straight, 1/4" Tube OD

Attachments

71Un5fbuo4L._SL1500_.jpg
.JPG | 102.9KB | 71Un5fbuo4L._SL1500_.jpg
Last edited by nepacoal on Thu. Nov. 29, 2018 6:44 pm, edited 1 time in total.

 
xmanjeff
Member
Posts: 52
Joined: Thu. Apr. 09, 2015 7:41 pm
Location: niagara falls new york
Hot Air Coal Stoker Stove: keystoker 90 dv

Post by xmanjeff » Thu. Nov. 29, 2018 6:36 pm

that would work perfectly, if you had a source with a part # ,im sure it would help a number of guys out , im sure msc or McMaster carr has these also

https://www.mscdirect.com/product/details/01795467

 
flyboydale54
New Member
Posts: 8
Joined: Wed. Apr. 13, 2016 11:52 pm
Hot Air Coal Stoker Furnace: Leisure Line AK110 forced air stoker furnace
Coal Size/Type: Rice

Post by flyboydale54 » Thu. Nov. 29, 2018 6:45 pm

xmanjeff wrote:
Thu. Nov. 29, 2018 6:36 pm
that would work perfectly, if you had a source with a part # ,im sure it would help a number of guys out , im sure msc or McMaster carr has these also

https://www.mscdirect.com/product/details/01795467
That look great xmanjeff. Problem is, I have a cast iron top door and that would not be the place to put this fitting, but I was thinking, after looking at the picture of my furnace I edited and put into my article, that I could safely drill through above the door, or beside the door and mount one of these bulkhead fasteners you have shown. That way I am only drilling through the plate steel in the firebox area. But then that brings about the question whether to the side of the door, above the door, centered or to the side? Also, does this clog frequently with flyash? :idea:
Last edited by flyboydale54 on Thu. Nov. 29, 2018 7:08 pm, edited 1 time in total.

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Thu. Nov. 29, 2018 6:56 pm

Page 11 step 15 in your manual talks about setting the draft with the probe in the flue pipe...

15. Check draft with draft meter. Or use instructions supplied with barometric damper if type with calibrated
scale. Draft should be set to between -0.03 to -0.05 between barometric damper and unit.

 
User avatar
WNY
Member
Posts: 6307
Joined: Mon. Nov. 14, 2005 8:40 am
Location: Cuba, NY
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Contact:

Post by WNY » Thu. Nov. 29, 2018 7:08 pm

Flue pipe close to stove is where many of us measure draft. easy to drill and add a fitting.
A lot of good threads on here for installing the manometer, the gauge itself doesn't have to be mounted on the stove, it can be mounted close and just run the tubing to it.

lots of good info here:
Manometer Install